Default Code Requirement for pigtailing Aluminum Wiring

Is there a code requirement to pigtail an electrical system with aluminum wiring?
Reply With Quote
Need a home inspection in Utah? Check out InterNACHI's listing of Utah certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 10/13/12, 8:05 PM
Jeffrey R. Pope, CMI's Avatar
Jeffrey R. Pope, CMI Jeffrey R. Pope, CMI is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 11,208
Default Re: Code Requirement for pigtailing Aluminum Wiring

No, there is not.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #3  
Old 10/13/12, 10:06 PM
Joseph Hagarty,  CMI's Avatar
Joseph Hagarty, CMI Joseph Hagarty,  CMI is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: West Chester, PA
Posts: 6,879
Default Re: Code Requirement for pigtailing Aluminum Wiring

The mix of Copper & Aluminum is a concern....
(older Split Main Panel)
Attached Thumbnails
code-requirement-pigtailing-aluminum-wiring-img_2546.jpg   code-requirement-pigtailing-aluminum-wiring-img_2544.jpg  



Joseph P. Hagarty
joseph.hagarty@comcast.net
Main Line Inspections, Inc.
Phone: 610-399-3675
Email: MainLineHI@comcast.net

http://pa.nachi.org/mainlinepa/about.html
http://www.householdinspector.com

National President / NACHI (2003-2004)
NACHI Education Committee Member
PA NACHI Certified Inspector # 01102902
Delaware Licensed Home Inspector # H4-071
Reply With Quote
  #4  
Old 10/13/12, 11:44 PM
Jim Port Jim Port is online now
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 1,302
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Code Requirement for pigtailing Aluminum Wiring

Typically the breakers and bus bars were listed for use with both Al and CU.
Reply With Quote
  #5  
Old 10/13/12, 11:52 PM
Joseph Hagarty,  CMI's Avatar
Joseph Hagarty, CMI Joseph Hagarty,  CMI is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: West Chester, PA
Posts: 6,879
Default Re: Code Requirement for pigtailing Aluminum Wiring

Quote:
Originally Posted by Jim Port View Post
Typically the breakers and bus bars were listed for use with both Al and CU.
But not for copper and aluminum twisted together....
correct me if wrong........



Joseph P. Hagarty
joseph.hagarty@comcast.net
Main Line Inspections, Inc.
Phone: 610-399-3675
Email: MainLineHI@comcast.net

http://pa.nachi.org/mainlinepa/about.html
http://www.householdinspector.com

National President / NACHI (2003-2004)
NACHI Education Committee Member
PA NACHI Certified Inspector # 01102902
Delaware Licensed Home Inspector # H4-071
Reply With Quote
  #6  
Old 10/14/12, 9:04 AM
Jim Port Jim Port is online now
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 1,302
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Code Requirement for pigtailing Aluminum Wiring

That would be correct Joe. I have seen reports where the AL was on a breaker and the suggested "fix" was to pigtail copper. This was an unnecessary step as the breaker or bus was already listed for use with the aluminum.
Reply With Quote
  #7  
Old 10/14/12, 9:14 AM
Peter W. Bennett Peter W. Bennett is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Little Silver, NJ
Posts: 695
Default Re: Code Requirement for pigtailing Aluminum Wiring

Quote:
Originally Posted by jpope View Post
No, there is not.
So when an electrician conducts the pigtailing, there's no code requirement?
The only guidelines would be the manufacturer's instructions on the package?
Reply With Quote
  #8  
Old 10/14/12, 10:48 AM
Jim Port Jim Port is online now
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 1,302
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Code Requirement for pigtailing Aluminum Wiring

Could you expand on why the pigtailing was requested?

Unless the devices are listed for use with AL there would need to be a method like pigtailing. The simple existence of AL does not require pigtailing. There are also devices that are listed for use directly connected to the AL.
Reply With Quote
  #9  
Old 10/14/12, 10:53 AM
cevans's Avatar
cevans cevans is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Stagecoach, TX
Posts: 3,487
Please Note: cevans is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Code Requirement for pigtailing Aluminum Wiring

Quote:
Originally Posted by pbennett1 View Post
So when an electrician conducts the pigtailing, there's no code requirement?
The only guidelines would be the manufacturer's instructions on the package?
The question asked was
Quote:
Is there a code requirement to pigtail an electrical system with aluminum wiring?
The answer is no.

If you are asking does code apply if you do pigtail, which is an entirely different question, the answer would be yes.
Reply With Quote
  #10  
Old 10/14/12, 8:06 PM
Peter W. Bennett Peter W. Bennett is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Little Silver, NJ
Posts: 695
Default Re: Code Requirement for pigtailing Aluminum Wiring

Quote:
Originally Posted by cevans View Post
The question asked was

The answer is no.

If you are asking does code apply if you do pigtail, which is an entirely different question, the answer would be yes.
Thanks Chuck.
What's the code requirement if an electrical does the pigtailing?
Reply With Quote
  #11  
Old 10/14/12, 9:41 PM
Jim Port Jim Port is online now
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 1,302
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Code Requirement for pigtailing Aluminum Wiring

It would need to be done in accordance with any listing or labeling requirements.
Reply With Quote
  #12  
Old 10/14/12, 11:21 PM
Jeffrey R. Pope, CMI's Avatar
Jeffrey R. Pope, CMI Jeffrey R. Pope, CMI is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 11,208
Default Re: Code Requirement for pigtailing Aluminum Wiring

Quote:
Originally Posted by pbennett1 View Post
So when an electrician conducts the pigtailing, there's no code requirement?
The only guidelines would be the manufacturer's instructions on the package?
Apparently, I misunderstood the question.

It is not required that AL wiring be pig tailed with CU - that's what I thought the question was.

If the AL is pig tailed with CU, the connectors must be appropriately listed, and used in accordance with their manufacturer.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Aluminum Branch Wiring update jshishilla Florida Inspectors 7 8/20/13 7:33 AM
1910 Build mcyr Electrical Inspections 12 8/1/10 1:41 PM
Garage/house fire door Steven C. Meyer General Inspection Discussion 15 2/5/08 7:06 AM
Aluminum Wiring jhagarty Electrical Inspections 23 10/5/07 2:56 AM

All times are GMT -4. The time now is 10:33 PM.
no new posts