Are these connectors allowed at breakers?
|
|
#2
|
||||
|
||||
|
I think those are for stranded wire. The picture looks like stranded wire is present. Have a close up pic?
B.A. King Home Inspections, LLC www.BAKingHomeInspections.com Serving Charlotte NC area and Rock Hill SC areas. CMI Certified Master Inspector and Independent 704 301-3207 "Discovery consists in seeing what everyone else has seen and thinking what no one else has thought." - Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937 |
|
#3
|
||||
|
||||
|
Quote:
Regards Gerry "To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future." (Mark B Adams) Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida. NACHI cell 484-429-5466 NACHI02121106 |
|
#4
|
||||
|
||||
|
This is a question for the super sparky's.... Paul Abernathy where are you???
Here is something that is a clue to me that this may not fly .... "Clamping force" under a screw on the OCPD is a factor on how amperage (current ) can move through a junction like this. Wire nuts and weak connections and so on.. So figure on the limitations when you try and "crimp" stranded wires with a tool and your hand pressure .. A heck of a lot less then a screw under a screw driver. Or nut driver, set screw..etc.. PAUL where are Youuuuuuuuu? |
|
#5
|
||||
|
||||
|
Hey Guys,
I also believe it is stranded wire and while the arguement could be made against them for Solid Core wire it is used widely in the industry in commercial to use the approved spade connectors as used here. For you code lovers......when making terminal connections and so on the code refers to Art. 110.14 and 110.14(A) Now...what is important is the method of the crimp MUST ensure the connection is a GOOD connection....many AHJ's will want to know the device used to make these connections. Also the spade connection MUST be approved for this application and rated for the application...also lets say the stranded wire is copper yet the spade connector is Aluminum.....does this not bring in Art 110.14 But....irrespective to that...we see it all the time and usually the connector will be rated for 120V/250V and listed AL/CU....but again their is a difference in using the same crimps you may buy in an auto parts store.... Must be listed and approved for the application...... Now.....I do not want to go into alot of detail....shame BOB is not here because I am sure he sees this alot....and I would venture to say it is used alot in Chicago area since they have to use conduit....but in most areas it will be solid. Crimp factor plays alot into the fact is the crimp method must ensure a GOOD solid connection.....in an overview...it is MUCH better as opposed to having stranded conductors on the standard terminal..... Important......rating of the terminal being used, approved for the application being used and quality of the crimping device and method used. Paul W. Abernathy,CMI,CPI,CME National Electrical Code Expert Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru Weekly Chat on Wednesdays -7:30 PM E.S.T * Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections" 2007 InterNACHI Member of the Year Last edited by pabernathy; 2/24/06 at 9:24 PM.. |
|
#6
|
||||
|
||||
|
Better late than never.......
Paul W. Abernathy,CMI,CPI,CME National Electrical Code Expert Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru Weekly Chat on Wednesdays -7:30 PM E.S.T * Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections" 2007 InterNACHI Member of the Year |
|
#7
|
||||
|
||||
|
"For you code lovers"....
Ya I was thinking code...hmmmm Ya that's the one.... I haven't seen too much of stranded around these here parts but I must admit it is installed for my central air compressor...only.... hmmm Wonder if that is acceptable.......PAUL waaaaaaaaahhhhhhhh |
|
#8
|
||||
|
||||
|
lol......Patrick I can't determine if you are harrassing me or playing with me...lol......Oh well.....either way...
I could probably argue the fact to allow or disallow them.....I can point out factors which would disallow them.....and most certainly can if they are attached to solid wire......anyway...... If this is a commercial inspection....and you are seeing it...Personally just let it go.......it is FAR better solution versus the obvious. Paul W. Abernathy,CMI,CPI,CME National Electrical Code Expert Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru Weekly Chat on Wednesdays -7:30 PM E.S.T * Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections" 2007 InterNACHI Member of the Year |
|
#9
|
||||
|
||||
|
Better eyes than me......I simply wanted to explain about the Spade Connectors......I did not actually look for anything else...lol
3M has terminals that are UL approved and rated for this application
Paul W. Abernathy,CMI,CPI,CME National Electrical Code Expert Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru Weekly Chat on Wednesdays -7:30 PM E.S.T * Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections" 2007 InterNACHI Member of the Year Last edited by pabernathy; 2/24/06 at 9:52 PM.. |
|
#10
|
||||
|
||||
|
OK,, thanks..
Oh I have a HVAC boiler question now.... Just kidding... I proding you with a no contact voltage detector.. I bought on Ebay a " Electrical Course for Apprentices and Journeymen" by Roland E. Palmquist with a revision by Joe Tedesco.... book for a few bucks used!! ...... It reminds me of my days in basic circuit analysis.. but in a much simpler form. I was much smarter back then....Now "I is dUm as a burnt out OCPD".... |
|
#11
|
||||
|
||||
|
lol...I hear ya.......
BTW....so I dont have to make a post......most of the Spade terminals are tin coated copper to reduce the corrosive effects...not aluminum....thought I better say that...lol Oh...I did need to add.......on one commercial job the AHJ jumped on a local electrical contractor who was co-working the job with our company who was using crimp-ons....and was using his klines to make the crimp..the AHJ said it was not the correct tool to ensure a GOOD connection and made the guy use the actual crimper that came with the terminals........Go Figure..... Paul W. Abernathy,CMI,CPI,CME National Electrical Code Expert Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru Weekly Chat on Wednesdays -7:30 PM E.S.T * Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections" 2007 InterNACHI Member of the Year Last edited by pabernathy; 2/24/06 at 10:09 PM.. |
|
#12
|
||||
|
||||
|
as stated one issue in this image is the (2) wires in one spade terminal assembly..it is most certainly only a single wire rated terminal assembly and has two wires entering it which violates Art 110.14(A)...
but in short the terminal assembly SHALL BE listed and identified as such if it allows multiple conductors. AS for the burnt mark...heck I dont know it is a burnt mark..I would think if this were the case the nylon insulator would have melted also...but who knows.....pictures dont tell much. Ok...anyone want a reason why solid wire is not good with these types of connections...getting away from code.....more practicle....because the crimp is not able to grab onto the solid wire effectivly and since copper expands and contracts...it works loose....where as with stranded it tends to go IN and wrap around and grab the conductors better.....thus holding better... Plus if you CRIMP too hard with a solid you could NICK the wire and damage it....which in its own causes issues with Art 110.14(A) Paul W. Abernathy,CMI,CPI,CME National Electrical Code Expert Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru Weekly Chat on Wednesdays -7:30 PM E.S.T * Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections" 2007 InterNACHI Member of the Year |
|
#13
|
|||
|
|||
|
Please Note:
jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#14
|
||||
|
||||
|
Joe,
List ME the reason for the non-approval of the application as it pertains to NEC. Many electricians today in commercial applications with open screw set breakers and stranded wire use this type of installation because the code does not dis-allow it. 3M makes the spade and closed loop terminals that are rated for up to 30A/250V applications and have insulated binding jackets as long as they are crimped in the proper matter....has nothing to do with torque as that is taken care of at the screw set itself. As an electrician I would be interested in knowing WHY you would not approve of this type of connection if the terminals are approved and meet the requirements of Art 110.14(A) and 110.14 Most home style breakers like SQ D and CH as designed in a way this is not possible, however open screw set type breakers are and in alot of commercial applications the open screw set style is still used and when dealing with stranded wire......we see it ALOT in commercial applications. IN other words.....would you turn it down because you have never seen it....or because you know it is a violation?...Important question to an AHJ.......without a reason opinions are nothing in the field as I have been known to go over the head of the AHJ IF they can't support a reason in understandable terms. I am not saying you are not right......could be I am wrong...hey....it's happened many times...lol.... Paul W. Abernathy,CMI,CPI,CME National Electrical Code Expert Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru Weekly Chat on Wednesdays -7:30 PM E.S.T * Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections" 2007 InterNACHI Member of the Year Last edited by pabernathy; 2/25/06 at 9:06 AM.. |
|
#15
|
|||
|
|||
|
Please Note:
jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Here's the rest of the story:
The termination in the picture [enlarged below] has a place for the conductor to be positioned so that the turn clockwise will assure a proper connection. I have seen some with some ridges, and others with a "bump". Using the crimps would be contrary to the UL Listing for that product at that time. I would also ask the major IBEW, NJATC, and other training agencies if they teach their apprentices to do this type of work! Also, the issues we discuss here should be handled courteously and professionally, and from here on we should remember that quoting the code is a "Mortal Sin Among Home Inspectors" and I personally will only quote a reference when specifically asked. Please let me know if there are any further questions. I respect all opinions and ask the same of mine -- "fellowship" Last edited by jtedesco1; 6/15/06 at 1:36 AM.. |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Nice Report on AL Wire Terminations - Enjoy | pabernathy | Electrical Inspections | 0 | 7/2/07 1:35 PM |
| Federal Panel: test the circuit breakers? | fbartlo | Electrical Inspections | 8 | 4/30/07 2:18 PM |
| Colorful breakers | cduphily | Electrical Inspections | 3 | 2/26/07 11:05 AM |