Can anyone provide me with a reference? I'm on an inspection and haven't had the opportunity to look this up yet.

What section/reference requires all conductors of a single circuit to be contained within a single conduit?

Thanks in advance.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
Need a home inspection in Florida? Check out InterNACHI's listing of Florida certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 12/15/11, 1:41 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: Code Question

300.3 Conductors

• (B) Circuit Conductors Grouped Together.
All conductors of a circuit must be installed
in the same raceway, cable, trench, cord,
or cable tray, except



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
  #3  
Old 12/15/11, 2:40 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Code Question

Thanks Mike.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #4  
Old 12/15/11, 8:08 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Code Question

There is an exception for circuits run in non-metallic methods.
Reply With Quote
  #5  
Old 12/15/11, 11:42 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Code Question

Quote:
Originally Posted by Jim Port View Post
There is an exception for circuits run in non-metallic methods.
Yes, I know. This was in two runs of side-by-side PVC, buried and supplying the pool equipment panel about 60 feet away.

I had never seen this done before, so I wanted to check the reference before I left the property. One PVC contained 1 ungrounded conductor and the neutral, while the other PVC contained the other ungrounded conductor and the EGC.
Attached Thumbnails
code-question-20111215_07.jpg   code-question-20111215_08.jpg  



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net



Last edited by jpope; 12/15/11 at 11:45 PM..
Reply With Quote
  #6  
Old 12/16/11, 4:53 AM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Code Question

That is also a violation of 300.20(A).

Quote:
300.20 Induced Currents in Ferrous Metal Enclosures or Ferrous Metal Raceways.
(A) Conductors Grouped Together. Where conductors carrying alternating current are installed in ferrous metal enclosures or ferrous metal raceways, they shall be arranged so as to avoid heating the surrounding ferrous metal by induction. To accomplish this, all phase conductors and, where used, the grounded conductor and all equipment grounding conductors shall be grouped together.
Reply With Quote
  #7  
Old 12/16/11, 7:36 AM
Sean Fogarty's Avatar
Sean Fogarty Sean Fogarty is offline
InterNACHI Member
 
Join Date: Sep 2009
Location: Somewhere in Knoxville TN flipping breakers
Posts: 2,267
Default Re: Code Question

To shed light on my ingonrance, with the exception of it not being code, what is the potential concern with running the wires in that manner?




Infraspection Institute Level 1 Certified Infrared Thermographer

Fogarty Inspection Services Group of Knoxville TN

Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.

865-256-5397

www.homeinspectorknoxville.com

www.moldandradon.com

www.thermal-inspection.net

www.commercial-building-inspector.net
Reply With Quote
  #8  
Old 12/16/11, 7:57 AM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Code Question

The magnetic fields will cause heating.
Reply With Quote
  #9  
Old 12/16/11, 9:41 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Code Question

Quote:
Originally Posted by Robert Meier View Post
That is also a violation of 300.20(A).
I read that, but didn't believe that to be at issue.

This was new construction, and the electrical inspector "assured" me this is acceptable after I questioned it. Based on the exception of 300.3, I conceded. After all, he does have the last word.

I didn't think 300.20 was at issue because the conductors don't really "travel through" separate metallic enclosures. I guess I can see the potential for a small portion of the box to become heated.

So (Robert and Jim), do you guys see this as an improper installation?



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #10  
Old 12/16/11, 9:56 AM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Code Question

I would not do it this way and never thought about this before. I believe this meets the exception in 300.3. As far as 300.20, once the conductors enter the enclosure they could be considered grouped. I would like to hear other opinions on this.
Reply With Quote
  #11  
Old 12/16/11, 4:22 PM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Code Question

You're correct I quoted the wrong section It should be 300.20(B). 300.3(B)(3) directs you to 300.20(B).

Quote:
300.3(B)(3) Nonferrous Wiring Methods. Conductors in wiring methods with a nonmetallic or other nonmagnetic sheath, where run in different raceways, auxiliary gutters, cable trays, trenches, cables, or cords, shall comply with the provisions of 300.20(B). Conductors in single-conductor Type MI cable with a nonmagnetic sheath shall comply with the provisions of 332.31. Conductors of single-conductor Type MC cable with a nonmagnetic sheath shall comply with the provisions of 330.31, 330.116, and 300.20(B).
Quote:
300.20(B) Individual Conductors. Where a single conductor carrying alternating current passes through metal with magnetic properties, the inductive effect shall be minimized by (1) cutting slots in the metal between the individual holes through which the individual conductors pass or (2) passing all the conductors in the circuit through an insulating wall sufficiently large for all of the conductors of the circuit.
Reply With Quote
  #12  
Old 12/16/11, 5:35 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Code Question

Robert, as I understand 300.20 it would apply to things like K&T entering a metallic junction box or enclosure.
Reply With Quote
  #13  
Old 12/16/11, 5:42 PM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Code Question

Quote:
Originally Posted by Jim Port View Post
Robert, as I understand 300.20 it would apply to things like K&T entering a metallic junction box or enclosure.
Yes, but 300.3(B)(3) sends you to 300.20(B) which, in the case of the photo, would require a slot to be cut between the raceways. Since in the photo you have conductors run in different raceways then the provisions of 300.20(B) would apply.
Reply With Quote
Need a home inspection in Florida? Check out InterNACHI's listing of Florida certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 12/16/11, 6:40 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Code Question

After reading both together I agree a slot is needed.
Reply With Quote
  #15  
Old 12/16/11, 6:42 PM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Code Question

Yes it's a bit confusing because when you read 300.20(B) as a standalone requirement it doesn't seem to fit the installation in question. Once you add 300.3(B)(3) into the mix it directs you to the requirement for a slot.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Cap and Trade: A License Required for your Home fcarrio Legislation, Licensing & Legal Issues for Inspectors 349 10/21/11 6:56 PM
Interesting Lawsuit Regarding Code Violations jbushart Legislation, Licensing & Legal Issues for Inspectors 1 3/19/10 2:26 PM
Fire Code Question rbennett General Inspection Discussion 2 6/8/06 8:13 PM


All times are GMT -4. The time now is 5:53 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts