Default Is this correct

Inspected a home today and it looks like the grounds and neutral are tied together. Is this correct? This was a Cutler Hammer panel circa 1978 I think
Attached Images
File Type: jpg Picture 054.jpg (162.2 KB, 90 views)
File Type: jpg Picture 055.jpg (160.4 KB, 68 views)
Reply With Quote
  #2  
Old 10/30/08, 11:06 PM
Gerry Beaumont's Avatar
Gerry Beaumont Gerry Beaumont is online now
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 5,197
Gerry Beaumont has a reputation beyond repute Gerry Beaumont has a reputation beyond repute Gerry Beaumont has a reputation beyond repute Gerry Beaumont has a reputation beyond repute Gerry Beaumont has a reputation beyond repute Gerry Beaumont has a reputation beyond repute Gerry Beaumont has a reputation beyond repute Gerry Beaumont has a reputation beyond repute Gerry Beaumont has a reputation beyond repute Gerry Beaumont has a reputation beyond repute Gerry Beaumont has a reputation beyond repute
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: Is this correct

Quote:
Originally Posted by rchorey View Post
Inspected a home today and it looks like the grounds and neutral are tied together. Is this correct? This was a Cutler Hammer panel circa 1978 I think

Ronald, as this appears to be the panel containg the main disconnect having the Neutrals and grounds on the same bus is OK, however I would question the multiple tapping of the Neutrals, they really should be seperately terminated on the bus.

Regards

Gerry



Virtue is more to be feared than vice, because its excesses are not subject to the regulation of conscience.
Adam Smith (1723-1790)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106
Reply With Quote
  #3  
Old 10/30/08, 11:08 PM
GARY R. EVANS GARY R. EVANS is online now
InterNACHI Member
 
Join Date: Oct 2008
Location: Coconut Creek, FL
Posts: 31
GARY R. EVANS has had a little positive feedback
Default Re: Is this correct

It is fine as long as the house main breaker is in the panel. The neutral is required to be bonded to the enclosure at the main disconnect location. If the Main was outside by the meter then the the grounds and neutrals should be isolated from each other in the interior panel.
Reply With Quote
  #4  
Old 10/31/08, 12:09 AM
Thomas H. Dietrich's Avatar
Thomas H. Dietrich Thomas H. Dietrich is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Hellertown, Pa
Posts: 1,852
Thomas H. Dietrich is very trusted source of information Thomas H. Dietrich is very trusted source of information Thomas H. Dietrich is very trusted source of information Thomas H. Dietrich is very trusted source of information Thomas H. Dietrich is very trusted source of information Thomas H. Dietrich is very trusted source of information Thomas H. Dietrich is very trusted source of information
Send a message via Yahoo to tdietrich1
Default Re: Is this correct

Quote:
Originally Posted by gbeaumont View Post
however I would question the multiple tapping of the Neutrals
The effort made braiding the wires to fit under one screw compared to using the empty screws ... tips me off to look closer at the electrical work. Common sense seems uncommon here.

Tom



Hellertown, Pa 18055 NACHI ID: NACHI06101299
Northampton County Home Inspector, Monroe County Home Inspector


Help Me Save Money For My Kids' Education.

"Might as well stick a fork in it, the real estate industry is done for now."
- Tom Dietrich November 4th 2008

Ayers: Obama was 'family friend'
Reply With Quote
  #5  
Old 10/31/08, 12:30 AM
James F. McKee's Avatar
James F. McKee James F. McKee is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Amherst, Oh
Posts: 3,651
James F. McKee has a reputation beyond repute James F. McKee has a reputation beyond repute James F. McKee has a reputation beyond repute James F. McKee has a reputation beyond repute James F. McKee has a reputation beyond repute James F. McKee has a reputation beyond repute James F. McKee has a reputation beyond repute James F. McKee has a reputation beyond repute James F. McKee has a reputation beyond repute James F. McKee has a reputation beyond repute James F. McKee has a reputation beyond repute
Default Re: Is this correct

Quote:
Originally Posted by gevans2 View Post
It is fine as long as the house main breaker is in the panel. The neutral is required to be bonded to the enclosure at the main disconnect location. If the Main was outside by the meter then the the grounds and neutrals should be isolated from each other in the interior panel.
welcome aboard Gary....come back often....jim



Classic Home inspections

Jim Mckee
Amherst, Ohio

www.amhersthomeinspector.com
Reply With Quote
  #6  
Old 10/31/08, 12:32 AM
James F. McKee's Avatar
James F. McKee James F. McKee is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Amherst, Oh
Posts: 3,651
James F. McKee has a reputation beyond repute James F. McKee has a reputation beyond repute James F. McKee has a reputation beyond repute James F. McKee has a reputation beyond repute James F. McKee has a reputation beyond repute James F. McKee has a reputation beyond repute James F. McKee has a reputation beyond repute James F. McKee has a reputation beyond repute James F. McKee has a reputation beyond repute James F. McKee has a reputation beyond repute James F. McKee has a reputation beyond repute
Default Re: Is this correct

Quote:
Originally Posted by gbeaumont View Post
Ronald, as this appears to be the panel containg the main disconnect having the Neutrals and grounds on the same bus is OK, however I would question the multiple tapping of the Neutrals, they really should be seperately terminated on the bus.

Regards

Gerry
agreed, but was this not a common practice Gerry???



Classic Home inspections

Jim Mckee
Amherst, Ohio

www.amhersthomeinspector.com
Reply With Quote
  #7  
Old 10/31/08, 3:44 AM
Paul Dickerson Paul Dickerson is offline
InterNACHI Member
 
Join Date: May 2004
Location: Clinton, WA
Posts: 301
Paul Dickerson is generally well trusted
Default Re: Is this correct

I think it was common in some areas of the country, but not in my area. I don't see double tapped neutrals or combined neutral-grounds all that often.
Reply With Quote
  #8  
Old 10/31/08, 7:49 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 6,358
David P. Valley has a reputation beyond repute David P. Valley has a reputation beyond repute David P. Valley has a reputation beyond repute David P. Valley has a reputation beyond repute David P. Valley has a reputation beyond repute David P. Valley has a reputation beyond repute David P. Valley has a reputation beyond repute David P. Valley has a reputation beyond repute David P. Valley has a reputation beyond repute David P. Valley has a reputation beyond repute David P. Valley has a reputation beyond repute
Default Re: Is this correct

Quote:
Originally Posted by jmckee View Post
agreed, but was this not a common practice Gerry???

Double lugged neutrals are a common practice here and I write every one of them up.
Reply With Quote
  #9  
Old 10/31/08, 8:22 AM
Ronald G. Chorey II's Avatar
Ronald G. Chorey II Ronald G. Chorey II is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Las Cruces, NM
Posts: 85
Ronald G. Chorey II is generally well trusted
Send a message via MSN to rchorey
Default Re: Is this correct

Thank you gentlemen for your expertise
Reply With Quote
  #10  
Old 10/31/08, 9:39 AM
Gerry Beaumont's Avatar
Gerry Beaumont Gerry Beaumont is online now
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 5,197
Gerry Beaumont has a reputation beyond repute Gerry Beaumont has a reputation beyond repute Gerry Beaumont has a reputation beyond repute Gerry Beaumont has a reputation beyond repute Gerry Beaumont has a reputation beyond repute Gerry Beaumont has a reputation beyond repute Gerry Beaumont has a reputation beyond repute Gerry Beaumont has a reputation beyond repute Gerry Beaumont has a reputation beyond repute Gerry Beaumont has a reputation beyond repute Gerry Beaumont has a reputation beyond repute
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: Is this correct

Quote:
Originally Posted by jmckee View Post
agreed, but was this not a common practice Gerry???
Hi Jim, so was pushing 5 year olds up chimneys

but we think we know better these days

Seriously though, The code on double tapping neutrals came in in the early 1980's if memory serves, and the picture that was posted appears to feature quad & quin taps

Regards

Gerry



Virtue is more to be feared than vice, because its excesses are not subject to the regulation of conscience.
Adam Smith (1723-1790)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106
Reply With Quote
  #11  
Old 10/31/08, 10:11 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI
Posts: 12,323
Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute
Default Re: Is this correct

It never has been permitted technically by UL67 and under NEC 110.3(B).

It was clarified in NEC 408.21

Even Mike Holt was confused by this issue.

Video link

Holt's comment:

Switchboards and Panelboards
408.21 Grounded Conductor Terminations
Intent: This new section should ensure that grounded (neutral) conductors terminate within the panelboard to an individual terminal. This has been a UL requirement (UL Std. 67 – Panelboard Standard) for some time, and the addition to the NEC is intended to bring this information to the installers. Technically, this is covered by 110.3(B), which requires all equipment to be installed in accordance with the manufacturer's installation instructions and markings, but nobody knew it existed. UL Std. 67 (Panelboard Standard) permits up to three 10 AWG equipment grounding conductors to terminate on a single terminal, if the terminal is marked for this purpose. Figure 408-3

The intent of this requirement is to ensure that the grounded (neutral) conductor of a multiwire branch circuit is not momentarily disconnected, which could result in the destruction of electrical equipment and fires from overvoltage.



"Never underestimate the difficulty of changing false beliefs by facts."
Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
or
Minnesota Home Inspector

Reply With Quote
  #12  
Old 10/31/08, 12:27 PM
Christopher B. Currins's Avatar
Christopher B. Currins Christopher B. Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Alton, IL
Posts: 2,581
Christopher B. Currins has a reputation beyond repute Christopher B. Currins has a reputation beyond repute Christopher B. Currins has a reputation beyond repute Christopher B. Currins has a reputation beyond repute Christopher B. Currins has a reputation beyond repute Christopher B. Currins has a reputation beyond repute Christopher B. Currins has a reputation beyond repute Christopher B. Currins has a reputation beyond repute Christopher B. Currins has a reputation beyond repute Christopher B. Currins has a reputation beyond repute Christopher B. Currins has a reputation beyond repute
Default Re: Is this correct

Here's another link that I include when I find double taps, All Burned Up
Reply With Quote
  #13  
Old 10/31/08, 2:53 PM
Jeffrey R. Wicklander's Avatar
Jeffrey R. Wicklander Jeffrey R. Wicklander is online now
InterNACHI Member
 
Join Date: Mar 2008
Location: Libertyville, Il
Posts: 226
Jeffrey R. Wicklander is often very helpful Jeffrey R. Wicklander is often very helpful
Default Re: Is this correct

Quote:
Originally Posted by mlarson View Post
It never has been permitted technically by UL67 and under NEC 110.3(B).

It was clarified in NEC 408.21

Even Mike Holt was confused by this issue.

Video link

Holt's comment:

Switchboards and Panelboards
408.21 Grounded Conductor Terminations
Intent: This new section should ensure that grounded (neutral) conductors terminate within the panelboard to an individual terminal. This has been a UL requirement (UL Std. 67 – Panelboard Standard) for some time, and the addition to the NEC is intended to bring this information to the installers. Technically, this is covered by 110.3(B), which requires all equipment to be installed in accordance with the manufacturer's installation instructions and markings, but nobody knew it existed. UL Std. 67 (Panelboard Standard) permits up to three 10 AWG equipment grounding conductors to terminate on a single terminal, if the terminal is marked for this purpose. Figure 408-3

The intent of this requirement is to ensure that the grounded (neutral) conductor of a multiwire branch circuit is not momentarily disconnected, which could result in the destruction of electrical equipment and fires from overvoltage.

In 2005, this reference was moved to 408.41, for whatever reason. In case people are trying to search for it.

Jeff
Reply With Quote
  #14  
Old 10/31/08, 2:59 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI
Posts: 12,323
Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute
Default Re: Is this correct

Quote:
Originally Posted by jwicklander View Post
In 2005, this reference was moved to 408.41, for whatever reason. In case people are trying to search for it.

Jeff