Default Comments Please!!

I was totally surprised to see this panel mounted horizontally. comments-please-image_00224.jpgIs it against code to do this. The biggest pain is turning sideways to read everthing & the door is hinged at the top so it won't stay open.

Roy
Attached Thumbnails
comments-please-image_00225.jpg  
Reply With Quote
  #2  
Old 12/8/08, 10:39 AM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 5,745
Default Re: Comments Please!!

How many breakers are in the on position when down? Not a good plan.



____________________________________________
"An Education, not just an Inspection"

Larry Kage
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond.


ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER

ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
Reply With Quote
  #3  
Old 12/8/08, 11:41 AM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Comments Please!!

It is not a code violation to install the panel like that in the US, but it is a violation to install breakers in that one column when the panel is oriented that way. The column of breakers that have the handle down when they're in the "ON" position are in violation. It looks like maybe the main is even in violation.
Reply With Quote
  #4  
Old 12/8/08, 12:02 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,027
Default Re: Comments Please!!

That panel definitely needs an Electrician's attention.
Reply With Quote
  #5  
Old 12/10/08, 3:10 PM
rromoser's Avatar
rromoser rromoser is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Fishers, IN
Posts: 187
Default Re: Comments Please!!

Is there an issue with the door not allowing "access" to the breakers since it won't stay open?
Reply With Quote
  #6  
Old 12/10/08, 5:36 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Comments Please!!

Quote:
Originally Posted by rromoser View Post
Is there an issue with the door not allowing "access" to the breakers since it won't stay open?
No, but realistically, that's a royal pain in the ***. Feel free to add that in your report, but there's no prohibition against it. My comment above is really the only prohibition against it. Your comment about the door is more of a nuisance issue. The code only requires that the door open 90 degrees. It doesn't say in what direction. "UP" is a stupid direction, but legal.
Reply With Quote
  #7  
Old 12/13/08, 4:18 PM
John Allingham John Allingham is offline
InterNACHI Member
 
Join Date: Jun 2004
Location: Milton, ON
Posts: 377
Default Re: Comments Please!!

Quote:
Originally Posted by Marc D. Shunk View Post
It is not a code violation to install the panel like that in the US, but it is a violation to install breakers in that one column when the panel is oriented that way. The column of breakers that have the handle down when they're in the "ON" position are in violation. It looks like maybe the main is even in violation.
Brand new house. Top row of breakers were definetly "on" in the down position.
Maybe we have no such rule in Canada.
Attached Thumbnails
comments-please-pc130020.jpg  
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
comments on these joists please mmatalik Structural 12 9/12/08 9:24 PM
Infrared Sample reports dvalley Thermal Imaging, Infrared Cameras & Energy Audits 26 1/1/08 9:40 PM
For those in favor of licensing gbeaumont Legislation, Licensing & Legal Issues 70 5/21/07 4:09 PM
Tidbits from the ASHI Message Board jbushart Misc. Discussion 124 4/27/07 12:05 PM


All times are GMT -4. The time now is 10:24 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts