Default Color Coding Ungrounded Conductors

Does the NEC (or other code reference) specifically address color coding of ungrounded conductors in residential panels with respect to white (unlabled) being used as such?

If so, I could sure use a quote!


Thanks!
Reply With Quote
  #2  
Old 8/4/08, 7:12 PM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,098
Default Re: Color Coding Ungrounded Conductors

See 2003 IRC E3307.3 ....please..don't make me type it all in by hand
Reply With Quote
  #3  
Old 8/4/08, 8:17 PM
Speedy Petey Speedy Petey is offline
Active Poster
 
Join Date: Jul 2006
Posts: 1,294
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Color Coding Ungrounded Conductors

White is a grounded conductor, and does in fact need identification.
Ungrounded conductors can both be black, no extra identification is needed.

Some areas will allow the stripe on the neutral of URD cable as identification, although it does not meet the letter of the NEC.
Reply With Quote
  #4  
Old 8/4/08, 8:20 PM
Speedy Petey Speedy Petey is offline
Active Poster
 
Join Date: Jul 2006
Posts: 1,294
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Color Coding Ungrounded Conductors

NEC

200.6 Means of Identifying Grounded Conductors

(B) Sizes Larger Than 6 AWG
An insulated grounded conductor larger than 6 AWG shall be identified by one of the following means:

(1) By a continuous white or gray outer finish.
(2) By three continuous white stripes along its entire length on other than green insulation.
(3) At the time of installation, by a distinctive white or gray marking at its terminations. This marking shall encircle the conductor or insulation.
Reply With Quote
  #5  
Old 8/4/08, 8:22 PM
William Warner's Avatar
William Warner William Warner is offline
InterNACHI Member
 
Join Date: May 2003
Location: Dayton, OH
Posts: 2,027
Default Re: Color Coding Ungrounded Conductors

Quote:
Originally Posted by mboyett
See 2003 IRC E3307.3 ....please..don't make me type it all in by hand
Thanks Mike!

I found it quoted elsewhere!
Reply With Quote
  #6  
Old 8/4/08, 8:27 PM
William Warner's Avatar
William Warner William Warner is offline
InterNACHI Member
 
Join Date: May 2003
Location: Dayton, OH
Posts: 2,027
Default Re: Color Coding Ungrounded Conductors

Quote:
Originally Posted by Speedy Petey
White is a grounded conductor, and does in fact need identification.
Ungrounded conductors can both be black, no extra identification is needed.

Some areas will allow the stripe on the neutral of URD cable as identification, although it does not meet the letter of the NEC.
Thanks Speedy!
Reply With Quote
  #7  
Old 8/4/08, 8:32 PM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,098
Default Re: Color Coding Ungrounded Conductors

Quote:
Originally Posted by wwarner
I found it quoted elsewhere!
Good deal...did it say:

Quote:
E3307.3 Ungrounded conductors.
Insulation on the ungrounded conductors shall be a continuous color other than white, gray and green.

Exceptions:
1. An insulated conductor that is part of a cable or flexible cord assembly and that has a white or gray finish or a finish marking with three continuous white
stripes shall be permitted to be used as an ungrounded conductor where it is permanently reidentified to indicate its use as an ungrounded conductor at all terminations and at each location where the conductor is visible and accessible. Identification shall encircle the insulation and shall be a color other than white, gray, and green.






Last edited by mboyett; 8/4/08 at 8:38 PM..
Reply With Quote
  #8  
Old 8/4/08, 8:40 PM
William Warner's Avatar
William Warner William Warner is offline
InterNACHI Member
 
Join Date: May 2003
Location: Dayton, OH
Posts: 2,027
Default Re: Color Coding Ungrounded Conductors

Quote:
Originally Posted by mboyett
Good deal...did it say:

Yup!

Except for the very last sentence. But I think they will get the gist of it. I called it out on an inspection in June and just now the electrician was looking at it and thought I was calling out the grounded conductor on an AFCI. I guess the picture with a red circle and arrow didn't help...

