Default Re: Copper Tie in Electrical Panel

When the red and black wire of the same multi-wire branch circuit are served by two overcurrent devices on the same leg, the current on the neutral will add. In the photographs, the red and black conductors for each multiwire branch circuit appear to land on two overcurrent devices in the same package (twin breaker). Each of these twins plug into a single buss slot. Both halves of the twin are on the same leg. If it is how I think it is, the neutrals will overload.

I'm not exactly a journalist, so I might have done a bad job of re-explaining this in layman's terms, but maybe somebody else can pick it up from here.

EDIT... nevermind.... I see they started at the bottom with a half size breaker. That puts each half of the twins on a different leg. No problem exists. Just had to get out my magnifying glass.
Reply With Quote
  #17  
Old 3/29/07, 11:22 PM
Peter Doane's Avatar
Peter Doane Peter Doane is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Olympia, WA
Posts: 2,055
Default Re: Copper Tie in Electrical Panel

Quote:
Originally Posted by Marc D. Shunk
When the red and black wire of the same multi-wire branch circuit are served by two overcurrent devices on the same leg, the current on the neutral will add. In the photographs, the red and black conductors for each multiwire branch circuit appear to land on two overcurrent devices in the same package (twin breaker). Each of these twins plug into a single buss slot. Both halves of the twin are on the same leg. If it is how I think it is, the neutrals will overload.

I'm not exactly a journalist, so I might have done a bad job of re-explaining this in layman's terms, but maybe somebody else can pick it up from here.

EDIT... nevermind.... I see they started at the bottom with a half size breaker. That puts each half of the twins on a different leg. No problem exists. Just had to get out my magnifying glass.
Thanks Marc,
I understand what your explaining, I totally missed the "twin breaker" part of it. Makes sense now, even though its not an issue in this panel.



Peter Doane
Realty Check Inspection Service
NACHI ID# 05120681
Reply With Quote
  #18  
Old 3/29/07, 11:36 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Copper Tie in Electrical Panel

Where is that romex coming from? It looks like it is going into the "main" compartment.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
National Electrical Code Information and Discussion jtedesco1 Electrical Inspections 50 6/15/10 7:28 PM
Access to Electrical Panel in Ontario by HVAC Contractors Nalliah Thayabharan Canadian Inspectors 10 5/21/07 3:01 PM
Electrical Safety Information jtedesco1 Electrical Inspections 0 2/19/06 1:48 AM
Bad electrical problem Pest Guy Electrical Inspections 4 1/20/06 9:26 PM


All times are GMT -4. The time now is 5:56 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts