Anyone care to comment about the ground wire connection on the left side of this distribution panel?
Attached Thumbnails
comments-ground-wires-left-side-img_6299_r1.jpg   comments-ground-wires-left-side-img_6301_r1.jpg  
Reply With Quote
  #2  
Old 1/6/06, 11:42 PM
brian winkle brian winkle is offline
Active Poster
 
Join Date: Sep 2005
Location: Arizona
Posts: 454
Please Note: brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Comments on ground wires (left side)

The only part that doesn't meet code is the screw. It should be a machine screw threaded into a tapped hole, not a cabinet mounting mounting screw. A terminal lug would've been nice, or even a bar. But not required. Also, most inspectors would request the ground wires be twisted before installing the barrel crimps.
Reply With Quote
  #3  
Old 1/7/06, 2:12 AM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Comments on ground wires (left side)

How is the cabinet bonded? Is this conduit?
I don't see any paint removed under the screw.
The other issue, is it a sheet metal screw?

I don't imagine an inspector would have much trouble talking them into a grounding bus kit but it may be "hold your nose legal. If it was my house I would shove a grounds wire in that pipe and install the $3 bus bar kit.
Reply With Quote
  #4  
Old 1/7/06, 7:58 AM
rwand1 rwand1 is offline
Active Poster
 
Join Date: Sep 2005
Location: Caledon, ON
Posts: 7,987
Please Note: rwand1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Comments on ground wires (left side)

Is this a sub-panel? Looks okay to me. If it is the main panel where is the bonding screw?

Raymond Wand
Alton, ON
Reply With Quote
  #5  
Old 1/7/06, 9:19 AM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 5,663
Default Re: Comments on ground wires (left side)

Quote:
Originally Posted by Greg Fretwell
If it was my house I would shove a grounds wire in that pipe and install the $3 bus bar kit.
Greg, I'm not following this. Can you expand on the pipe part some more?

Appreciate it.
Reply With Quote
  #6  
Old 1/7/06, 9:33 AM
Bob Badger Bob Badger is offline
New User
 
Join Date: Dec 2003
Posts: 77
Please Note: Bob Badger is a non-member guest and is in no way affiliated with InterNACHI or its members.
Smile Re: Comments on ground wires (left side)

Quote:
Originally Posted by lkage
Greg, I'm not following this. Can you expand on the pipe part some more?

Appreciate it.
I think Greg is suggesting a grounding wire run in the pipe with the feeder back to the source attached to a grounding bar in this panel would be a more reliable grounding means than the EMT that is apparently being used as the EGC now.

I do not see that as a big deal but at that same time it is hard to argue against the grounding redundancy of EMT and a grounding conductor.

Just to be clear EMT is an NEC approved grounding conductor and can do that job quite well if installed correctly and all joints are made tight.

It is not unusual to find loose couplings in EMT which can greatly effect the ability of the EMT to handle fault current.
Reply With Quote
  #7  
Old 1/7/06, 9:43 AM
Bob Badger Bob Badger is offline
New User
 
Join Date: Dec 2003
Posts: 77
Please Note: Bob Badger is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Comments on ground wires (left side)

I should also point out that now there is an NEC section requiring a grounding terminal bar installed in panels used with non-metallic raceways or cables. 408.20

However I do not know when that section was added to the NEC.
Reply With Quote
  #8  
Old 1/7/06, 9:44 AM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 5,663
Default Re: Comments on ground wires (left side)

Thanks, Bob.
Reply With Quote
  #9  
Old 1/7/06, 11:17 AM
brian winkle brian winkle is offline
Active Poster
 
Join Date: Sep 2005
Location: Arizona
Posts: 454
Please Note: brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Comments on ground wires (left side)

I was in such a rush I didn't notice the absence of a grounding conductor. No way to tell from the pic if there is pipe all the way to the main. If there isn't, well then those grounding conductors are bonded to nothing. Of course they could test grounded thru the furnace gas connection etc if one of those circuits is the air handler.
Reply With Quote
  #10  
Old 1/7/06, 11:46 AM
Bob Badger Bob Badger is offline
New User
 
Join Date: Dec 2003
Posts: 77
Please Note: Bob Badger is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Comments on ground wires (left side)

Quote:
Originally Posted by brian winkle
No way to tell from the pic if there is pipe all the way to the main.


A scary thought if an electrician left the raceway incomplete.


But your right, if it runs concealed we do not really know.

A reasonable test would be simply hot to ground, I would 'lift' the branch circuit grounds first so a ground is not found through an appliance like a furnace and gas line.

Any real load testing of the raceway could be destructive so for the most part we have to assume the installation was inspected before the walls where closed.
Reply With Quote
  #11  
Old 1/7/06, 12:14 PM
Paul Burrows Paul Burrows is offline
New User
 
Join Date: Jan 2006
Posts: 13
Please Note: Paul Burrows is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Comments on ground wires (left side)

If you are not sure recommend further evaluation by licensed electrician.
Reply With Quote
  #12  
Old 1/7/06, 12:56 PM
jweinberg's Avatar
jweinberg jweinberg is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: San Jose, CA
Posts: 420
Please Note: jweinberg is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Comments on ground wires (left side)

Quote:
Originally Posted by rwand1
Is this a sub-panel? Looks okay to me. If it is the main panel where is the bonding screw?

Raymond Wand
Alton, ON
This is a sub panel inside one of the units in a 4plex
Reply With Quote
  #13  
Old 1/7/06, 1:07 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Comments on ground wires (left side)

I don't know about your Shurtest but my Ecos uses a significant amount of current to test the ground integrity. It will bite you if the ground is open and you are touching the EGC. (lots of warnings in the manual) If the EGC is <1 ohm you probably have a fairly good connection on the EGC.
Reply With Quote
  #14  
Old 1/7/06, 6:44 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,524
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Comments on ground wires (left side)

Hey Guys,

I would guess for the HI's the most important thing in this picture when reporting is the following:

1.) Incorrect method of bonding the EGC to the Enclosure
2.) Call me names if you will....but in that picture it looks like the lockring is not a what we call "self bonding" style that actually digs into the enclosure and removes the coating and makes a proper bonding on that EMT.

Now....as I have said in the past...I am not really a fan of giving comments on pictures that i can't blow up and see very well so these are just comments...take them for what they are worth.

3.)...Again I can't tell but the screw in the middle of the grounded conductor bar may be the bonding screw...again so many different panels and so on I can't tell...but it would be easy to check that and we will assume you did and it is truly floating. A test from bar to inside threads of the cover screw holes would tell you...lol...

4.) again..just me or I can't tell if the old cloth cables are coming in via a connector....man I am just getting OLD i guess and can't see clearly plus I have the FLU so that always sucks.

Anyway...suggestion is 1.) you are safe to say consult a licensed electrical contractor 2.) improper EGC bonding method and you should cover youself as you atleast suggested a licensed electrical contractor review this panel and they will do the checks on the system to determine if it is properly bonded and grounded from point A to point B.



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #15  
Old 1/7/06, 6:54 PM
Bob Badger Bob Badger is offline
New User
 
Join Date: Dec 2003
Posts: 77
Please Note: Bob Badger is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Comments on ground wires (left side)

Quote:
Originally Posted by pabernathy
Hey Guys,

2.) Call me names if you will....but in that picture it looks like the lockring is not a what we call "self bonding" style that actually digs into the enclosure and removes the coating and makes a proper bonding on that EMT.
Paul I would never call you names but I will point out that all EMT connectors are listed for grounding and the locknuts are designed to cut the paint.

Bonding bushings or locknuts are only required for certain areas, service raceways and for some applications above 250 to ground. I do not believe that this is either.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical 6 9/15/08 8:57 AM
Electrical Safety Foundation International Links jtedesco1 Electrical 5 12/8/07 4:10 PM
Tidbits from the ASHI Message Board jbushart Misc. Discussion 124 4/27/07 12:05 PM
All Breakers on left side of bus mcotten Electrical 18 2/1/07 2:24 PM
Chapter Listings on the Left Hand side of this bb? jbowman Misc. Discussion 14 1/30/06 5:15 PM


All times are GMT -4. The time now is 5:21 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts