Default Commercial Sub Panel Question

I've got a commercial inspection that I am doing next week. Did a site visit today, and have what is probably a basic question.

I know that sub panels should not have more than 6 breakers (throws) in general without having a "main" breaker in them. However there is/are main breakers, and I want to know if it's ok...
Main Service enters in and is labeled as 800AMP service with a single breaker to shut off power to the whole building.

Right next to this are 12 individual meters, each with an attached "panel" with a single 125A breaker.

Inside the building there are sub-panels throughout, that have various numbers of breakers in them, almost all have more than 6. None of these have a single shutoff.

My question is, since there is a single main outside, and each meter has its own shutoff, is there still a requirement that the sub panels have a shutoff too?
Reply With Quote
  #2  
Old 12/4/08, 1:52 PM
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 11,750
Default Re: Commercial Sub Panel Question

Quote:
Originally Posted by mnahrgang View Post
My question is, since there is a single main outside, and each meter has its own shutoff, is there still a requirement that the sub panels have a shutoff too?

No..



"Never ever threaten anyone in Camoflage"
Tim Wilson

"Not everyone follows the same path"
Governor Sanford, musings on the Appalachian Trail
Reply With Quote
  #3  
Old 12/4/08, 4:13 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,038
Default Re: Commercial Sub Panel Question

Quote:
Originally Posted by mnahrgang View Post
I know that sub panels should not have more than 6 breakers (throws) in general without having a "main" breaker in them.
This is incorrect. The "six-throw" rule applies to the service equipment.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #4  
Old 12/4/08, 4:23 PM
Speedy Petey Speedy Petey is offline
Active Poster
 
Join Date: Jul 2006
Posts: 1,294
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Commercial Sub Panel Question

Quote:
Originally Posted by jpope View Post
This is incorrect. The "six-throw" rule applies to the service equipment.
Or a feeder to a detached structure.
Reply With Quote
  #5  
Old 12/4/08, 4:26 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,038
Default Re: Commercial Sub Panel Question

The feeder requires a disconnect even if there are six or less breakers, does it not?



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #6  
Old 12/4/08, 5:01 PM
Speedy Petey Speedy Petey is offline
Active Poster
 
Join Date: Jul 2006
Posts: 1,294
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Commercial Sub Panel Question

No Jeff. I am referring to NEC 225.33
Reply With Quote
  #7  
Old 12/4/08, 5:06 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,038
Default Re: Commercial Sub Panel Question

Got it.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #8  
Old 12/4/08, 5:16 PM
Mark Nahrgang's Avatar
Mark Nahrgang Mark Nahrgang is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Saint Peters, MO
Posts: 3,959
Default Re: Commercial Sub Panel Question

Quote:
Originally Posted by jpope View Post
This is incorrect. The "six-throw" rule applies to the service equipment.
Ok, Got it. Thanks guys.
Reply With Quote
  #9  
Old 12/4/08, 5:52 PM
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 11,750
Default Re: Commercial Sub Panel Question

Quote:
Originally Posted by bkelly2 View Post
No..
I thought no covered it quite nicely.



"Never ever threaten anyone in Camoflage"
Tim Wilson

"Not everyone follows the same path"
Governor Sanford, musings on the Appalachian Trail
Reply With Quote
  #10  
Old 12/4/08, 5:56 PM
James F. McKee's Avatar
James F. McKee James F. McKee is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Amherst, Oh
Posts: 4,403
Default Re: Commercial Sub Panel Question

Quote:
Originally Posted by bkelly2 View Post
I thought no covered it quite nicely.
in a minimalist fashion it did



Classic Home inspections

Jim Mckee
Amherst, Ohio

www.amhersthomeinspector.com

Last edited by jmckee; 12/4/08 at 6:55 PM..
Reply With Quote
  #11  
Old 12/4/08, 6:53 PM
Mark Nahrgang's Avatar
Mark Nahrgang Mark Nahrgang is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Saint Peters, MO
Posts: 3,959
Default Re: Commercial Sub Panel Question

Quote:
Originally Posted by bkelly2 View Post
I thought no covered it quite nicely.
It did! That that was exactly what I needed. The additional info and correction was also well appreciated.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Sub panel question smcintire Electrical 2 4/13/08 10:20 PM
Panel Question gmckenzie Electrical 9 8/24/07 2:25 AM
Electrical panel question hziegenbein Electrical 7 3/17/07 3:11 PM
Service Panel question for board sparkies pbolliger Electrical 8 5/14/06 10:24 AM
Bad electrical problem Pest Guy Electrical 4 1/20/06 10:26 PM


All times are GMT -4. The time now is 1:51 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts