  #1  
Old 3/15/11, 4:58 PM
Gary T. Heller's Avatar
Gary T. Heller Gary T. Heller is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: Peoria, AZ
Posts: 461
Default Copper/Alu same breaker

My comment in the report is as follows.

The 220 volt breaker feeding the water heater has both aluminum and copper conductors. This is not a common practice but these conductors are sized properly for the 30 amp breaker they are connected to and the breaker is rated for both copper and aluminum.

What say you?
Attached Thumbnails
copper-alu-same-breaker-004.jpg  
Reply With Quote
Need a home inspection in Nevada? Check out InterNACHI's listing of Nevada certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 3/15/11, 5:37 PM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Copper/Alu same breaker

Are these in a raceway? What size is the Al conductor?
Reply With Quote
  #3  
Old 3/15/11, 5:45 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: Copper/Alu same breaker

Kind of odd 2 separate types of conductors serving the same circuit outlet .



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #4  
Old 3/15/11, 6:05 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Copper/Alu same breaker

It might be a shadow but the CU looks larger than the AL. You also might have issues if all conductors of the circuit are not run together.
Reply With Quote
  #5  
Old 3/15/11, 6:45 PM
KEVIN WOOD's Avatar
KEVIN WOOD KEVIN WOOD is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 3,106
Default Re: Copper/Alu same breaker

Well done Jim.
I was wondering who would catch this one.



THE RIGHT TRAK
CIAQP, IAC2
Certified Master Inspector
kwoodinspections@hotmail.com
www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ
www.linkedin.com/in/kevinwoodiaq
OOVOO account kwoodinspections
Cell: 705-971-2096
Ph : 705-946-2676
Reply With Quote
  #6  
Old 3/15/11, 7:21 PM
Gary T. Heller's Avatar
Gary T. Heller Gary T. Heller is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: Peoria, AZ
Posts: 461
Default Re: Copper/Alu same breaker

They are not in a raceway. The Copper is stranded and larger than the solid Aluminum.
Reply With Quote
  #7  
Old 3/15/11, 7:45 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,194
Default Re: Copper/Alu same breaker

Quote:
Originally Posted by gheller View Post
They are not in a raceway. The Copper is stranded and larger than the solid Aluminum.
Screech..... <<<slamming on the brakes>>>

If that is actually 'solid' aluminum, now I have an issue with it. (Other than what was said above). That would be enough for me to call it out.

Are you sure? Looks like strand aluminum from here.
Reply With Quote
  #8  
Old 3/15/11, 7:46 PM
Jeffrey Moore Jeffrey Moore is offline
InterNACHI Member
 
Join Date: Feb 2008
Location: Mesa, AZ
Posts: 282
Default Re: Copper/Alu same breaker

what size are the wires as the Al should be larger if the copper is properly sized?


Is this a situation where the breaker has been changed at one time?



Jeff Moore
www.quantumhomeinspections.com
Flir (ITC) Level II Thermographer
Mesa, AZ
Reply With Quote
  #9  
Old 3/15/11, 8:11 PM
Gary T. Heller's Avatar
Gary T. Heller Gary T. Heller is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: Peoria, AZ
Posts: 461
Default Re: Copper/Alu same breaker

The aluminum doesn't need to be larger than the copper. The copper is larger than what it needs to be. The aluminum needs to be one size larger than it would have to be if it were copper.

This is a fairly new Cutler Hammer panel. It appears to be proffessionaly installed on a home built in 1978. I cannot understand why anyone would use two differnet conductors. I stopped by the house today and did the panel and roof. I'm going back tomorrow to do the interior and the pool.

I appreciate all the comments. Jim...can you expand on the issues if the circuits are not run together?
Reply With Quote
  #10  
Old 3/15/11, 8:39 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Copper/Alu same breaker

Article 300.3(B) requires that all conductors of the same circuit be run in the same raceway or sheath. Article 300.20 also applies where the raceway or enclosure is ferrous that the conductors be run together to avoid inductive heating.
Reply With Quote
  #11  
Old 3/16/11, 1:04 AM
Jeffrey Moore Jeffrey Moore is offline
InterNACHI Member
 
Join Date: Feb 2008
Location: Mesa, AZ
Posts: 282
Default Re: Copper/Alu same breaker

Quote:
Originally Posted by gheller View Post
The aluminum doesn't need to be larger than the copper. The copper is larger than what it needs to be. The aluminum needs to be one size larger than it would have to be if it were copper.
That is why I had in the question- if the Cu is properly sized, you did not state that the Cu was oversized



Jeff Moore
www.quantumhomeinspections.com
Flir (ITC) Level II Thermographer
Mesa, AZ
Reply With Quote
  #12  
Old 3/16/11, 5:00 AM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Copper/Alu same breaker

Quote:
Originally Posted by gheller View Post
The aluminum doesn't need to be larger than the copper. The copper is larger than what it needs to be. The aluminum needs to be one size larger than it would have to be if it were copper.
Since these are not in a raceway then one could conclude that they are in two separate cables which is a violation as Jim has outlined. With a limited exception stranded conductors in cables, (the copper one in this case) start with #8 and larger, which means that the copper conductor is likely #8. According to your last sentence quoted above, for a 30 amp circuit the Aluminum conductor would also be required to be a #8 since #10 copper would be the minimum for a 30 amp circuit for a water heater load. So is the Al conductor actually a #8 AL or is this quote from the OP incorrect?

Quote:
The 220 volt breaker feeding the water heater has both aluminum and copper conductors. This is not a common practice but these conductors are sized properly for the 30 amp breaker they are connected to and the breaker is rated for both copper and aluminum.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
AFCI Questions and Answers - Mike Holt pabernathy Electrical Inspections 7 4/16/12 9:51 PM
Federal Electric 100A standalone main breaker -- OK or problematic? fbartlo Electrical Inspections 16 9/6/10 5:17 PM
Breaker Question mhawley Electrical Inspections 5 1/14/08 3:25 PM
Electrical Guru Question? Breaker lock outs pdoane Electrical Inspections 4 9/7/07 2:05 PM
Double Tapped Breaker tjohnson3 Electrical Inspections 8 4/20/07 9:04 AM


All times are GMT -4. The time now is 5:54 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts