InterNACHI


Go Back   InterNACHI Inspection Forum > Specific Inspection Topics > Electrical Inspections

Notices

Electrical Inspections Contains discussions about electrical systems. This includes receptacles, panels, wiring, etc.

 
Reply
 
LinkBack Thread Tools
  #1  
Old 11/2/06, 5:59 AM
kkenny's Avatar
kkenny kkenny is offline
InterNACHI Member
 
Join Date: Jul 2006
Location: Oak Forest, IL
Posts: 475
Default Crouse-hinds Box GE Breaker?

Anybody know if you can use a GE breaker in a Crouse-Hinds panel? It fit in there, but it looks out of place to me.

Thanks
Kevin



Kevin M. Kenny, Sr.
Kenny Home Inspections
Oak Forest, Illinois 60452
Nachi #6070990

http://kennyhomeinspections.com

Reply With Quote
  #2  
Old 11/2/06, 6:24 AM
wsiegel wsiegel is offline
Active Poster
 
Join Date: Oct 2006
Location: Hialeah, Fl
Posts: 2,646
Please Note: wsiegel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Crouse-hinds Box GE Breaker?

Kevin,

You need to check the panel cover. It will tell you what breakers have been tested and approved to be used in the box. Most times it will say to use only (in this case) GE breakers. Using other breakers will void the warranty on the box and the box will not be UL listed any more.

Sometimes the box will say to use a like type breaker. When that happens, it must be written on the breaker that it is compatable with another brand. Many times you will not see this, as the marking may be on the side of the breaker, which is not visible without removing the breaker.

In this case, Im willining to bet that it is not compatabile. Electricians will use anything they happen to have on the truck.

If you did not read the panel cover, call it out for evaluation by a sparky (I'm sure you had other electrical issues). Say something like "have the electrician verify that the GE breaker is compatable with this box when repairing the other items listed".
Reply With Quote
  #3  
Old 11/2/06, 8:33 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Crouse-hinds Box GE Breaker?

Quote:
Originally Posted by wsiegel

In this case, Im willining to bet that it is not compatabile. Electricians will use anything they happen to have on the truck.
I will speak for Myself, Greg, Speedy ( Peter), Joe T, Brian and all good electricians nationwide in saying I resent that remark...lol

How about a redo to : " Some Jackleg, Lazy and good for nothing wanna be Electricians will use anything they happen to have on the truck, but not the electricians that come onto this message board...they RULE "

yeah...I like that version better

You GE Breaker will fit in : American Switch, Arrow Hart, Challenger ( Sylvania ) ,General Electric( Full Size Only ), General Switch, Murray ( Crouse Hinds ), Siemens (ITE,GOULD) and Westinghouse.......

BUT again very important is that the panel MUST allow for this.....just because it fits TECHNICALLY does not make it meet the listing and labeling instructions...so check the panel instructions and it will either way..

* You should only use (BLAH ) manufactuere in this enclosure

or it may say...

* Use of any other manufacture will void the manufacturers warranty

my opinion is this is a hard call..........really will cause a possible stink so do the following...

1.) Verify is fits properly
2.) Verify it correctly fits the panel cover knockout, If it does not fit it correctly thats a concern adn write that up....
3.) Verify the panel door will close properly
4.) In the possible missing panel label.....err on the side of the above 3 and it should be fine.

see....Thomas and Betts makes breakers as well that are classified to be in Crouse Hinds, Murray, GE and other panelboards so it is VERY hard for you to make the call on that.....unless you know all the makers and can actually see the labels as in the case of the T & B ones.......it is on the side of the breaker.........hard to see once it is installed...

Hope this helps



Paul W. Abernathy

Last edited by pabernathy; 11/2/06 at 8:50 AM..
Reply With Quote
  #4  
Old 11/2/06, 12:21 PM
wsiegel wsiegel is offline
Active Poster
 
Join Date: Oct 2006
Location: Hialeah, Fl
Posts: 2,646
Please Note: wsiegel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Crouse-hinds Box GE Breaker?

Appoligies to those of you good 'sparkies' who may be offended.

Unfortunately, the bad apples make the rest of the apples in the crate look bad also. You have to sift through to find the good ones.
Reply With Quote
  #5  
Old 11/2/06, 2:03 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Crouse-hinds Box GE Breaker?

Quote:
Unfortunately, the bad apples make the rest of the apples in the crate look bad also. You have to sift through to find the good ones.

lol...Same could be said about Home Inspectors....lol...but we all know the ones on here are the BEST....



Paul W. Abernathy
Reply With Quote
  #6  
Old 11/2/06, 9:15 PM
brian winkle brian winkle is offline
Active Poster
 
Join Date: Sep 2005
Location: Arizona
Posts: 454
Please Note: brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Crouse-hinds Box GE Breaker?

GE was very smart when they designed their breakers and panels. Their breakers would fit everyone elses panel, but no one elses breaker would fit their panel.

If you notice, most times when a non GE breaker is forced into a GE panel, the raised part does not line up with the deadfront cutout.
Reply With Quote
  #7  
Old 11/2/06, 9:45 PM
brian winkle brian winkle is offline
Active Poster
 
Join Date: Sep 2005
Location: Arizona
Posts: 454
Please Note: brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Crouse-hinds Box GE Breaker?

As far as using whats on the truck, I carry over $2,000 just in circuit breakers on my truck. I ALWAYS have the right one. And every time anything gets used, it goes into my PDA and gets replaced at the next parts house reload, which happens at least twice a week.

Before I went into business for myself I worked for some guys who never carried anything on the truck, and some who did but didn't have a clue where it was. I guess I learned what NOT to do from them. Being well equipped makes it so much more profitable without all the wasted time etc. Here are some photos of my truck if anyone is interested. http://i39.photobucket.com/albums/e1...e/Truck008.jpg

http://i39.photobucket.com/albums/e1...e/Truck005.jpg

http://i39.photobucket.com/albums/e1...e/Truck004.jpg

http://i39.photobucket.com/albums/e1...e/Truck003.jpg

http://i39.photobucket.com/albums/e1...e/Truck014.jpg

(the 2K in breakers are on the top left in the gray bins from that first pillar to the cab)
Reply With Quote
  #8  
Old 11/2/06, 9:48 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Crouse-hinds Box GE Breaker?

Brian....if only MY guys would LEARN for your pictures......wish we had those tall boy trucks also.....we have mini-vans...cramped at BEST !



Paul W. Abernathy
Reply With Quote
  #9  
Old 11/8/06, 11:21 PM
Joseph Hagarty,  CMI's Avatar
Joseph Hagarty, CMI Joseph Hagarty,  CMI is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Parkesburg, PA
Posts: 5,636
Default Re: Crouse-hinds Box GE Breaker?

......



Joseph P. Hagarty
joseph.hagarty@comcast.net
Main Line Inspections, Inc.
Phone: 610-399-3675
Email: MainLineHI@comcast.net

http://pa.nachi.org/mainlinepa/about.html
http://www.householdinspector.com

National President / NACHI (2003-2004)
NACHI Education Committee Member
Reply With Quote
  #10  
Old 11/9/06, 1:03 AM
Patrick Bolliger's Avatar
Patrick Bolliger Patrick Bolliger is offline
InterNACHI Member
 
Join Date: Aug 2005
Location: Chicago, IL
Posts: 890
Send a message via Skype™ to pbolliger
Default Re: Crouse-hinds Box GE Breaker?

Dang! Does this mean I have to change my GE breakers now in my Crouse-Hinds panel?

I have one with GE breakers....
Reply With Quote
  #11  
Old 11/9/06, 6:46 AM
jking2 jking2 is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Troy, MI
Posts: 183
Default Re: Crouse-hinds Box GE Breaker?

Brian,
The truck looks great. Good thing you don't have to drive on Michigan roads, or all that neatly stacked stuff would be on the floor!
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
AFCI Questions and Answers - Mike Holt pabernathy Electrical Inspections 7 4/16/12 9:51 PM
Electrical Guru Question? Breaker lock outs pdoane Electrical Inspections 4 9/7/07 2:05 PM
Crouse Hinds wsiegel Electrical Inspections 5 5/3/07 7:59 AM
Double Tapped Breaker tjohnson3 Electrical Inspections 8 4/20/07 9:04 AM


All times are GMT -4. The time now is 2:27 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts