Default Conduit as Ground

This is what I don't like about using the conduit at the ground to remote distribution panels
Attached Thumbnails
conduit-ground-dulitz-116.jpg  
Reply With Quote
  #2  
Old 4/12/07, 8:27 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Conduit as Ground

That is what I don't like about using the conduit as a ground regardless of the application.
Reply With Quote
  #3  
Old 4/12/07, 8:43 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Conduit as Ground

That's a hack job, anyhow. You're not supposed to use couplings on bends. They're not designed for that.

Reference NEMA Standards Publication FB 2.10-2003, "Selection and Installation Guidelines For Fittings for Use With Non-Flexible Metallic Conduit or Tubing (Rigid Metal Conduit, Intermediate Metal Conduit, and Electrical Metallic Tubing)". Section 1.4 covers the proper use and installation of EMT couplings.

Free download:
http://www.nema.org/stds/fb2-10.cfm#download
Reply With Quote
  #4  
Old 4/12/07, 9:13 PM
cbuell's Avatar
cbuell cbuell is offline
Active Poster
 
Join Date: Feb 2004
Location: Shorline, WA
Posts: 380
Please Note: cbuell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Conduit as Ground

This was an 8 unit condo conversion---Zinsco everything (originally)----conduit installed 1966. I think it came apart when they pulled new wires to the replaced panels.
Reply With Quote
  #5  
Old 4/12/07, 11:22 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Conduit as Ground

Granted that is a CRAPPY install and simply wrong......also just a good chance for me to JAB at Chicago and their "overzelous" love for all CONDUIT installations yet "SNUB" a nose at Non-Metallic Cable.............



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #6  
Old 4/14/07, 9:45 PM
jbreazeale jbreazeale is offline
Active Poster
 
Join Date: Aug 2006
Location: Sardis, MS
Posts: 618
Please Note: jbreazeale is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Conduit as Ground

Marc, you have once again beaten me to the punch!! Conduit couplings in bends are a no-no. What'a amazing is that they actually seemed to have gotten the bend made accurately!

So, am I to understand that Chicago requires all wiring run in conduit? I have heard that some jurisdictions "up there" require this. I suppose they think that it's a more durable installation.
Reply With Quote
  #7  
Old 4/15/07, 12:12 AM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Conduit as Ground

I bet that is where the wire stalled, they cut it, pulled the wire and put it back together. (another violation)
Reply With Quote
  #8  
Old 4/15/07, 12:24 AM
William J. Decker's Avatar
William J. Decker William J. Decker is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 7,717
Default Re: Conduit as Ground

Quote:
Originally Posted by pabernathy
Granted that is a CRAPPY install and simply wrong......also just a good chance for me to JAB at Chicago and their "overzelous" love for all CONDUIT installations yet "SNUB" a nose at Non-Metallic Cable.............
Yeah! Gloat, you Hillbilly, you

But we gotta live here.



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
  #9  
Old 4/16/07, 9:20 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Conduit as Ground

Quote:
Originally Posted by wdecker
Yeah! Gloat, you Hillbilly, you

But we gotta live here.
lol..what....?...you think VA is the only state with Non-Metalic Cable....ok Chicago-Man.....



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #10  
Old 4/16/07, 1:15 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Conduit as Ground

Thank god for non-metalic wiring methods. EMT becomes a rusty mess with exposed conductors in a few years down here on the beach.
Reply With Quote
  #11  
Old 4/16/07, 2:11 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Conduit as Ground

oh no doubt greg.....every year we vacation to Nags Head and the EMT that is exposed down their is a MESS......rusty as all get out...



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #12  
Old 4/16/07, 2:45 PM
mthomas2 mthomas2 is offline
Active Poster
 
Join Date: Oct 2005
Location: Evanston, IL
Posts: 703
Please Note: mthomas2 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Conduit as Ground

Part of the logic for requiring conduit in my town (a suburb north of Chicago) is that it's a lot easier to maintain and upgrade such circuits. And assuming pull-boxes were installed where required, its true. My own house is a good example - I would really like to pull a third kitchen outlet circuit. Hard to pull new wire through BX, however...
Reply With Quote
  #13  
Old 4/16/07, 7:18 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Conduit as Ground

lol....I have no problem "FISHING" up a NM Cable....lol....do it all the time....



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 4:56 PM
Ground Wires Inside a Panel mveitenhans Electrical Inspections 13 10/29/06 12:39 PM
NACHI Chapters Free Electrical Training Available jtedesco1 Inspection Education & Training 5 8/11/06 5:46 PM
Electrical Inspection Training for Home Inspectors jtedesco1 Inspection Education & Training 6 4/27/06 11:43 PM
Harmonized Ground Fault Circuit Interrupters jtedesco1 Electrical Inspections 5 3/21/06 9:48 AM


All times are GMT -4. The time now is 4:15 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts