Old 4/10/08, 3:25 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 746
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: conduit

Quote:
Originally Posted by dvalley
Romex is allowed on the exterior, depending upon location and whether or not it's encased in conduit if sunlight becomes an issue.

In other words, Romex can be used under a deck as long it's properly secured. No sunlight.
Sorry David,

NM is not allowed outside whether it is in conduit or not. 334.10(A)(1) cleary states "For both exposed and concealed work in normally dry locations" and 334.12(10) TYpe NM shall not be used as follows d. states " Where exposed or subject to excessive moisture or dampness".

A wet location is defined in Article 100 as "Installations underground or in cocrete slabs or masonry in contact with the earth; in locations subject to saturation with water or other liquids, such as vehicle washing areas; and in unprotected locations exposed to weather"
Reply With Quote
  #17  
Old 4/10/08, 4:05 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,684
Default Re: conduit

Quote:
Originally Posted by Jim Port
Sorry David,

NM is not allowed outside whether it is in conduit or not. 334.10(A)(1) cleary states "For both exposed and concealed work in normally dry locations" and 334.12(10) TYpe NM shall not be used as follows d. states " Where exposed or subject to excessive moisture or dampness".

A wet location is defined in Article 100 as "Installations underground or in cocrete slabs or masonry in contact with the earth; in locations subject to saturation with water or other liquids, such as vehicle washing areas; and in unprotected locations exposed to weather"
I don't do code.

If I see a romex installed properly and protected on the exterior (which I do many times) under decks, sheds, utility closets, etc., I leave it be.

The only time I call it out is if there is an issue with trhe actual placement and is susceptible to mechanical damage or sunlight damage or improperly used for underground burial.
Reply With Quote
  #18  
Old 4/10/08, 4:16 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 746
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: conduit

NM outside is not properly installed. The jacket is not sunlight resistant either.

If you don't "do code" how do you know what a proper installation would be?
Reply With Quote
  #19  
Old 4/10/08, 4:18 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,684
Default Re: conduit

Quote:
Originally Posted by Jim Port
NM outside is not properly installed. The jacket is not sunlight resistant either.

If you don't "do code" how do you know what a proper installation would be?
Like I said, if it looks safe to me...It passes.

I'm done.
Reply With Quote
  #20  
Old 4/10/08, 4:28 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: conduit

Quote:
Originally Posted by dvalley
The only time I call it out is if there is an issue with trhe actual placement and is susceptible to mechanical damage or sunlight damage or improperly used for underground burial.
Just add excessive moisture and you are OK.


Quote:
Originally Posted by Jim Port
If you don't "do code" how do you know what a proper installation would be?
I agree.


I personally think the whole "I don't do code" mentality meeds some re-thinking.
Without knowing the basic codes and procedures all you are doing is giving your opinion. Which in this case is flawed.
Unfortunately, folks pay a LOT of money, an put a LOT of stock in that "opinion".
Reply With Quote
  #21  
Old 4/10/08, 4:52 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 746
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: conduit

Quote:
Originally Posted by Speedy Petey
Without knowing the basic codes and procedures all you are doing is giving your opinion. Which in this case is flawed.
Unfortunately, folks pay a LOT of money, and put a LOT of stock in that "opinion".
Maybe all you need to do is to spend a night at Holiday Inn.

Without a knowledgeable reference as to acceptable practices how are you to properly judge during an inspection?
Reply With Quote
  #22  
Old 4/10/08, 4:56 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 746
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: conduit

Quote:
Originally Posted by dvalley
I don't do code.

If I see a romex installed properly and protected on the exterior (which I do many times) under decks, sheds, utility closets, etc., I leave it be.

The only time I call it out is if there is an issue with trhe actual placement and is susceptible to mechanical damage or sunlight damage or improperly used for underground burial.
How would you know if the actual placement was acceptable or that it was not rated for underground burial? These conditions ARE what is called out in the Code.
Reply With Quote
  #23  
Old 4/10/08, 5:01 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,684
Default Re: conduit

Quote:
Originally Posted by Jim Port
How would you know if the actual placement was acceptable or that it was not rated for underground burial? These conditions ARE what is called out in the Code.
I'm not color blind and I can read the print on the sheathing....Name:  headbang.gif
Views: 79
Size:  983 Bytes
Reply With Quote
  #24  
Old 4/10/08, 5:09 PM
Mike Whitt's Avatar
Mike Whitt Mike Whitt is offline
Unmoderated Guest
 
Join Date: Sep 2005
Location: North Carolina
Posts: 477
Please Note: Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: conduit

Quote:
Originally Posted by dvalley
Quote:
Originally Posted by Mike Whitt
Not trying to sound smart but feel the need to point out that Nonmetallic Cable (Romex) is not allowed to be installed on the exterior at all. It can not be installed exposed or in a conduit, it cain't be installed outside at all.
Romex is allowed on the exterior, depending upon location and whether or not it's encased in conduit if sunlight becomes an issue. In other words, Romex can be used under a deck as long it's properly secured. No sunlight.


Again not trying to sound smart or belittling but you wouldn’t last long in NC if you didn’t call it out knowing that it is wrong.

With all the talk about law suits on this forum I would think that you would have a concern about something that you know is wrong and want to call it out.

NM cable is not allowed in a wet location and exposed to weather is a wet location.
Reply With Quote
  #25  
Old 4/10/08, 5:15 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,684
Default Re: conduit

Quote:
Originally Posted by Mike Whitt

Again not trying to sound smart or belittling but you wouldn’t last long in NC if you didn’t call it out knowing that it is wrong.

With all the talk about law suits on this forum I would think that you would have a concern about something that you know is wrong and want to call it out.

NM cable is not allowed in a wet location and exposed to weather is a wet location.
Thank you kindly. I don't come here to argue code.

That's for the other guys who get bored with their lives.
Reply With Quote
  #26  
Old 4/10/08, 6:13 PM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Southwest Missouri
Posts: 20,490
Default Re: conduit

Quote:
Originally Posted by Mike Whitt

Again not trying to sound smart or belittling but you wouldn’t last long in NC if you didn’t call it out knowing that it is wrong.

With all the talk about law suits on this forum I would think that you would have a concern about something that you know is wrong and want to call it out.

NM cable is not allowed in a wet location and exposed to weather is a wet location.
I inspected a commercial facility last month where they had run NM from the service box for an outdoor sign....buried under about three to six inches of dirt and mud...for a length of 50 feet to a parking lot light.

NM has some very interesting uses in creative hands.



James H. Bushart

Professional Building Analyst, BPI
Missouri, Kansas and Arkansas
314-803-2167
Inspecting in Aurora, Branson, Carthage, Granby, Joplin, Kimberling City, Monett, Mount Vernon, Neosho, Nixa, Purdy, Reed Spring, Republic, Springfield and surrounding areas.

Reply With Quote
  #27  
Old 4/10/08, 6:16 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,684
Default Re: conduit

Quote:
Originally Posted by jbushart
I inspected a commercial facility last month where they had run NM from the service box for an outdoor sign....buried under about three to six inches of dirt and mud...for a length of 50 feet to a parking lot light.

NM has some very interesting uses in creative hands.
Yup...
Reply With Quote
  #29  
Old 4/10/08, 6:52 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: conduit

Romex cannot be used under the following conditions, or in the following locations:

Where exposed to corrosive fumes or vapors

Where embedded in masonry, concrete, adobe, fill, or plaster

In a shallow chase in masonry, concrete, or adobe and covered with plaster, adobe, or similar finish

In wet or damp locations


.

Last edited by jtedesco1; 4/11/08 at 6:20 AM..
Reply With Quote
  #30  
Old 4/10/08, 7:32 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 746
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: conduit

Joe,

As long as it looks good it is Ok to run NM outside.

Having to know all that Code stuff really slows down an inspection.

I think I just found out how to save tons of time on my next rough-in.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Dwelling and Commercial Electrical Equipment jtedesco1 Electrical Inspections 4 1/10/08 7:46 AM
Conduit as Ground cbuell Electrical Inspections 12 4/16/07 7:18 PM
Should this be in conduit kblair1 Electrical Inspections 18 12/26/06 5:50 PM
NACHI Chapters Free Electrical Training Available jtedesco1 Inspection Education & Training 5 8/11/06 5:46 PM
Conduit psmothers Electrical Inspections 2 6/3/06 1:05 PM


All times are GMT -4. The time now is 9:57 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts