Default Complex challenge with bath exhaust fan - need help with solution!

Don't know if this is an electric or HVAC question, but here is my problem ...

we have a 60's brick ranch house that we are remodeling ... one story with a full basement ... it has 2 small baths that stack on top of each other, both on the back wall of the house ... the exterior wall on the top bath is brick veneer on wood frame and the the exterior wall on the lower bath is 10" concrete block ... now, the issue we have ...

neither bath has an exhaust fan ... I don't want to just exhaust the upper bath into the attic space and going through the brick wall to the outside would be a pain; however, going into the attic and piping to the soffit (we have a fairly wide overhang) seems like a reasonable solution ... but, what about ...

the lower bath? ... the only options I can come up with to vent to the outside is to go through the concrete block (ugh!), go into the space between the two floors and then through the brick wall above (not easy either), or lastly ...

go up and through the upstairs bath and tie into the exhaust pipe in the attic (in other words, share the same exit pipe with the upstairs bath) ... this could be done fairly easily since both baths are currently torn down to the studs ... my question is ...

can or should this be done? ... I've never seen it done before ... it's a long way for the exhaust to go up and out from the lower bath to the soffit on the upper floor ...

any ideas or suggestions about how to solve this exhaust challenge? ...

if my idea makes sense, how should I size each of the exhaust fans? again, both baths are small (about 6' x 8').

Thanks in advance, Bill
Reply With Quote
  #2  
Old 11/2/07, 11:20 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,020
Default Re: Complex challenge with bath exhaust fan - need help with solution!

You can install one fan to control both bathrooms. The lower bathroom hose is going to be quite long but it should be fine. If your concerned about condensation build-up in the lower bathroom then you have no choice but to penetrate the solid wall.

Go here and scroll down to
Reply With Quote
  #3  
Old 11/2/07, 11:55 AM
Bill Featherstone Bill Featherstone is offline
New User
 
Join Date: Nov 2007
Location: NW Arkansas
Posts: 39
Please Note: Bill Featherstone is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Complex challenge with bath exhaust fan - need help with solution!

Quote:
Originally Posted by dvalley
If your concerned about condensation build-up in the lower bathroom then you have no choice but to penetrate the solid wall.
Thanks for your help, David. Just emailed a question to the fan company.

Steam from the lower bath can't be exhausted up and out?
Reply With Quote
  #4  
Old 11/2/07, 12:46 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Complex challenge with bath exhaust fan - need help with solution!

I think 2 fans sharing one stack will end up sending a significant portion of the air down to the other fan. Bathroom 1 will steam up bathroom 2
Reply With Quote
  #5  
Old 11/2/07, 1:09 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,020
Default Re: Complex challenge with bath exhaust fan - need help with solution!

Quote:
Originally Posted by Greg Fretwell
I think 2 fans sharing one stack will end up sending a significant portion of the air down to the other fan. Bathroom 1 will steam up bathroom 2
Not with a back flow damper....
Reply With Quote
  #6  
Old 11/2/07, 1:33 PM
jschulte jschulte is offline
Active Poster
 
Join Date: Jul 2006
Location: Moberly, MO
Posts: 447
Please Note: jschulte is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Complex challenge with bath exhaust fan - need help with solution!

Have someone cut a hole in the concrete for you. It's not as bad as it sounds.
Reply With Quote
  #7  
Old 11/4/07, 10:41 AM
William J. Decker's Avatar
William J. Decker William J. Decker is online now
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 6,524
Default Re: Complex challenge with bath exhaust fan - need help with solution!

You don't want to take the exhaust through a soffit if the soffit has vents to the attic.



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
  #8  
Old 11/4/07, 10:48 AM
Bill Featherstone Bill Featherstone is offline
New User
 
Join Date: Nov 2007
Location: NW Arkansas
Posts: 39
Please Note: Bill Featherstone is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Complex challenge with bath exhaust fan - need help with solution!

Quote:
Originally Posted by wdecker
You don't want to take the exhaust through a soffit if the soffit has vents to the attic.
Will,

I do have soffit vents and a ridge cap vent to ventilate the attic. Why should I not exhaust these two baths into the attic and out through the soffit? ... of course, the soffit vent for the bath exhaust would be ducted.

Thanks,

Bill
Reply With Quote
  #9  
Old 11/4/07, 4:20 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,020
Default Re: Complex challenge with bath exhaust fan - need help with solution!

Quote:
Originally Posted by Bill Featherstone
Will,

I do have soffit vents and a ridge cap vent to ventilate the attic. Why should I not exhaust these two baths into the attic and out through the soffit? ... of course, the soffit vent for the bath exhaust would be ducted.

Thanks,

Bill
I don't see a problem with a bathroom vent being installed in a soffit, even if the soffit is being utilized for venting of the attic.

Reply With Quote
  #10  
Old 11/4/07, 6:38 PM
Bill Featherstone Bill Featherstone is offline
New User
 
Join Date: Nov 2007
Location: NW Arkansas
Posts: 39
Please Note: Bill Featherstone is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Complex challenge with bath exhaust fan - need help with solution!

Where can one buy an outlet vent for a soffit application? Seems like all of the exhaust fans at Lowe's and Home Depot are geared for an exterior wall application with the flapper vents, which wouldn't work in a horizontal installation.

What is the bath exhaust setup used in most new houses today?
Reply With Quote
  #11  
Old 11/5/07, 12:26 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,020
Default Re: Complex challenge with bath exhaust fan - need help with solution!

Quote:
Originally Posted by Bill Featherstone
Where can one buy an outlet vent for a soffit application? Seems like all of the exhaust fans at Lowe's and Home Depot are geared for an exterior wall application with the flapper vents, which wouldn't work in a horizontal installation.

