Default copper clad aluminimum wire

Know someone who bought a home with this wire. Is it a hazard or worth being concerned about?
Reply With Quote
  #2  
Old 4/11/06, 2:56 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,038
Default Re: copper clad aluminimum wire

I have only seen this type of wire once. The conductor itself is considered safe.

Quote:
Copper-clad aluminum wire has a thin copper outer skin and a core of aluminum. Therefore it looks like copper, except on close examination of a cut end. Markings on the cable jacket would include "Al" or "Aluminum". There is no known history of connection overheating problems associated with copper-clad aluminum wire. No corrective actions are required for copper-clad aluminum wire.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #3  
Old 4/11/06, 3:24 PM
bob haller bob haller is offline
New User
 
Join Date: Sep 2004
Posts: 4
Please Note: bob haller is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: copper clad aluminimum wire

should this wire of been noted on the home inspection? does it require special connectors wirenuts etc?
Reply With Quote
  #4  
Old 4/11/06, 4:00 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,038
Default Re: copper clad aluminimum wire

This type of conductor is easily mistaken for copper wiring, unless the identifying markings or cut ends of the conductors are visible, however, there are no known (documented) issues with this particular wiring that I am aware of.

No special connection devices are required.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #5  
Old 4/11/06, 4:23 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,908
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: copper clad aluminimum wire

Copper-Clad Aluminum Conductors. Conductors drawn from a copper-clad aluminum rod with the copper metallurgically bonded to an aluminum core. The copper forms a minimum of 10 percent of the cross-sectional area of a solid conductor or each strand of a stranded conductor.

FPN: For aluminum and copper-clad aluminum conductors, see 310.15.

110.14 Electrical Connections

Because of different characteristics of dissimilar metals, devices such as pressure terminal or pressure splicing connectors and soldering lugs shall be identified for the material of the conductor and shall be properly installed and used. Conductors of dissimilar metals shall not be intermixed in a terminal or splicing connector where physical contact occurs between dissimilar conductors (such as copper and aluminum, copper and copper-clad aluminum, or aluminum and copper-clad aluminum), unless the device is identified for the purpose and conditions of use.



Identified (as applied to equipment).




Recognizable as suitable for the specific purpose, function, use, environment, application, and so forth, where described in a particular Code requirement.







FPN: Some examples of ways to determine suitability of equipment for a specific purpose, environment, or application include investigations by a qualified testing laboratory (listing and labeling), an inspection agency, or other organizations concerned with product evaluation.
Source: 2005 NEC



Reply With Quote
  #6  
Old 4/11/06, 4:43 PM
Gerry Beaumont's Avatar
Gerry Beaumont Gerry Beaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 5,749
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: copper clad aluminimum wire

Hi to all,

I believe that the largest problem facing home inspectors is a Jeff suggested identifying copper clad.

It should also be remebered than copper clad aluminum should be sized as per standard aluminum.

Regards

Gerry



Virtue is more to be feared than vice, because its excesses are not subject to the regulation of conscience.
Adam Smith (1723-1790)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106
Reply With Quote
  #7  
Old 4/11/06, 4:53 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,038
Default Re: copper clad aluminimum wire

There was no mention of dissimilar conductors - only copper-clad AL - to which I stated, no special connectors are needed.

If you disagree, say so. According to the references you've posted, I am correct.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #8  
Old 4/11/06, 5:32 PM
bob haller bob haller is offline
New User
 
Join Date: Sep 2004
Posts: 4
Please Note: bob haller is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: copper clad aluminimum wire

the wiring was clearly marked in the basement Al Cu/clad and the inspector was asked specifically about alunimum wire, should he of reported it?
Reply With Quote
  #9  
Old 4/11/06, 6:40 PM
rcooke rcooke is offline
Banned for Violating COE
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 9,381
Please Note: rcooke is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: copper clad aluminimum wire

Quote:
Originally Posted by bob haller
the wiring was clearly marked in the basement Al Cu/clad and the inspector was asked specifically about alunimum wire, should he of reported it?
CYA Yes he can not be wrong by telling what it is , he could have to expain himself for not telling what it is .
I would say Copper clad aluminum wire and move on. Roy sr
Reply With Quote
  #10  
Old 4/11/06, 6:58 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 5,745
Default Re: copper clad aluminimum wire

Quote:
Originally Posted by jtedesco1
Copper-Clad Aluminum Conductors. Conductors drawn from a copper-clad aluminum rod with the copper metallurgically bonded to an aluminum core. The copper forms a minimum of 10 percent of the cross-sectional area of a solid conductor or each strand of a stranded conductor.

FPN: For aluminum and copper-clad aluminum conductors, see 310.15.

110.14 Electrical Connections

Because of different characteristics of dissimilar metals, devices such as pressure terminal or pressure splicing connectors and soldering lugs shall be identified for the material of the conductor and shall be properly installed and used. Conductors of dissimilar metals shall not be intermixed in a terminal or splicing connector where physical contact occurs between dissimilar conductors (such as copper and aluminum, copper and copper-clad aluminum, or aluminum and copper-clad aluminum), unless the device is identified for the purpose and conditions of use.






Identified (as applied to equipment).



















Recognizable as suitable for the specific purpose, function, use, environment, application, and so forth, where described in a particular Code requirement.
















FPN: Some examples of ways to determine suitability of equipment for a specific purpose, environment, or application include investigations by a qualified testing laboratory (listing and labeling), an inspection agency, or other organizations concerned with product evaluation.
Source: 2005 NEC









I'm having a hard time understanding you, Joe.

You cut and paste items from the NEC and elsewhere but don't say what you think about the post at hand.

You make reference to dissimilar metals and highlight "unless" and that's as far as you take it.

Care to expand specifically on copper clad aluminum wire usage, in your own words?

Thanks.
Reply With Quote
  #11  
Old 4/11/06, 7:09 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: copper clad aluminimum wire

As jeff has stated.....we are talking about ALL the conductors within the branch circuit layout being Copper Clad Alum. so it would be of SIMILAR metals....thus as jeff stated would not require anything special....

Just again make sure the connectors and terminals allow Copper Clad Alum.( AL/CU) wires to be terminated on them and that the splice wirenuts are approved as well for the same.

Report it...Yes, report what you see..and GERRY made a WONDERFUL point.....Bravo Gerry......Remember it must be sized as Aluminum....Dang that Englishman knows some stuff...thehehehe



Paul W. Abernathy,CMI,CEI,CEPE
NEC® Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #12  
Old 4/11/06, 7:16 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 5,745
Default Re: copper clad aluminimum wire

Thanks, Paul.

I did understand other's posts...just not Joe's.

I was hoping he could make his posts more clear and useful...or maybe it's just me.
Reply With Quote
  #13  
Old 4/11/06, 7:17 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,038
Default Re: copper clad aluminimum wire

Quote:
Originally Posted by bob haller
the wiring was clearly marked in the basement Al Cu/clad and the inspector was asked specifically about alunimum wire, should he of reported it?
The fact that he did not mention the type of wiring is inconsequential (IMHO) as there are no safety issues associated with Cu-clad AL- which answers your original questiion.

Had this been solid AL wiring, he may certainly be in trouble for not mentioning it.

If you're looking to have the inspector pay for re-wiring of the home for failing to mention the conductor material, you have no leg to stand on.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #14  
Old 4/11/06, 7:24 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: copper clad aluminimum wire

Larry....No it is not you...Trust me...you are not alone fella...



Paul W. Abernathy,CMI,CEI,CEPE
NEC® Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #15  
Old 4/11/06, 7:27 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: copper clad aluminimum wire

Jeff,

I did not mean report it as being a defect....Report it as the type of wire found.....nothing technically wrong with Copper Clad Aluminum...just happen to personally not like it......

All my reports require me to list the type of wire found....regardless but really nothing to get overly concerned about most certainly bob....Should be fine..



Paul W. Abernathy,CMI,CEI,CEPE
NEC® Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical 6 9/15/08 8:57 AM
Nice Report on AL Wire Terminations - Enjoy pabernathy Electrical 0 7/2/07 1:35 PM
Proper Marr Connectors for Aluminum Pigtails jskrypka Canadian Inspectors 4 3/25/07 11:41 PM
Aluminum or tin coated copper wire?? mlong Electrical 8 5/14/06 11:36 PM
Looking for comment by Caoimhín P. Connell phinsperger Ancillary Services & Additional Topics 2 2/18/06 12:22 PM


All times are GMT -4. The time now is 11:39 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts