Default I could use comments on this one

From todays inspection, this run had a switch in the basement near the door for heat tape which was up in the gutters.

Bearing in mind that the heat tape is made for out door use , is it allowed to be permenantly installed this way?.

( other than clogging the gutter issue.) Need words.

Seems like automatic shock hazard but then the gutter is metal too.

could-use-comments-one-dscn0070-small-.jpg.JPG
Views:	157
Size:	56.4 KB
ID:	21758

Last edited by belliott; 6/5/08 at 9:21 PM..
Reply With Quote
  #2  
Old 6/5/08, 9:27 PM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: I could use comments on this one

Hi Bob,

How about stupid and dangerous??

Failing that lets just go with, down spout being improperly used as electrical conduit

OH BTW, nice siding material!!

Regards

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #3  
Old 6/5/08, 9:35 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: I could use comments on this one

Gerry, while this install is at least suspect as the downspout is being used as a raceway, we do have gutter and roof ice melting systems up here because of the potential of ice dams in the great white North.

Here is one type.



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
  #4  
Old 6/5/08, 9:37 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: I could use comments on this one

Thanks Gerry and that is my point Mike.

So what is my defect comment?
Reply With Quote
  #5  
Old 6/5/08, 9:44 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: I could use comments on this one

That is a hard one.
This is not really a case of using the gutter as a conduit. The heat tape IS supposed to go up inside the leader.
I think the heat tape in the sealtite is an issue since it is supposed to be in free air. I think it would over heat inside the flexible conduit.
Reply With Quote
  #6  
Old 6/5/08, 9:52 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: I could use comments on this one

Speedy, Bob didn't post a picture of what he said was heat tape. Bob?

Gutter/downspout and roof installation instructions are here for the type I am familiar with.



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
  #7  
Old 6/5/08, 10:18 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: I could use comments on this one

I do not have a pic of it coming out of the gutter.
Unless it was encluded in one of my roof shots by accident. (duh I know but that hatch weighed 100 pounds.)(caught the gutter run after the ladder was back.)
Reply With Quote
  #8  
Old 6/5/08, 10:24 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: I could use comments on this one

How secure is the conduit to the wall Bob? With the height it's set at and the location, I'd be concerned with kids climbing on it and pulling it right off of the wall.



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #9  
Old 6/5/08, 10:24 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: I could use comments on this one

If you saw the roof shots with all the clogged waste stacks you would know why I was preoccupied
could-use-comments-one-dscn0017-small-.jpg.JPG
Views:	102
Size:	34.4 KB
ID:	21761

I do recall seeing the heat tape futher up (note gutter raceway below in background)
Reply With Quote
  #10  
Old 6/5/08, 10:27 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: I could use comments on this one

Chris that was not really much of a concern.

300 defect pics.
Reply With Quote
  #11  
Old 6/5/08, 10:32 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: I could use comments on this one

Quote:
Originally Posted by relliott
Chris that was not really much of a concern.

300 defect pics.
That's only 25 per unit. I hope they don't find out where you live.



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #12  
Old 6/5/08, 10:34 PM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: I could use comments on this one

Quote:
Originally Posted by mlarson
Gerry, while this install is at least suspect as the downspout is being used as a raceway, we do have gutter and roof ice melting systems up here because of the potential of ice dams in the great white North.

Here is one type.
I know Mike, I lived above the artic circle in MA & NH for 10 years

Way too familiar with ice damning, why do you think I live in the sun damning state??

Regards

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #13  
Old 6/5/08, 10:39 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: I could use comments on this one

Chris see my other thread in electric for one of the fun ones.

Mike according to your link it may be ok to clog a gutter with conductors.

Great I can save that $3 a 8 foot section of conduit from now on.
Reply With Quote
  #14  
Old 6/5/08, 10:47 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: I could use comments on this one

Quote:
Originally Posted by mlarson
Speedy, Bob didn't post a picture of what he said was heat tape. Bob?
I maybe mistook this as saying this was the heat tape installation:
Quote:
Originally Posted by relliott
From todays inspection, this run had a switch in the basement near the door for heat tape which was up in the gutters.
Wouldn't be the first time I was wrong.
Reply With Quote
  #15  
Old 6/5/08, 10:47 PM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: I could use comments on this one

Quote:
Originally Posted by relliott
Chris see my other thread in electric for one of the fun ones.

Mike according to your link it may be ok to clog a gutter with conductors.

Great I can save that $3 a 8 foot section of conduit from now on.
Bob I would bet any money you like that the UL listing for that heat tape does not include its installation within down spouts, I'll also place the same bet on the down spout not being a UL listed raceway.

Regards

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Infrared Sample reports dvalley Thermal Imaging, Infrared Cameras & Energy Audits 26 1/1/08 8:40 PM
Any comments mbyrd Electrical Inspections 13 6/10/07 11:45 PM
For those in favor of licensing gbeaumont Legislation, Licensing & Legal Issues for Inspectors 70 5/21/07 3:09 PM
Tidbits from the ASHI Message Board jbushart Miscellaneous Discussion for Inspectors 126 4/27/07 11:05 AM


All times are GMT -4. The time now is 5:57 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts