Brain cramp here - should copper clad aluminum conductors be sized larger for a circuit (like regular aluminum), or can they be sized like copper conductors?
"A man cannot be truly grateful and remain unhappy"
http://www.SmithHomeInspection.com SmithHomeInspection@yahoo.com NY State Lic. # 16000008304 631-434-5200 |
| Need a home inspection in Nebraska? Check out InterNACHI's listing of Nebraska certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#2
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
According to the NEC Table 310.16 they're sized the same as Aluminum conductors.
|
|
#3
|
||||
|
||||
|
Thought so - thanks for the reply Robert.
"A man cannot be truly grateful and remain unhappy"
http://www.SmithHomeInspection.com SmithHomeInspection@yahoo.com NY State Lic. # 16000008304 631-434-5200 |
|
#4
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Bill, just curious, where are you seeing copper-clad aluminum? I think that I've only seen it once in 25 years as an electrician.
|
|
#5
|
||||
|
||||
|
I've heard that it exists, but have never seen it myself. . .
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#6
|
|||
|
|||
|
I've Seen It.....
Paul W. Abernathy |
|
#7
|
||||
|
||||
|
Pics please if you have them - I've never seen it.
Was this something transitional between the older and newer alloys? Timeframe used? Thanks Chuck Evans (TREC #7657) Level III Infraspection Institute Certified Infrared Thermographer (#8402) HomeCert Houston Home Inspections & Thermal Inspections Find us on Facebook Houston Thermal Inspections & Infrared Imaging Find us on Facebook Houston Home Inspector Houston, TX |
|
#8
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
If anyone's interested, here's the NEC, Article 100 definition:
Quote:
|
|
#9
|
||||
|
||||
|
Quote:
Any concerns with it? Mark Nahrgang www.DaytonSpringfieldHomeInspector.com www.HeyMark.info Home Inspections for Springfield, Dayton, and surrounding OH areas. |
|
#10
|
||||
|
||||
|
Here is a pic of the sheathing. The conductor itself looks like copper, except for the cut end where you can see the aluminum. I have found it 5 or 6 times. It was used in the 70's for a short while.
"A man cannot be truly grateful and remain unhappy"
http://www.SmithHomeInspection.com SmithHomeInspection@yahoo.com NY State Lic. # 16000008304 631-434-5200 |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Light Switch Near Shower | vsantos | Electrical Inspections | 204 | 3/19/12 9:58 AM |
| Old wires. Copper or aluminum? | bforeman | Electrical Inspections | 6 | 10/19/08 7:35 PM |
| Nice Report on AL Wire Terminations - Enjoy | pabernathy | Electrical Inspections | 0 | 7/2/07 12:35 PM |
| Aluminum or tin coated copper wire?? | mlong | Electrical Inspections | 8 | 5/14/06 10:36 PM |
| Looking for comment by Caoimhín P. Connell | phinsperger | Ancillary Inspection Services & Additional Topics | 2 | 2/18/06 11:22 AM |