What is the bath exhaust setup used in most new houses today?
The covers you are looking for can be found at most hardware stores. If you having a hard time trying to locate one locally, order one on-line here for 12 bucks.
Reply With Quote
  #12  
Old 11/5/07, 2:16 PM
Frank M. Carrio, CMI's Avatar
Frank M. Carrio, CMI Frank M. Carrio, CMI is offline
ESOP Committee Member
 
Join Date: Jan 2004
Posts: 3,968
Default Re: Complex challenge with bath exhaust fan - need help with solution!

[Quote: Bill]
but, what about ... the lower bath? ... the only options I can come up with to vent to the outside is to go through the concrete block (ugh!), go into the space between the two floors and then through the brick wall above (not easy either), or lastly ... [End Quote]
Bill,
Cutting through "concrete block" is very easy. I would strongly recommend that you vent this basement bathroom to the outside wall.

When you pull the permits for this job ask your local town code compliance inspector what they recommend.
  • If you do this renovation without permits you could wind up having to tear it down and "redo it according to code."
Looking for the most current information?
Here is some information that you might find useful;


The 2006 International Residential Code for One and Two Family Dwellings

Definition:
ENVIRONMENTAL AIR.
Air that is conveyed to or from occupied areas through ducts which are not part of the heating or air-conditioning system, such as ventilation for human usage, domestic kitchen range exhaust, bathroom exhaust and domestic clothes dryer exhaust.

IRC, Section Are 303, Light, Ventilation, and Heating.
R303.3 Bathrooms.
Bathrooms, water closet compartments and other similar rooms shall be provided with aggregate glazing area in windows of not less than 3 square feet (0.3 m2), one-half of which must be openable.
Exception: The glazed areas shall not be required where artificial light and a mechanical ventilation system are provided. The minimum ventilation rates shall be 50 cubic feet per minute (24 L/s) for intermittent ventilation or 20 cubic feet per minute (10 L/s) for continuous ventilation. Ventilation air from the space shall be exhausted directly to the outside.

IRC, Chapter 15, SECTION M1507, MECHANICAL VENTILATION
M1507.1 General.
Where toilet rooms and bathrooms are mechanically ventilated, the ventilation equipment shall be installed in accordance with this section.

M1506.2 Recirculation of air.
Exhaust air from bathrooms and toilet rooms shall not be recirculated within a residence or to another dwelling unit and shall be exhausted directly to the outdoors. Exhaust air from bathrooms and toilet rooms shall not discharge into an attic, crawl space or other areas inside the building.

M1507.3 Ventilation rate.
Ventilation systems shall be designed to have the capacity to exhaust the minimum air flow rate determined in accordance with Table M1507.3. Mechanical exhaust capacity of 50 CFM intermittent or 20 CFM continuous

2006, International Mechanical Code
502.18 Specific rooms.
Specific rooms, including bathrooms, locker rooms, smoking lounges and toilet rooms, shall be exhausted in accordance with the ventilation requirements of Chapter 4.

2006, International Property Maintenance Code
Definition:
BATHROOM. A room containing plumbing fixtures including a bathtub or shower.

Chapter 4, Light, Ventilation, and Occupancy Limitations

SECTION 403, VENTILATION
403.2 Bathrooms and toilet rooms.
Every bathroom and toilet room shall comply with the ventilation requirements for habitable spaces as required by Section 403.1, except that a window shall not be required in such spaces equipped with a mechanical ventilation system. Air exhausted by a mechanical ventilation system from a bathroom or toilet room shall discharge to the outdoors and shall not be recirculated.

403.4 Process ventilation.
Where injurious, toxic, irritating or noxious fumes, gases, dusts or mists are generated, a local exhaust ventilation system shall be provided to remove the contaminating agent at the source. Air shall be exhausted to the exterior and not be recirculated to any space.

2006 International Plumbing Code
Definition:
BATHROOM GROUP. A group of fixtures consisting of a water closet, lavatory, bathtub or shower, including or excluding a bidet, an emergency floor drain or both. Such fixtures are located together on the same floor level.

2006 International Building Code
IBC, 1203.4.2.1 Bathrooms.
Rooms containing bathtubs, showers, spas and similar bathing fixtures shall be mechanically ventilated in accordance with the International Mechanical Code.
{See Chapter 15, SECTION M1507 MECHANICAL VENTILATION, M1507.1 General. located above}

2006, ICC Performance Code for Buildings and Facilities
Chapter 9 Moisture, Section 903 Internal Moisture
903.3 Performance requirements.
903.3.1 Excess moisture removal and protection.
An adequate means shall be provided to remove excess moisture or protect the structure from the effects of excess moisture and condensation to all habitable spaces, bathrooms, laundries and other locations where moisture may be generated.

I hope that this information can be of some help.



Signed, Frank Carrio, CMI
Certified Master Inspector & Consultant
Certified Commercial Building Inspector
Certified, WDI Inspector
Founder & Current President, New Hampshire State Chapter NACHI
NACHI, State Representative for Legislative Affairs
Retired: ICC Certified Member
Retired: Code Compliance Inspector.
Retired: ASTM Committee Member
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Anyone smart enough to know a reasonable solution to this problem? Bill Featherstone HVAC 4 12/7/07 12:15 AM
Bath exhaust fan opinion rgiglio Plumbing 6 3/16/07 4:06 PM
Bad Dryer and Bath Fan Venting Jkrt00 HVAC 3 3/14/06 12:07 AM


All times are GMT -4. The time now is 10:51 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts