Doing a 4 unit, older rental unit, today.
(See http://www.nachi.org/forum/showthread.php?t=28565 for more "fun" details.) Normal drop and a 4 meter box on the exterior. 4 SEs (NMT) going to the 4 panels under the back porch basement walkin. 1) Ground was taken from a water pipe that was on the downstream side of one of the 4 water heaters. Suretest had the ground impedance at the best recepticle at 7.3 ohms. The main water line was at the front of the building, some 45 feet away. 2) This "ground electrode condutor" entered the first panel and was connected to the neutral bus (Challanger, 100 amp panels). 3) The neutral bus was bonded to the panel enclosure with one of those little clips. 4) The three remaining panels had the neutral bus bonded to the panel boxes. 5) All the panels were connected with EMT, that was properly bonded to the panel boxes. Was ground continuity proper? Where all the panels "service equipment"? Is the bonding of the panels, only through the EMT enough? Sorry, no pictures. (Hey! Learn to be verbally decriptive.) Comments? Will Decker, CMI ILL License # 450.0002240 Board Certified Master Inspector Decker Home Services, LLC Chicago and Northern Suburban Home Inspections Office: (847) 676-8393 Cell: (847) 609-2345 Home: (847) 673-2702 wjd@DeckerHomeServices.com www.DeckerHomeServices.com Learn, Educate, Serve and have fun doing it! |
If the EMT came through a concentric knock-out, then there should be a grounding bushing attached to one. If it is not concentric, then I believe the connector (with the EMT pushed all the way, so that the hub is in contact) should be adequate.
Will....
also take a look at (depending which NEC version you have) 2002.......250.24(B) 2005 & 2008......250.24(C) It should translate to say that you are O.K. (the bonding actually) |
Seems normal ,from the sound of it.
http://www.nachi.org/forum/showthread.php?t=28565 Jeffrey R. Jonas Critical Eye Property Inspections JRJ Consultants Owatonna, Minnesota Chapter President InterNachi Awards Portal: http://co.nachi.org/inachiawards/
If you really have 7.3 ohms of ground impedence you should defer. This won't clear a fault on a 20 a breaker and will take quite a while to trip a 15. Ground impedence anything above 1 ohm is a potential problem.
BTW this has nothing to do with the ground electrode. It is only testing the neutral to equipment grounding conductor, back through the main bonding jumper. In your case I would look for a loose EMT connector if they don't pull a hard wire ground. Last edited by Greg Fretwell; 5/8/08 at 1:25 AM.. |
Will
The hot side is a big no as it is a danger if some one is to replace the water heater and does no know that it is hooked to the hot side Good call -- This is all wrong -- Yes it works but some one can get hurt on this one Would you wire it this way?? Have a good day rlb |
To be clear, the water pipe, on the hot side of one of the water heaters, was the "grounding electrode conductor connection". I understand that the high ground impedance can have many causes (you would vomit if you saw this place, BTW: All "Chicago Code" approved with regards to the electric, or maybe it was just that the owner was a big wig in the local plumber's union). my point, and question, was about the bonding of the ground to neutral an only the first panel, with neutral bonded to metal on the subsequesnt panes (that little clip) and the EMT bonded between the metals of the subsequent panels. OK, now, so that we are clear, what say you. Will Decker, CMI ILL License # 450.0002240 Board Certified Master Inspector Decker Home Services, LLC Chicago and Northern Suburban Home Inspections Office: (847) 676-8393 Cell: (847) 609-2345 Home: (847) 673-2702 wjd@DeckerHomeServices.com www.DeckerHomeServices.com Learn, Educate, Serve and have fun doing it! |
I still say that part is ok.
No answer from a sparky yet Will? |
You should only have the neutral bonded in the service disconnect enclosure. I am betting when you lift the bond in the other panels your 7 ohms will get worse.
The big problem with EMT is when you have a sloppy installation and they use the raceway for bonding. (no ground wire) |
You only need to ground a service once but when you have the ground occuring in the service disconnect they will usually bring one to each enclosure. That still has nothing to do with the impedence you see with your sure test. It is only looking at the continuity between the neutral conductor and the grounding conductors in the feeder and branch circuits via the bonding jumper.
If your voltage drop number is reasonable the problem is in the EGC or the bonding jumper. You could disconnect the ground electrode entirely and the sure test should still show good ground impedence |