#1
|
||||
|
||||
|
I was totally surprised to see this panel mounted horizontally.
Is it against code to do this. The biggest pain is turning sideways to read everthing & the door is hinged at the top so it won't stay open.Roy |
|
#2
|
|||
|
|||
|
How many breakers are in the on position when down? Not a good plan.
____________________________________________ "An Education, not just an Inspection" Larry Kage Lake Ann (Traverse City), Michigan 49650 231 929 3525 Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond. ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
|
|
#3
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
It is not a code violation to install the panel like that in the US, but it is a violation to install breakers in that one column when the panel is oriented that way. The column of breakers that have the handle down when they're in the "ON" position are in violation. It looks like maybe the main is even in violation.
|
|
#4
|
||||
|
||||
|
That panel definitely needs an Electrician's attention.
|
|
#5
|
||||
|
||||
|
Is there an issue with the door not allowing "access" to the breakers since it won't stay open?
|
|
#6
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
No, but realistically, that's a royal pain in the ***. Feel free to add that in your report, but there's no prohibition against it. My comment above is really the only prohibition against it. Your comment about the door is more of a nuisance issue. The code only requires that the door open 90 degrees. It doesn't say in what direction. "UP" is a stupid direction, but legal.
|
|
#7
|
|||
|
|||
|
Quote:
Maybe we have no such rule in Canada. |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| comments on these joists please | mmatalik | Structural | 12 | 9/12/08 9:24 PM |
| Infrared Sample reports | dvalley | Thermal Imaging, Infrared Cameras & Energy Audits | 26 | 1/1/08 9:40 PM |
| For those in favor of licensing | gbeaumont | Legislation, Licensing & Legal Issues | 70 | 5/21/07 4:09 PM |
| Tidbits from the ASHI Message Board | jbushart | Misc. Discussion | 124 | 4/27/07 12:05 PM |