Default Corrosion at breaker connections

I did an inspection today and found corrosion at a double breaker for the clothes dryer--40 amp. The corrosion is at the 3rd terminal form the top in the attached photo. A portion of the cable sheathing appears to have melted. I ran the dryer for 20 minutes and neither the terminal nor the cable overheated. Can anyone give me a reason for the corrosion and the previous overheating?
Attached Images
File Type: jpg photos 081.jpg (89.4 KB, 94 views)
Reply With Quote
  #2  
Old 10/21/08, 9:16 PM
Thomas J. Brady Thomas J. Brady is offline
InterNACHI Member
 
Join Date: Nov 2003
Location: Cortland, NY
Posts: 9
Thomas J. Brady hasn't had much positive or negative feedback
Default Re: Corrosion at breaker connections

May be from previously loose connection at the terminal on te breaker that may have caused an arcing condition that melted the sheathing - Ask the current owner if any recent repair has been conducted to the dryer or branch circuit -some wire/cables can loosen from expansion & contraction or not enough torque on the terminal to fasten cable in place
Reply With Quote
  #3  
Old 10/22/08, 12:43 PM
jkogel jkogel is offline
Active Poster
 
Join Date: Jan 2007
Location: Sooke, BC
Posts: 566
jkogel is well trusted jkogel is well trusted jkogel is well trusted
Please Note: jkogel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Corrosion at breaker connections

Regardless, it needs a repair by a qualified electrician.

John Kogel
www.allsafehome.ca
Reply With Quote
  #4  
Old 10/22/08, 9:05 PM
Allen L. Catterton Allen L. Catterton is offline
InterNACHI Member
 
Join Date: May 2004
Location: Cantonment, FL
Posts: 57
Allen L. Catterton is generally well trusted
Default Re: Corrosion at breaker connections

Thanks for your replies and I did recommend that an electrician inspect, clean and repair the deficiency.
Reply With Quote
  #5  
Old 10/22/08, 11:48 PM
Jim Port Jim Port is offline
Active Poster
 
Join Date: Jul 2007
Location: Maryland
Posts: 131
Jim Port has had a little positive feedback
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Corrosion at breaker connections

Did you note that the breaker was incorrecly sized for its purpose? In 30 years I have never seen a residential dryer that required more than 30 amps at 240 volts.
Reply With Quote
  #6  
Old 10/25/08, 11:18 AM
Sean Corcoran Sean Corcoran is offline
InterNACHI Member
 
Join Date: Mar 2007
Location: St. Catharines, Ontario
Posts: 123
Sean Corcoran is often very helpful Sean Corcoran is often very helpful
Default Re: Corrosion at breaker connections

Also shouldn't the white wire next to it be marked with electrical tape as hot?
Reply With Quote
  #7  
Old 10/27/08, 7:28 PM
John Allingham John Allingham is offline
InterNACHI Member
 
Join Date: Jun 2004
Location: Milton, ON
Posts: 284
John Allingham is generally well trusted John Allingham is generally well trusted
Default Re: Corrosion at breaker connections

What guage is that burnt wire. Looks small.
Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

Similar Threads
Thread Thread Starter Forum Replies Last Post
Breaker Question mhawley Electrical 5 1/14/08 4:25 PM
Electrical Guru Question? Breaker lock outs pdoane Electrical 4 9/7/07 3:05 PM
Double Tapped Breaker tjohnson3 Electrical 8 4/20/07 10:04 AM
Soldered pipe supports causing corrosion kshepard Plumbing 7 12/3/06 3:30 PM
AFCI Questions and Answers - Mike Holt pabernathy Electrical 0 7/7/06 1:24 PM


All times are GMT -4. The time now is 5:59 PM.


Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics