Hey guys
I inspected a condominium town home (late 1980's) yesterday and the panel did not have a main disconnect nor a grounding conductor coming off the neutral bar. Also the dryer circuit was protected by 40amp breaker but the wire was awg10. I assume that the main disconnect and grounding conductor are in a separate utility space with the meter. Questions: 1. Would my assumption be correct? Is this a common arrangement for condos? If so how does bonding of hot and cold water pipes work in this case? 2. Is there some kind of exception to the rule for a dryer circuit that it can be overfused? I have seen this arrangement in a number of service panels lately. Any advice is appreciated. Craig |
|
#2
|
||||
|
||||
|
1) Common for condos, yes. Bondinding of components is typically near the service equipment with jumpers at water heaters.
2) No exception for 240V dryer receptacles (that I am aware of). Paul? IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#3
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
3 wire or 4 wire feeder?
|
|
#4
|
|||
|
|||
|
Please Note:
cbarrows is a non-member guest and is in no way affiliated with InterNACHI or its members.
The feeder to the panel has 2 hot, 1 Neutral and a bare copper ground.
|
|
#5
|
|||
|
|||
|
Please Note:
cbarrows is a non-member guest and is in no way affiliated with InterNACHI or its members.
Thanks Jeffrey.
|
|
#6
|
||||
|
||||
|
Jeff,
Yes, you are correct in that the grounding will take place at the FIRST point of Service Disconnection probably at the main panels location for the condo's in the mechanical room. I also suggest they make sure the proper wiring is to the " Remote Distrubution Panels" in the condo units themselves. On the Dryer wiring, no exceptions on branch circuits for a # 10 AWG to be protected by anything other than a 30A breaker or smaller...in this example. While smaller would most certainly cause a TRIP issue, you can't fix it by placing it on a larger breaker....ranges can be on 40 or 50A breakers in certain case...but not in regards to a 30A appliance as stated. Paul W. Abernathy,CMI,CPI,CME National Electrical Code Expert Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru Weekly Chat on Wednesdays -7:30 PM E.S.T * Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections" 2007 InterNACHI Member of the Year |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| National Electrical Code Information and Discussion | jtedesco1 | Electrical Inspections | 50 | 6/15/10 8:28 PM |
| Panel Inspection Safety | roconnor | Electrical Inspections | 10 | 9/24/06 10:02 PM |
| Bad electrical problem | Pest Guy | Electrical Inspections | 4 | 1/20/06 10:26 PM |