It was the breaker just above one of the AFCI's...

Client was looking for a code source to give to the builder's electrician.

All is well (I hope)

Last edited by wwarner; 8/4/08 at 8:44 PM..
Reply With Quote
  #9  
Old 8/4/08, 9:20 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Color Coding Ungrounded Conductors

It might be noted that the requirement to reidentify a white wire in a switch loop is fairly recent (1999 or 2002?) so in older homes you might see a white and black on a switch. The white should be the hot leg and the black the switched leg so you end up with a hot (switched) black and a white neutral where it attaches to the luminaire. That makes it line up with the pigtail on the light. If you see a black and a white under a wirenut in the box, that should tip you off that this is the outgoing switch loop leg ... if you are an old guy who worked before 2002.
Reply With Quote
  #10  
Old 8/4/08, 11:59 PM
Mike Whitt's Avatar
Mike Whitt Mike Whitt is offline
Active Poster
 
Join Date: Sep 2005
Location: North Carolina
Posts: 474
Please Note: Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Color Coding Ungrounded Conductors

Quote:
Originally Posted by Greg Fretwell
It might be noted that the requirement to reidentify a white wire in a switch loop is fairly recent (1999 or 2002?)
200.7 Exception 1 of the 1968 code cycle had the requirement to change the color of a white conductor when it was being used for an ungrounded conductor.
Reply With Quote
  #11  
Old 8/5/08, 1:26 AM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Color Coding Ungrounded Conductors

In 1996 it says
200-7 ex2 <cable switch loop verbiage> ... "In these applications re-identification of the white or natural gray conductor shall not be required".

That goes away in 1999.

I just looked and ex2 goes as far back as 75, the oldest book I have handy. What does it say in 68 again?

Last edited by Greg Fretwell; 8/5/08 at 1:30 AM..
Reply With Quote
  #12  
Old 8/5/08, 12:57 PM
Mike Whitt's Avatar
Mike Whitt Mike Whitt is offline
Active Poster
 
Join Date: Sep 2005
Location: North Carolina
Posts: 474
Please Note: Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Color Coding Ungrounded Conductors

Let’s start with the original question:
Quote:
Originally Posted by wwarner
Does the NEC (or other code reference) specifically address color coding of ungrounded conductors in residential
Quote:
Originally Posted by wwarner
panels with respect to white (unlabled) being used as such?
If so, I could sure use a quote!
Thanks!
Then you made your statement about switch loops and I came back to the original question to show that in the panel the requirement has been in the code for several years.



As one can see from the 1968 code cycle in the panel the conductor is required to be identified as something other than white or gray when being used as an ungrounded conductor.

As you have pointed out the requirement about switch loops is correct but is not part of the original post.
I was just trying to keep the original poster from confusing the switch loop from the conductors found in a panel.
Reply With Quote
  #13  
Old 8/5/08, 2:02 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Color Coding Ungrounded Conductors

I agree Mike, that is why I was very clear to differentiate "switch loops" when I made the original comment.
Reply With Quote
  #14  
Old 8/5/08, 10:39 PM
Mike Whitt's Avatar
Mike Whitt Mike Whitt is offline
Active Poster
 
Join Date: Sep 2005
Location: North Carolina
Posts: 474
Please Note: Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Color Coding Ungrounded Conductors

Quote:
Originally Posted by Greg Fretwell
I agree Mike, that is why I was very clear to differentiate "switch loops" when I made the original comment.
Good deal this means we are all on the same page, and thank you.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
What do you think? Can this work for you? jtedesco1 Electrical 13 2/9/09 11:58 PM
Where is it written.... bgromicko General Inspection Discussion 18 1/19/08 10:02 PM
Article 240 : Overcurrent Protection Article pabernathy Electrical 0 5/23/07 12:40 PM
Need Help from the Learned... gbrasseur Electrical 15 12/19/06 6:04 PM


All times are GMT -4. The time now is 11:34 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts