I inspected a house with an unfinished garage and there were some branch wiring (romex) running along the top plate (8 to 9 feet high)of the rafters. A few of the branch wires were run down the wall to an exterior mounted receptacle box. Does all the exposed wire need conduit or just the wire with in reach.
Reply With Quote
  #2  
Old 4/10/08, 4:03 AM
Mark Jones Mark Jones is offline
InterNACHI Member
 
Join Date: Jan 2006
Location: Roundlake Beach, IL
Posts: 240
Default Re: conduit

I don't know what the code is in Fl., but it wouldn't matter to me anyway. I would recommend for safety reasons that the wire coming down the wall be protected. As long as the wire above is out of the way and fastened correctly it would probably be fine.

Mark Jones



Mark Jones
Allmark Home Inspection Services Inc.
Serving all of Northern Illinois, Vernon Hills, Libertyville, Gurnee, Fox Lake, Round Lake

Phone: 847 651 2053
E-Mail: AllmarkInspect@aol.com

www.AllmarkHomeInspection.com
Reply With Quote
  #3  
Old 4/10/08, 7:49 AM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Cassville, MO
Posts: 13,647
Default Re: conduit

Conduit. Protects it from rodent damage.
Reply With Quote
  #4  
Old 4/10/08, 7:53 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,022
Default Re: conduit

Quote:
Originally Posted by pkusic
I inspected a house with an unfinished garage and there were some branch wiring (romex) running along the top plate (8 to 9 feet high)of the rafters. A few of the branch wires were run down the wall to an exterior mounted receptacle box. Does all the exposed wire need conduit or just the wire with in reach.
If Romex can be mechanically damaged, I recommend conduit protection. Most exterior Romex needs a conduit pipe for protection.

An unfinished garage in Massachusetts doesn't require conduit protection, so long as it's properly secured.
Reply With Quote
  #5  
Old 4/10/08, 9:53 AM
Speedy Petey Speedy Petey is offline
Active Poster
 
Join Date: Jul 2006
Posts: 1,294
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: conduit

Quote:
Originally Posted by jbushart
Conduit. Protects it from rodent damage.
So in attics, crawlspaces and wall cavities rodents are not a problem????
Reply With Quote
  #6  
Old 4/10/08, 9:54 AM
Speedy Petey Speedy Petey is offline
Active Poster
 
Join Date: Jul 2006
Posts: 1,294
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: conduit

Quote:
Originally Posted by dvalley
An unfinished garage in Massachusetts doesn't require conduit protection, so long as it's properly secured.
Yup, same here.
Reply With Quote
  #7  
Old 4/10/08, 10:36 AM
Mike Whitt's Avatar
Mike Whitt Mike Whitt is offline
Active Poster
 
Join Date: Sep 2005
Location: North Carolina
Posts: 474
Please Note: Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: conduit

Quote:
Originally Posted by dvalley
Most exterior Romex needs a conduit pipe for protection.
Not trying to sound smart but feel the need to point out that Nonmetallic Cable (Romex) is not allowed to be installed on the exterior at all. It can not be installed exposed or in a conduit, it cain't be installed outside at all.
Reply With Quote
  #8  
Old 4/10/08, 10:53 AM
brian winkle brian winkle is offline
Active Poster
 
Join Date: Sep 2005
Location: Arizona
Posts: 454
Please Note: brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: conduit

Quote:
Originally Posted by Mike Whitt
Not trying to sound smart but feel the need to point out that Nonmetallic Cable (Romex) is not allowed to be installed on the exterior at all. It can not be installed exposed or in a conduit, it cain't be installed outside at all.
Often I get called out to "put the exposed Romex in conduit". Sometimes the realtor and seller think I can just waltz in and magically slip some conduit onto the Romex in twenty minutes or so. Many are upset when I tell them the only fix is to tear it all out and do it right.

Plus, it would probably take longer to do it wrong.
Reply With Quote
  #9  
Old 4/10/08, 11:00 AM
bkelly1's Avatar
bkelly1 bkelly1 is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: Rives, TN
Posts: 1,757
Please Note: bkelly1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: conduit

No conduit here as long as it is properly secured and is wood framing. Rodents have nothing to do with it here.
Reply With Quote
  #10  
Old 4/10/08, 11:46 AM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: conduit

It all comes down to whether it is "subject to physical damage" and that is always in the opinion of the AHJ. Most Florida AHJs want protection if it is below 6'6 or so but that is not written anywhere. There are NO local amendments in Florida, only local opinions.
Reply With Quote
  #11  
Old 4/10/08, 12:23 PM
Speedy Petey Speedy Petey is offline
Active Poster
 
Join Date: Jul 2006
Posts: 1,294
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: conduit

I read this as running down the inside of the garage into the back of an exterior receptacle.
Am I wrong?
Reply With Quote
  #12  
Old 4/10/08, 12:40 PM
Thomas H. Dietrich's Avatar
Thomas H. Dietrich Thomas H. Dietrich is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: conduit

Sounds hocky to me. Your description is too vague.

Is the NM being run through bored holes?
Is the NM running along any 'surfaces'?
Is the NM exposed to any possible 'realistic' physical damage?

Photos please.

tom
Reply With Quote
  #13  
Old 4/10/08, 12:41 PM
Jim Port Jim Port is online now
Active Poster
 
Join Date: Jul 2007
Location: Maryland
Posts: 285
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: conduit

That's the way it sounds to me Petey.
Reply With Quote
  #14  
Old 4/10/08, 3:07 PM
Mike Whitt's Avatar
Mike Whitt Mike Whitt is offline
Active Poster
 
Join Date: Sep 2005
Location: North Carolina
Posts: 474
Please Note: Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: conduit

Quote:
Originally Posted by pkusic
A few of the branch wires were run down the wall to an exterior mounted receptacle box.

Quote:
Originally Posted by Speedy Petey
I read this as running down the inside of the garage into the back of an exterior receptacle.
Quote:
Originally Posted by Speedy Petey
Am I wrong?

Quote:
Originally Posted by Jim Port
That's the way it sounds to me Petey.


After reading it again I may be the one that don’t know how to read!
Reply With Quote
  #15  
Old 4/10/08, 3:10 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,022
Default Re: conduit

Quote:
Originally Posted by Mike Whitt
Not trying to sound smart but feel the need to point out that Nonmetallic Cable (Romex) is not allowed to be installed on the exterior at all. It can not be installed exposed or in a conduit, it cain't be installed outside at all.
Romex is allowed on the exterior, depending upon location and whether or not it's encased in conduit if sunlight becomes an issue.

In other words, Romex can be used under a deck as long it's properly secured. No sunlight.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Dwelling and Commercial Electrical Equipment jtedesco1 Electrical 4 1/10/08 7:46 AM
Conduit as Ground cbuell Electrical 12 4/16/07 7:18 PM
Should this be in conduit kblair1 Electrical 18 12/26/06 5:50 PM
NACHI Chapters Free Electrical Training Available jtedesco1 Education 5 8/11/06 5:46 PM
Conduit psmothers Electrical 2 6/3/06 1:05 PM


All times are GMT -4. The time now is 4:32 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts