  #1  
Old 3/15/10, 10:00 AM
Bill Smith's Avatar
Bill Smith Bill Smith is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: East Northport, NY
Posts: 1,043
Default Copper Clad Aluminum

Brain cramp here - should copper clad aluminum conductors be sized larger for a circuit (like regular aluminum), or can they be sized like copper conductors?



"A man cannot be truly grateful and remain unhappy"
http://www.SmithHomeInspection.com
SmithHomeInspection@yahoo.com
NY State Lic. # 16000008304
631-434-5200
Reply With Quote
Need a home inspection in Nebraska? Check out InterNACHI's listing of Nebraska certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 3/15/10, 10:11 AM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Copper Clad Aluminum

According to the NEC Table 310.16 they're sized the same as Aluminum conductors.
Reply With Quote
  #3  
Old 3/15/10, 10:12 AM
Bill Smith's Avatar
Bill Smith Bill Smith is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: East Northport, NY
Posts: 1,043
Default Re: Copper Clad Aluminum

Thought so - thanks for the reply Robert.



"A man cannot be truly grateful and remain unhappy"
http://www.SmithHomeInspection.com
SmithHomeInspection@yahoo.com
NY State Lic. # 16000008304
631-434-5200
Reply With Quote
  #4  
Old 3/15/10, 11:47 AM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Copper Clad Aluminum

Bill, just curious, where are you seeing copper-clad aluminum? I think that I've only seen it once in 25 years as an electrician.
Reply With Quote
  #5  
Old 3/15/10, 12:27 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Copper Clad Aluminum

I've heard that it exists, but have never seen it myself. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #6  
Old 3/15/10, 1:21 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Copper Clad Aluminum

I've Seen It.....



Paul W. Abernathy
Reply With Quote
  #7  
Old 3/15/10, 1:32 PM
Chuck Evans's Avatar
Chuck Evans Chuck Evans is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Stagecoach, TX
Posts: 2,037
Default Re: Copper Clad Aluminum

Pics please if you have them - I've never seen it.

Was this something transitional between the older and newer alloys? Timeframe used? Thanks



Chuck Evans (TREC #7657)
Level III Infraspection Institute Certified Infrared Thermographer (#8402)
HomeCert Houston Home Inspections & Thermal Inspections Find us on Facebook
Houston Thermal Inspections & Infrared Imaging Find us on Facebook
Houston Home Inspector

Houston, TX
Reply With Quote
  #8  
Old 3/15/10, 1:57 PM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Copper Clad Aluminum

If anyone's interested, here's the NEC, Article 100 definition:

Quote:
Copper-Clad Aluminum Conductors. Conductors drawn from a copper-clad aluminum rod with the copper metallurgically bonded to an aluminum core. The copper forms a minimum of 10 percent of the cross-sectional area of a solid conductor or each strand of a stranded conductor.
Reply With Quote
  #9  
Old 3/15/10, 4:32 PM
mnahrgang's Avatar
mnahrgang mnahrgang is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Springfield, OH
Posts: 5,799
Default Re: Copper Clad Aluminum

Quote:
Originally Posted by cevans View Post
Pics please if you have them - I've never seen it.

Was this something transitional between the older and newer alloys? Timeframe used? Thanks
Any Pics guys. I've never seen it either (that I am aware of.)

Any concerns with it?



Mark Nahrgang
www.DaytonSpringfieldHomeInspector.com
www.HeyMark.info

Home Inspections for Springfield, Dayton, and surrounding OH areas.
Reply With Quote
  #10  
Old 3/15/10, 6:18 PM
Bill Smith's Avatar
Bill Smith Bill Smith is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: East Northport, NY
Posts: 1,043
Default Re: Copper Clad Aluminum

Here is a pic of the sheathing. The conductor itself looks like copper, except for the cut end where you can see the aluminum. I have found it 5 or 6 times. It was used in the 70's for a short while.
Attached Thumbnails
copper-clad-aluminum-cu-al.jpg  



"A man cannot be truly grateful and remain unhappy"
http://www.SmithHomeInspection.com
SmithHomeInspection@yahoo.com
NY State Lic. # 16000008304
631-434-5200
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Light Switch Near Shower vsantos Electrical Inspections 204 3/19/12 9:58 AM
Old wires. Copper or aluminum? bforeman Electrical Inspections 6 10/19/08 7:35 PM
Nice Report on AL Wire Terminations - Enjoy pabernathy Electrical Inspections 0 7/2/07 12:35 PM
Aluminum or tin coated copper wire?? mlong Electrical Inspections 8 5/14/06 10:36 PM
Looking for comment by Caoimhín P. Connell phinsperger Ancillary Inspection Services & Additional Topics 2 2/18/06 11:22 AM


All times are GMT -4. The time now is 5:56 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts