Default Copper-Aluminum GEC

at same grounding clamp. Is this dual rated?



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!

Last edited by ccurrins; 7/31/11 at 2:08 AM..
Reply With Quote
Need a home inspection in Oregon? Check out InterNACHI's listing of Oregon certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 7/30/11, 6:13 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Copper-Aluminum GEC

I don't know if the lug is rated for multiple conductors, but it appears you have tinned-copper rather than aluminum.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #3  
Old 7/30/11, 7:14 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: Copper-Aluminum GEC

Thanks Michael, wanting to be sure this is not a connector I wasn't familiar with.

Jeff you're correct, it's tinned-copper.



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #4  
Old 7/30/11, 7:19 PM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,749
Default Re: Copper-Aluminum GEC

It's a moot point. The IRC and NEC prohibit GEC splices:

Quote:
E3510.1 Continuous. The unspliced grounding electrode conductor shall run to any convenient grounding electrode available
in the grounding electrode system, or to one or more
grounding electrode(s) individually. The grounding electrode
conductor shall be sized for the largest grounding electrode
conductor required among all of the electrodes connected to it.

Commentary:The grounding electrode conductors are to be
unspliced to achieve the greatest reliability and continuity
(see Section 250.64(C) of the NEC).
Where electrodes
are connected together to a common electrode
conductor, the largest required size of the conductors
will dictate the size of the common conductor. For example,
if a 6 AWG conductor ran from the service to a
ground rod and a 4 AWG conductor was required to
connect the ground rod to the footing steel, the 6 AWG
conductor would have to be upsized to a 4 AWG.
Reply With Quote
  #5  
Old 7/30/11, 8:11 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: Copper-Aluminum GEC

Quote:
Originally Posted by mboyett View Post
It's a moot point. The IRC and NEC prohibit GEC splices:
Thanks



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #6  
Old 7/31/11, 11:24 AM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Copper-Aluminum GEC

Do you have a photo of this installation? You need to be careful when determining what's actually a GEC and what's a bonding jumper. Only the GEC is required to be continuous. You can use bonding jumpers to interconnect all of the electrodes that are part of the grounding electrode system. Here's a few examples:



Reply With Quote
  #7  
Old 7/31/11, 1:16 PM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Copper-Aluminum GEC

Yes that's a violation in photo #3. You have bare copper and tinned copper which is fine, however your splicing of the GEC is required to be irreversible. Also it is not permitted to use that lug in that fashion with two conductors. I see some other problems with the length of the SE cable to the panel on the left.
Reply With Quote
  #8  
Old 7/31/11, 1:24 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: Copper-Aluminum GEC

Quote:
Originally Posted by Robert Meier View Post
Yes that's a violation in photo #3. You have bare copper and tinned copper which is fine, however your splicing of the GEC is required to be irreversible. Also it is not permitted to use that lug in that fashion with two conductors. I see some other problems with the length of the SE cable to the panel on the left.
Thanks Robert, that was my original question. I deleted the photo. The service entrance and main panel installed in 1960.

With photo at left (main panel) where bare copper and tinned copper is under same lug, that's also a violation, correct?



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #9  
Old 7/31/11, 2:08 PM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Copper-Aluminum GEC

Quote:
Originally Posted by ccurrins View Post

With photo at left (main panel) where bare copper and tinned copper is under same lug, that's also a violation, correct?

Yes, here's the code references:

Quote:
250.64 Grounding Electrode Conductor Installation.
(C) Continuous. Grounding electrode conductor(s) shall be installed in one continuous length without a splice or joint except as permitted in (1) and (2):
(1) Splicing shall be permitted only by irreversible compression-type connectors listed as grounding and bonding equipment or by the exothermic welding process.
Quote:
110.14 Electrical Connections.
Because of different characteristics of dissimilar metals, devices such as pressure terminal or pressure splicing connectors and soldering lugs shall be identified for the material of the conductor and shall be properly installed and used. Conductors of dissimilar metals shall not be intermixed in a terminal or splicing connector where physical contact occurs between dissimilar conductors (such as copper and aluminum, copper and copper-clad aluminum, or aluminum and copper-clad aluminum), unless the device is identified for the purpose and conditions of use. Materials such as solder, fluxes, inhibitors, and compounds, where employed, shall be suitable for the use and shall be of a type that will not adversely affect the conductors, installation, or equipment.
FPN: Many terminations and equipment are marked with a tightening torque.
(A) Terminals. Connection of conductors to terminal parts shall ensure a thoroughly good connection without damaging the conductors and shall be made by means of pressure connectors (including set-screw type), solder lugs, or splices to flexible leads. Connection by means of wire-binding screws or studs and nuts that have upturned lugs or the equivalent shall be permitted for 10 AWG or smaller conductors.
Terminals for more than one conductor and terminals used to connect aluminum shall be so identified.
Reply With Quote
  #10  
Old 7/31/11, 7:13 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: Copper-Aluminum GEC

Quote:
Originally Posted by Robert Meier View Post
Yes, here's the code references:
Thanks for the info.



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #11  
Old 7/31/11, 7:47 PM
KEVIN WOOD's Avatar
KEVIN WOOD KEVIN WOOD is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 3,106
Default Re: Copper-Aluminum GEC

They do have one that is designed for Linking the grounds and they have a separator between each GEC. Never payed attention to the company name on them. Do you know Robert Meier?
You find it in encased situations in concrete. I think it is called a Servit.



THE RIGHT TRAK
CIAQP, IAC2
Certified Master Inspector
kwoodinspections@hotmail.com
www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ
www.linkedin.com/in/kevinwoodiaq
OOVOO account kwoodinspections
Cell: 705-971-2096
Ph : 705-946-2676
Reply With Quote
  #12  
Old 7/31/11, 8:26 PM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Copper-Aluminum GEC

Quote:
Originally Posted by kwood View Post
They do have one that is designed for Linking the grounds and they have a separator between each GEC. Never payed attention to the company name on them. Do you know Robert Meier?
You find it in encased situations in concrete. I think it is called a Servit.

There are only two permissible types of products available to splice a GEC, one is an irreversible compression splice and the other is an exothermic welding (Cadweld) splice.

I believe that you're referring to a split bolt that has a separator which would sit in between the two conductors. Those typically would be used when splicing aluminum and copper. That type wouldn't be required here since the to conductors are both copper nor permitted due to the only types allowed as previously mentioned.
Reply With Quote
  #13  
Old 7/31/11, 8:35 PM
KEVIN WOOD's Avatar
KEVIN WOOD KEVIN WOOD is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 3,106
Default Re: Copper-Aluminum GEC

Correct. What is the name of the one I am refering to?
Electrical has always been my week spot in Home Inspection.
The reason is I seem to not be able to wrap my head around the confusion as the wire # system. I have talked to electricians and they can't figure out why they did it this way either.
Is there a reason?
One more point Robert don't forget I am from Canada.



THE RIGHT TRAK
CIAQP, IAC2
Certified Master Inspector
kwoodinspections@hotmail.com
www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ
www.linkedin.com/in/kevinwoodiaq
OOVOO account kwoodinspections
Cell: 705-971-2096
Ph : 705-946-2676

Last edited by kwood; 7/31/11 at 8:38 PM..
Reply With Quote
Need a home inspection in Oregon? Check out InterNACHI's listing of Oregon certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 8/1/11, 4:54 AM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Copper-Aluminum GEC

Quote:
Originally Posted by kwood View Post
They do have one that is designed for Linking the grounds and they have a separator between each GEC. Never payed attention to the company name on them. Do you know Robert Meier?
You find it in encased situations in concrete. I think it is called a Servit.
Quote:
Originally Posted by kwood View Post
Correct. What is the name of the one I am refering to?
Electrical has always been my week spot in Home Inspection.
The reason is I seem to not be able to wrap my head around the confusion as the wire # system. I have talked to electricians and they can't figure out why they did it this way either.
Is there a reason?
One more point Robert don't forget I am from Canada.
Yes, Servit is a brand name for a split bolt connector that is made by Burndy. Although they are permitted to be used for taps to the GEC they are not permitted to be used for splicing the GEC.


Reply With Quote
  #15  
Old 8/1/11, 7:53 AM
KEVIN WOOD's Avatar
KEVIN WOOD KEVIN WOOD is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 3,106
Default Re: Copper-Aluminum GEC

Robert:

I know the name of that one. The one I am talking about has a separating shim in the middle that is used for two different size GEC's
What is it called?
One is split bolt single wire. The other is two wire.
Same company but different name and application.



THE RIGHT TRAK
CIAQP, IAC2
Certified Master Inspector
kwoodinspections@hotmail.com
www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ
www.linkedin.com/in/kevinwoodiaq
OOVOO account kwoodinspections
Cell: 705-971-2096
Ph : 705-946-2676
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Light Switch Near Shower vsantos Electrical Inspections 204 3/19/12 9:58 AM
Total galvanic reaction? jtribuzio Plumbing Inspections 19 4/3/10 2:18 AM
Nice Report on AL Wire Terminations - Enjoy pabernathy Electrical Inspections 0 7/2/07 12:35 PM
Aluminum or tin coated copper wire?? mlong Electrical Inspections 8 5/14/06 10:36 PM
Looking for comment by Caoimhín P. Connell phinsperger Ancillary Inspection Services & Additional Topics 2 2/18/06 11:22 AM