Doing a 4 unit, older rental unit, today.

(See http://www.nachi.org/forum/showthread.php?t=28565 for more "fun" details.)

Normal drop and a 4 meter box on the exterior. 4 SEs (NMT) going to the 4 panels under the back porch basement walkin.

1) Ground was taken from a water pipe that was on the downstream side of one of the 4 water heaters. Suretest had the ground impedance at the best recepticle at 7.3 ohms. The main water line was at the front of the building, some 45 feet away.
2) This "ground electrode condutor" entered the first panel and was connected to the neutral bus (Challanger, 100 amp panels).
3) The neutral bus was bonded to the panel enclosure with one of those little clips.
4) The three remaining panels had the neutral bus bonded to the panel boxes.
5) All the panels were connected with EMT, that was properly bonded to the panel boxes.

Was ground continuity proper? Where all the panels "service equipment"? Is the bonding of the panels, only through the EMT enough?

Sorry, no pictures. (Hey! Learn to be verbally decriptive.)

Comments?



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
  #2  
Old 5/7/08, 8:17 PM
Jeffrey R. Wicklander's Avatar
Jeffrey R. Wicklander Jeffrey R. Wicklander is offline
InterNACHI Member
 
Join Date: Mar 2008
Location: Lake Forest, Il
Posts: 1,117
Default Re: Complicated and need answer

If the EMT came through a concentric knock-out, then there should be a grounding bushing attached to one. If it is not concentric, then I believe the connector (with the EMT pushed all the way, so that the hub is in contact) should be adequate.
Reply With Quote
  #3  
Old 5/7/08, 8:38 PM
Jeffrey R. Wicklander's Avatar
Jeffrey R. Wicklander Jeffrey R. Wicklander is offline
InterNACHI Member
 
Join Date: Mar 2008
Location: Lake Forest, Il
Posts: 1,117
Default Re: Complicated and need answer

Will....
also take a look at (depending which NEC version you have)

2002.......250.24(B)
2005 & 2008......250.24(C)

It should translate to say that you are O.K. (the bonding actually)
Reply With Quote
  #4  
Old 5/7/08, 9:32 PM
relliott's Avatar
relliott relliott is offline
Active Poster
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 8,567
Please Note: relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Complicated and need answer

Seems normal ,from the sound of it.
Reply With Quote
  #5  
Old 5/7/08, 10:41 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 30,554
Default Re: Complicated and need answer

Quote:
Originally Posted by wdecker
Sorry, no pictures. (Hey! Learn to be verbally decriptive.)
Did you lose your camera again?



He who knows nothing is closer to the truth than he whose mind is filled with falsehoods and errors - Thomas Jefferson - Founding Father

The democracy will cease to exist when you take away from those who are willing to work and give to those who would not. Thomas Jefferson

Never underestimate the difficulty of changing false beliefs by facts.
- Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
and
Minnesota Home Inspector

Reply With Quote
  #6  
Old 5/8/08, 1:15 AM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 11,040
Default Re: Complicated and need answer

Quote:
Originally Posted by mlarson
Did you lose your camera again?
The dog ate it

http://www.nachi.org/forum/showthread.php?t=28565
Reply With Quote
  #7  
Old 5/8/08, 2:22 AM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Complicated and need answer

If you really have 7.3 ohms of ground impedence you should defer. This won't clear a fault on a 20 a breaker and will take quite a while to trip a 15. Ground impedence anything above 1 ohm is a potential problem.
BTW this has nothing to do with the ground electrode. It is only testing the neutral to equipment grounding conductor, back through the main bonding jumper. In your case I would look for a loose EMT connector if they don't pull a hard wire ground.

Last edited by Greg Fretwell; 5/8/08 at 2:25 AM..
Reply With Quote
  #8  
Old 5/8/08, 9:03 PM
William J. Decker's Avatar
William J. Decker William J. Decker is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 7,717
Default Re: Complicated and need answer

Quote:
Originally Posted by Greg Fretwell
If you really have 7.3 ohms of ground impedence you should defer. This won't clear a fault on a 20 a breaker and will take quite a while to trip a 15. Ground impedence anything above 1 ohm is a potential problem.
BTW this has nothing to do with the ground electrode. It is only testing the neutral to equipment grounding conductor, back through the main bonding jumper. In your case I would look for a loose EMT connector if they don't pull a hard wire ground.
What about the ground being taken from the hot water side of one of the water heaters?



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
  #9  
Old 5/8/08, 9:40 PM
Richard L. Bennett Richard L. Bennett is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Frostproof, Fl
Posts: 2,307
Default Re: Complicated and need answer

Will

The hot side is a big no as it is a danger if some one is to replace the water heater and does no know that it is hooked to the hot side

Good call -- This is all wrong -- Yes it works but some one can get hurt on this one

Would you wire it this way??

Have a good day

rlb
Reply With Quote
  #10  
Old 5/8/08, 11:19 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Complicated and need answer

Quote:
Originally Posted by wdecker
What about the ground being taken from the hot water side of one of the water heaters?
The ground isn't really "taken" from anywhere. What you observed was either the metallic water piping being bonded, as required, or it was the grounding electrode conductor connection. If this was the grounding electrode conductor connection, it was in a not very desirable location in terms of functionality. If this was simply bonding for the metallic pipework, it's fine. In any case, the location or the quality of the connection to the metallic pipework has absolutely nothing to do with your measured high ground impedance on any given branch circuit. I would also rather suspect a loose EMT joint, but it could also be a loose/marginal main bonding jumper in the serving panel.
Reply With Quote
  #11  
Old 5/9/08, 12:07 AM
William J. Decker's Avatar
William J. Decker William J. Decker is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 7,717
Default Re: Complicated and need answer

Quote:
Originally Posted by Marc D. Shunk
The ground isn't really "taken" from anywhere. What you observed was either the metallic water piping being bonded, as required, or it was the grounding electrode conductor connection. If this was the grounding electrode conductor connection, it was in a not very desirable location in terms of functionality. If this was simply bonding for the metallic pipework, it's fine. In any case, the location or the quality of the connection to the metallic pipework has absolutely nothing to do with your measured high ground impedance on any given branch circuit. I would also rather suspect a loose EMT joint, but it could also be a loose/marginal main bonding jumper in the serving panel.
I understand everything you are saying.

To be clear, the water pipe, on the hot side of one of the water heaters, was the "grounding electrode conductor connection".

I understand that the high ground impedance can have many causes (you would vomit if you saw this place, BTW: All "Chicago Code" approved with regards to the electric, or maybe it was just that the owner was a big wig in the local plumber's union).

my point, and question, was about the bonding of the ground to neutral an only the first panel, with neutral bonded to metal on the subsequesnt panes (that little clip) and the EMT bonded between the metals of the subsequent panels.

OK, now, so that we are clear, what say you.



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
  #12  
Old 5/9/08, 12:48 AM
relliott's Avatar
relliott relliott is offline
Active Poster
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 8,567
Please Note: relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Complicated and need answer

I still say that part is ok.
No answer from a sparky yet Will?
Reply With Quote
  #13  
Old 5/9/08, 2:57 AM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Complicated and need answer

You should only have the neutral bonded in the service disconnect enclosure. I am betting when you lift the bond in the other panels your 7 ohms will get worse.
The big problem with EMT is when you have a sloppy installation and they use the raceway for bonding. (no ground wire)
Reply With Quote
  #14  
Old 5/9/08, 9:10 AM
William J. Decker's Avatar
William J. Decker William J. Decker is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 7,717
Default Re: Complicated and need answer

Quote:
Originally Posted by Greg Fretwell
You should only have the neutral bonded in the service disconnect enclosure. I am betting when you lift the bond in the other panels your 7 ohms will get worse.
The big problem with EMT is when you have a sloppy installation and they use the raceway for bonding. (no ground wire)
That was part of my point, Greg. All four panels had disconnects and all four were, for your purposes, were being treated and service equipment. i would have thought that, in such a case, they would have run the GEC into each panel and bonded it directly.



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
  #15  
Old 5/9/08, 11:27 AM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Complicated and need answer

You only need to ground a service once but when you have the ground occuring in the service disconnect they will usually bring one to each enclosure. That still has nothing to do with the impedence you see with your sure test. It is only looking at the continuity between the neutral conductor and the grounding conductors in the feeder and branch circuits via the bonding jumper.
If your voltage drop number is reasonable the problem is in the EGC or the bonding jumper. You could disconnect the ground electrode entirely and the sure test should still show good ground impedence
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT -4. The time now is 7:25 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts