Anyone care to comment about the ground wire connection on the left side of this distribution panel?
|
|
#2
|
|||
|
|||
|
Please Note:
brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
The only part that doesn't meet code is the screw. It should be a machine screw threaded into a tapped hole, not a cabinet mounting mounting screw. A terminal lug would've been nice, or even a bar. But not required. Also, most inspectors would request the ground wires be twisted before installing the barrel crimps.
|
|
#3
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
How is the cabinet bonded? Is this conduit?
I don't see any paint removed under the screw. The other issue, is it a sheet metal screw? I don't imagine an inspector would have much trouble talking them into a grounding bus kit but it may be "hold your nose legal. If it was my house I would shove a grounds wire in that pipe and install the $3 bus bar kit. |
|
#4
|
|||
|
|||
|
Please Note:
rwand1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Is this a sub-panel? Looks okay to me. If it is the main panel where is the bonding screw?
Raymond Wand Alton, ON |
|
#5
|
|||
|
|||
|
Quote:
Appreciate it. |
|
#6
|
|||
|
|||
|
Please Note:
Bob Badger is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
I do not see that as a big deal but at that same time it is hard to argue against the grounding redundancy of EMT and a grounding conductor. Just to be clear EMT is an NEC approved grounding conductor and can do that job quite well if installed correctly and all joints are made tight. It is not unusual to find loose couplings in EMT which can greatly effect the ability of the EMT to handle fault current. |
|
#7
|
|||
|
|||
|
Please Note:
Bob Badger is a non-member guest and is in no way affiliated with InterNACHI or its members.
I should also point out that now there is an NEC section requiring a grounding terminal bar installed in panels used with non-metallic raceways or cables. 408.20
However I do not know when that section was added to the NEC. |
|
#8
|
|||
|
|||
|
Thanks, Bob.
|
|
#9
|
|||
|
|||
|
Please Note:
brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
I was in such a rush I didn't notice the absence of a grounding conductor. No way to tell from the pic if there is pipe all the way to the main. If there isn't, well then those grounding conductors are bonded to nothing. Of course they could test grounded thru the furnace gas connection etc if one of those circuits is the air handler.
|
|
#10
|
|||
|
|||
|
Please Note:
Bob Badger is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
A scary thought if an electrician left the raceway incomplete. But your right, if it runs concealed we do not really know. A reasonable test would be simply hot to ground, I would 'lift' the branch circuit grounds first so a ground is not found through an appliance like a furnace and gas line. Any real load testing of the raceway could be destructive so for the most part we have to assume the installation was inspected before the walls where closed. |
|
#11
|
|||
|
|||
|
Please Note:
Paul Burrows is a non-member guest and is in no way affiliated with InterNACHI or its members.
If you are not sure recommend further evaluation by licensed electrician.
|
|
#12
|
||||
|
||||
|
Please Note:
jweinberg is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#13
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
I don't know about your Shurtest but my Ecos uses a significant amount of current to test the ground integrity. It will bite you if the ground is open and you are touching the EGC. (lots of warnings in the manual) If the EGC is <1 ohm you probably have a fairly good connection on the EGC.
|
|
#14
|
||||
|
||||
|
Hey Guys,
I would guess for the HI's the most important thing in this picture when reporting is the following: 1.) Incorrect method of bonding the EGC to the Enclosure 2.) Call me names if you will....but in that picture it looks like the lockring is not a what we call "self bonding" style that actually digs into the enclosure and removes the coating and makes a proper bonding on that EMT. Now....as I have said in the past...I am not really a fan of giving comments on pictures that i can't blow up and see very well so these are just comments...take them for what they are worth. 3.)...Again I can't tell but the screw in the middle of the grounded conductor bar may be the bonding screw...again so many different panels and so on I can't tell...but it would be easy to check that and we will assume you did and it is truly floating. A test from bar to inside threads of the cover screw holes would tell you...lol... 4.) again..just me or I can't tell if the old cloth cables are coming in via a connector....man I am just getting OLD i guess and can't see clearly plus I have the FLU so that always sucks. Anyway...suggestion is 1.) you are safe to say consult a licensed electrical contractor 2.) improper EGC bonding method and you should cover youself as you atleast suggested a licensed electrical contractor review this panel and they will do the checks on the system to determine if it is properly bonded and grounded from point A to point B. Paul W. Abernathy,CMI,CEI,CEPE NECŪ Consultant/Columnist www.twitter.com/ElectricalGuru - ICC & IAEI Certified Electrical Inspector - ICC & IAEI Certified Electrical Plans Examiner - Look for my article in the Nov/Dec 2009 IAEI Magazine - 2007 "Top Gun" Winner - Mike Holt Enterprises " visit www.TheElectricalGuru.com Today !" |
|
#15
|
|||
|
|||
|
Please Note:
Bob Badger is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
Bonding bushings or locknuts are only required for certain areas, service raceways and for some applications above 250 to ground. I do not believe that this is either. |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| "UFER" Ground? see last paragraph. | jtedesco1 | Electrical | 6 | 9/15/08 8:57 AM |
| Electrical Safety Foundation International Links | jtedesco1 | Electrical | 5 | 12/8/07 4:10 PM |
| Tidbits from the ASHI Message Board | jbushart | Misc. Discussion | 124 | 4/27/07 12:05 PM |
| All Breakers on left side of bus | mcotten | Electrical | 18 | 2/1/07 2:24 PM |
| Chapter Listings on the Left Hand side of this bb? | jbowman | Misc. Discussion | 14 | 1/30/06 5:15 PM |