Default Connection at SEC

I observed one of the SEC wires. Would this be the Grounded or Non grounded conductor?

There are several strands not connecting the lug and one is actually touching the nuetral ground bar & would like to inquire as to if this may be a potential safety concern.

There is enough wire to cut & attach properly.
Attached Thumbnails
connection-sec-89807-024-small-.jpg.jpg
Views:	67
Size:	61.7 KB
ID:	8421  
Reply With Quote
  #2  
Old 1/15/07, 5:10 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Connection at SEC

That is a really crappy attempt to connect the grounded neutral.
Reply With Quote
  #3  
Old 1/15/07, 5:47 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Connection at SEC

Agreeeeeed........also looks like possibly some of the Ungrounded conductor in that lug on the right was a snip and tuck job.....look real close but it could be my eyes....dang pictures.

And of course the 408.21 issues going on with that buss bar...but I agree....



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #4  
Old 1/15/07, 6:15 PM
cbuell's Avatar
cbuell cbuell is offline
Active Poster
 
Join Date: Feb 2004
Location: Shorline, WA
Posts: 380
Please Note: cbuell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Connection at SEC

Hey Paul,
2005NEC has no 408.21? Are you referring to the double tapped neutrals?
Reply With Quote
  #5  
Old 1/15/07, 6:35 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Connection at SEC

ahh....thats the 2002 NEC number.....might have redone it in 2005...I only have my 2002 on this PC at the office...lol....someone translate the Section please...lol......

Yes, refers to the double tapping of the grounded conductor.

408.21 Grounded Conductor Terminations.



Each grounded conductor shall terminate within the panelboard
in an individual terminal that is not also used for another
conductor.


Exception: Grounded conductors of circuits with parallel




conductors shall be permitted to terminate in a single terminal
if the terminal is identi
fied for connection of more than one conductor.


lol...I am SOOOO 2002 NEC right now as I am gearing up for the NEC Update 2002 classes around VA....so I have 2002 NEC on the brain.

For those using 2005 NEC - Section 408.41....Enjoy !




Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year

Last edited by pabernathy; 1/15/07 at 6:55 PM..
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 4:56 PM
Grounding rod connection from meter box fbartlo Electrical Inspections 37 7/28/07 1:30 PM
Looking for comments on this service ground wire connection cbuell Electrical Inspections 6 2/8/07 7:27 PM
Flue vent connection for water heater hspinnler Plumbing Inspections 11 5/11/06 10:56 PM
Is this connection correct? mpeterson Electrical Inspections 9 3/27/06 11:45 PM


All times are GMT -4. The time now is 5:30 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts