I've got a commercial inspection that I am doing next week. Did a site visit today, and have what is probably a basic question.

I know that sub panels should not have more than 6 breakers (throws) in general without having a "main" breaker in them. However there is/are main breakers, and I want to know if it's ok...
Main Service enters in and is labeled as 800AMP service with a single breaker to shut off power to the whole building.

Right next to this are 12 individual meters, each with an attached "panel" with a single 125A breaker.

Inside the building there are sub-panels throughout, that have various numbers of breakers in them, almost all have more than 6. None of these have a single shutoff.

My question is, since there is a single main outside, and each meter has its own shutoff, is there still a requirement that the sub panels have a shutoff too?



Mark Nahrgang
www.DaytonSpringfieldHomeInspector.com
www.HeyMark.info

Home Inspections for Springfield, Dayton, and surrounding OH areas.
Reply With Quote
  #2  
Old 12/4/08, 1:52 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,852
Default Re: Commercial Sub Panel Question

Quote:
Originally Posted by mnahrgang View Post
My question is, since there is a single main outside, and each meter has its own shutoff, is there still a requirement that the sub panels have a shutoff too?

No..
Reply With Quote
  #3  
Old 12/4/08, 4:13 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Commercial Sub Panel Question

Quote:
Originally Posted by mnahrgang View Post
I know that sub panels should not have more than 6 breakers (throws) in general without having a "main" breaker in them.
This is incorrect. The "six-throw" rule applies to the service equipment.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #4  
Old 12/4/08, 4:23 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Commercial Sub Panel Question

Quote:
Originally Posted by jpope View Post
This is incorrect. The "six-throw" rule applies to the service equipment.
Or a feeder to a detached structure.
Reply With Quote
  #5  
Old 12/4/08, 4:26 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Commercial Sub Panel Question

The feeder requires a disconnect even if there are six or less breakers, does it not?



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #6  
Old 12/4/08, 5:01 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Commercial Sub Panel Question

No Jeff. I am referring to NEC 225.33
Reply With Quote
  #7  
Old 12/4/08, 5:06 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Commercial Sub Panel Question

Got it.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #8  
Old 12/4/08, 5:16 PM
mnahrgang's Avatar
mnahrgang mnahrgang is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Springfield, OH
Posts: 5,799
Default Re: Commercial Sub Panel Question

Quote:
Originally Posted by jpope View Post
This is incorrect. The "six-throw" rule applies to the service equipment.
Ok, Got it. Thanks guys.



Mark Nahrgang
www.DaytonSpringfieldHomeInspector.com
www.HeyMark.info

Home Inspections for Springfield, Dayton, and surrounding OH areas.
Reply With Quote
  #9  
Old 12/4/08, 5:52 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,852
Default Re: Commercial Sub Panel Question

Quote:
Originally Posted by bkelly2 View Post
No..
I thought no covered it quite nicely.
Reply With Quote
  #10  
Old 12/4/08, 5:56 PM
James F. McKee's Avatar
James F. McKee James F. McKee is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Amherst, Oh
Posts: 5,393
Default Re: Commercial Sub Panel Question

Quote:
Originally Posted by bkelly2 View Post
I thought no covered it quite nicely.
in a minimalist fashion it did



Classic Home inspections

Jim Mckee
Amherst, Ohio

www.amhersthomeinspector.com

Last edited by jmckee; 12/4/08 at 6:55 PM..
Reply With Quote
  #11  
Old 12/4/08, 6:53 PM
mnahrgang's Avatar
mnahrgang mnahrgang is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Springfield, OH
Posts: 5,799
Default Re: Commercial Sub Panel Question

Quote:
Originally Posted by bkelly2 View Post
I thought no covered it quite nicely.
It did! That that was exactly what I needed. The additional info and correction was also well appreciated.



Mark Nahrgang
www.DaytonSpringfieldHomeInspector.com
www.HeyMark.info

Home Inspections for Springfield, Dayton, and surrounding OH areas.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Sub panel question smcintire Electrical Inspections 2 4/13/08 10:20 PM
Panel Question gmckenzie Electrical Inspections 9 8/24/07 2:25 AM
Electrical panel question hziegenbein Electrical Inspections 7 3/17/07 3:11 PM
Service Panel question for board sparkies pbolliger Electrical Inspections 8 5/14/06 10:24 AM
Bad electrical problem Pest Guy Electrical Inspections 4 1/20/06 10:26 PM


All times are GMT -4. The time now is 3:24 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts