I inspected a condominium town home (late 1980's) yesterday and the panel did not have a main disconnect nor a grounding conductor coming off the neutral bar. Also the dryer circuit was protected by 40amp breaker but the wire was awg10. I assume that the main disconnect and grounding conductor are in a separate utility space with the meter. Questions: 1. Would my assumption be correct? Is this a common arrangement for condos? If so how does bonding of hot and cold water pipes work in this case? 2. Is there some kind of exception to the rule for a dryer circuit that it can be overfused? I have seen this arrangement in a number of service panels lately. Any advice is appreciated. Craig |
|
#2
|
||||
|
||||
|
1) Common for condos, yes. Bondinding of components is typically near the service equipment with jumpers at water heaters.
2) No exception for 240V dryer receptacles (that I am aware of). Paul? IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ℠ Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#3
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
3 wire or 4 wire feeder?
|
|
#4
|
|||
|
|||
|
Please Note:
cbarrows is a non-member guest and is in no way affiliated with InterNACHI or its members.
The feeder to the panel has 2 hot, 1 Neutral and a bare copper ground.
|
|
#5
|
|||
|
|||
|
Please Note:
cbarrows is a non-member guest and is in no way affiliated with InterNACHI or its members.
Thanks Jeffrey.
|
|
#6
|
||||
|
||||
|
Jeff,
Yes, you are correct in that the grounding will take place at the FIRST point of Service Disconnection probably at the main panels location for the condo's in the mechanical room. I also suggest they make sure the proper wiring is to the " Remote Distrubution Panels" in the condo units themselves. On the Dryer wiring, no exceptions on branch circuits for a # 10 AWG to be protected by anything other than a 30A breaker or smaller...in this example. While smaller would most certainly cause a TRIP issue, you can't fix it by placing it on a larger breaker....ranges can be on 40 or 50A breakers in certain case...but not in regards to a 30A appliance as stated. Paul W. Abernathy,CMI,CEI,CEPE NECŪ Consultant/Columnist www.twitter.com/ElectricalGuru - ICC & IAEI Certified Electrical Inspector - ICC & IAEI Certified Electrical Plans Examiner - Look for my article in the Nov/Dec 2009 IAEI Magazine - 2007 "Top Gun" Winner - Mike Holt Enterprises " visit www.TheElectricalGuru.com Today !" |
![]() |