Default Re: conduit

Quote:
Originally Posted by dvalley
So you are assuming that this was suppose to go into a weatherproof box. And if this location is not outside, then my name is Dick Tracy.
How are you Dick. Nice to meet you.

NM-B CAN most certainly come into the BACK of a properly sealed weathproof box installed out doors.
This installation DOES NOT expose any part of the cable to sunlight, excessive moisture or weather. IF installed properly!
Reply With Quote
  #47  
Old 4/12/08, 4:04 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: conduit

Quote:
Originally Posted by dvalley
So that explains why I see this type of wiring on the exterior.....It's UF NM!!!
Yes, UF cable IS sunlight and moisture resistant. It is also a type of NM cable.

Don't be fooled by grey or white either. I still have some 14/2 UF cable that is white, not grey.
The ONLY way to be sure what you are looking at is to read the sheath.
Reply With Quote
  #48  
Old 4/12/08, 4:06 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: conduit

Quote:
Originally Posted by Greg Fretwell
I think the main problem with NM outside is the paper packing around the wires. It can wick water up into the cable and that might end up in a box inside.

MC uses a plastic wrapper so the aluminum stuff is usually "wet" listed

UF has no packing at all
UF-B/3W/W/GRND

Last edited by jtedesco1; 6/12/08 at 5:39 PM..
Reply With Quote
  #49  
Old 4/12/08, 5:16 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,684
Default Re: conduit

Quote:
Originally Posted by Mike Whitt
Not trying to sound smart but feel the need to point out that Nonmetallic Cable (Romex) is not allowed to be installed on the exterior at all. It can not be installed exposed or in a conduit, it cain't be installed outside at all.
Mike,

Did you see Speedy's post....


Quote:
Originally Posted by speedy
NM-B CAN most certainly come into the BACK of a properly sealed weathproof box installed out doors.
This installation DOES NOT expose any part of the cable to sunlight, excessive moisture or weather. IF installed properly!
Reply With Quote
  #50  
Old 4/12/08, 10:23 PM
Joe Farsetta's Avatar
Joe Farsetta Joe Farsetta is offline
ESOP Committee Member
 
Join Date: Oct 2002
Location: Pearl River, NY
Posts: 4,107
Default Re: conduit

I the photo Joe T supplied, is the ground insulated or not.

Here's the next question:

Can individual conductors installed in conduit be installed in exterior and/or damp locations. If so, then why?

This goes back to my question/statement regarding if romex can be installed in exterior or damp locations. If it is not suited, even when installed in conduit, then I ask why? Someone mentioned paper wrapping, which goes to my point regarding the ground conductor having its own insulation.
Reply With Quote
  #51  
Old 4/12/08, 11:28 PM
Mike Whitt's Avatar
Mike Whitt Mike Whitt is offline
Unmoderated Guest
 
Join Date: Sep 2005
Location: North Carolina
Posts: 477
Please Note: Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: conduit

Quote:
Originally Posted by jfarsetta
I the photo Joe T supplied, is the ground insulated or not.

Here's the next question:

Can individual conductors installed in conduit be installed in exterior and/or damp locations. If so, then why?

This goes back to my question/statement regarding if romex can be installed in exterior or damp locations. If it is not suited, even when installed in conduit, then I ask why? Someone mentioned paper wrapping, which goes to my point regarding the ground conductor having its own insulation.
To be installed in a wet location and outside is a wet location the conductor must comply with this section

310.8(C) Wet Locations. Insulated conductors and cables used in wet locations shall be
(1) Moisture-impervious metal-sheathed;
(2) Types MTW, RHW, RHW-2, TW, THW, THW-2, THHW, THHW-2, THWN, THWN-2, XHHW, XHHW-2, ZW; or
(3) Of a type listed for use in wet locations.
Reply With Quote
  #52  
Old 4/12/08, 11:29 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: conduit

Individual conductors can be installed in conduit outdoors if it is rated for it.
MOST new(er) THHN wiring is also dual rated as THHN/THWN. The "W" stands for wet.
**EDIT - Or better yet read Mike's post above.

Again, the point of an "insulated" ground is not the point. UF cable has a bare ground, but it is within the sheath.

As to specifically why NM-B cannot be used wet, that is a call for the Mfg to make. I never really gave it a thought, I just always knew it was always a no-no.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Dwelling and Commercial Electrical Equipment jtedesco1 Electrical Inspections 4 1/10/08 7:46 AM
Conduit as Ground cbuell Electrical Inspections 12 4/16/07 7:18 PM
Should this be in conduit kblair1 Electrical Inspections 18 12/26/06 5:50 PM
NACHI Chapters Free Electrical Training Available jtedesco1 Inspection Education & Training 5 8/11/06 5:46 PM
Conduit psmothers Electrical Inspections 2 6/3/06 1:05 PM


All times are GMT -4. The time now is 9:50 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts