- Zinsco panel in a detached garage (main for the manufactured home).
- 4 poll main breaker - Three splits under the main breaker, (1) down to the panel below, (2) out to the manufactured home, (3) could not trace where its going. First time I've seen a set up like this, was hoping you electrical vets had any comments other then the normal zinsco - blah, blah. Thanks Peter Doane Realty Check Inspection Service NACHI ID# 05120681
|
|
#2
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
That's a pretty freaking weird panel. That's not a 4-pole main breaker. That's two, two pole breakers. One, for a subfeed breaker, and one to take care of the branch breakers in the lower section. A 200 amp feed hits those main lugs on top, then it goes through two double pole, 100 amp breakers. That's 100 amps for the subfeed breaker, and 100 amps for the branch breaker buss below.
It appears the main breaker on the left there is double-tapped. Once, for another subfeed, and once to go down the the buss for the branch breakers. Last edited by Marc D. Shunk; 4/26/07 at 1:02 AM.. |
|
#3
|
|||
|
|||
|
Please Note:
jbreazeale is a non-member guest and is in no way affiliated with InterNACHI or its members.
Dang, Marc, you must LIVE on this board!! LOL!! Anyway, for the record I concur with your assessment. Gotta call out that double tap.....as if there was no way to avoid it! Geeze!
|
|
#4
|
||||
|
||||
|
Quote:
The reason I called it a 4 pole was because I could not trip each double pole independently. All 4 trip together,.... and I could not find out where they tied together other then possibly internally and hence my deduction of a 4 pole. Thanks for your insight! Peter Doane Realty Check Inspection Service NACHI ID# 05120681
|
|
#5
|
|||
|
|||
|
All 4 trip together? That is hella weird.
"Howard, Fine, and Howard Electrical at your service" ... nyuk, nyuk, nyuk... Can't make out whether the bottom left terminals are double-tapped or they are hard-wired connection off the mains passing under the "quadruple pole" breaker to the bottom bus... were they double-tapped, Peter? |
|
#6
|
|||
|
|||
|
Please Note:
Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
I have one in my own home. |
|
#7
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#8
|
|||
|
|||
|
Please Note:
Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Oh. OK, I see it now.
Pretty much like the old fuse panels with the two pullouts at the top. One lighting main and one range. |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Furnace Problem Comments Welcome | rfrost | Inspecting HVAC Systems | 28 | 10/21/07 6:26 PM |
| For those in favor of licensing | gbeaumont | Legislation, Licensing & Legal Issues for Inspectors | 70 | 5/21/07 3:09 PM |
| Tidbits from the ASHI Message Board | jbushart | Miscellaneous Discussion for Inspectors | 126 | 4/27/07 11:05 AM |