Default CT can inside home

Well, not being an old timer nor an electrician, I've not seen this before. I consulted with my local "sparky" and his opinion was to have the local utility relocate to the exterior. My report stated that the utility is responsible for the transformer and the utility rep said the owner/seller is responsible for the can. I recommended that box be moved outside utility said they probably would not unless paid to do so. I asked them about their liability, considering that it is at floor level and easily accessible to kids, etc. The response was a sticker stating that the components were the property of the Public Utility District, NO locks on box. I feel like this is ultimately between the seller and the utility, however, my basic concern is safety. Any advise or opinions would be highly appreciated.
Attached Thumbnails
ct-can-inside-home-img_3542.jpg   ct-can-inside-home-img_3541.jpg   ct-can-inside-home-img_3543.jpg  



Randie L. Carley
Simcoe Inspection Services, LLC
(509)-250-2617 Cell
(509)-773-4864 Office

"It's not our differences that divide us,

it's our inablility to recognize, accept and

ultimately, celebrate those differences."

http://www.simcoeinspections.com/
Reply With Quote
  #2  
Old 10/19/07, 6:21 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: CT can inside home

I see no problems, save for the fact that a CT can is supposed to have a seal tag, lead seal, or a padlock provided by the utility.
Reply With Quote
  #3  
Old 10/19/07, 7:13 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: CT can inside home

The only problem I have with it is how EASY it was to get into it....I would consider it a liability if I had small kids in the house....they need to figure out a way to seal it up...

But alas......it is POCO's and well.....we could not do alot about it anyway so all is good.....just note that it should be sealed to prevent children and young adults wanting to end life quickly from getting into it.



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #4  
Old 10/20/07, 1:28 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: CT can inside home

I would call this a 230.70(A)(1) violation but I run on the stricter side of this ambiguous language.

Quote:
(1) Readily Accessible Location. The service disconnecting means shall be installed at a readily accessible location either outside of a building or structure or inside nearest the point of entrance of the service conductors.
It looks like there is an unnecessary amount of unprotected service equipment inside the building before you get to the service disconnect.
This is a judgement call so other inspectors will have other opinions.
Reply With Quote
  #5  
Old 10/20/07, 3:29 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 18,917
Default Re: CT can inside home

I have never seen CT Cabinets inside a home before and believe they should be at the exterior near the meter and usually are sealed by the Public Utilities for that area.

I have found this to reiforce that statement, which is in Colorado Springs,
http://www.csu.org/extrx/util_dev_sv..._chapter_5.pdf

And yet another that agrees in the same way.
http://www.chugachelectric.com/pdfs/...section300.pdf

It might be prudent to check with the requirements of the local jurisdiction of that particular area you are in at the time.

I can not imagine they would allow this in most places. But that is just my opinion.

Marcel
Reply With Quote
  #6  
Old 10/20/07, 4:10 PM
rcarley rcarley is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Goldendale, WA
Posts: 49
Default Re: CT can inside home

Thank you, again you've shown your professional attitude in offering help to those of us with less experience. You guys rock.



Randie L. Carley
Simcoe Inspection Services, LLC
(509)-250-2617 Cell
(509)-773-4864 Office

"It's not our differences that divide us,

it's our inablility to recognize, accept and

ultimately, celebrate those differences."

http://www.simcoeinspections.com/
Reply With Quote
  #7  
Old 10/20/07, 4:17 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: CT can inside home

Quote:
Originally Posted by mcyr
[COLOR=blue]I have never seen CT Cabinets inside a home before and believe they should be at the exterior near the meter...
You need to get out more.

There is no general prohibition against indoor CT cans, save for POCO rules. For every POCO that required them outdoors, there's one that will permit them indoors. Matter of fact, most larger indoor switchgear has the CT can (called CT section) built into the switchgear at the factory.

There is no hazard in the photo, other than the lack of sealing.
Reply With Quote
  #8  
Old 10/20/07, 4:27 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: CT can inside home

Pop quiz...

Homes that have a 200 amp CT can indoors, where they could have had traditional across the line metering equipment, normally also have the phone NID (demarc), and CATV splitters mounted indoors also. Why do you suppose that is? I know the answer, but I'm just encouraging a little expanded thinking...
Reply With Quote
  #9  
Old 10/20/07, 4:34 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 18,917
Default Re: CT can inside home

Quote:
Originally Posted by Marc D. Shunk
You need to get out more.

There is no general prohibition against indoor CT cans, save for POCO rules. For every POCO that required them outdoors, there's one that will permit them indoors. Matter of fact, most larger indoor switchgear has the CT can (called CT section) built into the switchgear at the factory.

There is no hazard in the photo, other than the lack of sealing.
I do go out once in awhile Mark.

And you are right, they do allow them indoors as you said, like this photo;

Attachment 15342 But this is not the standard for Residential and far from it.

They even have monitoring systems integegral also like this.
Attachment 15343

All I am saying is that different Utilities will prohibit interior CT cabinet installations, so it would be wise to check with that first before one inserts foot in month.

Marcel

Last edited by mcyr; 4/9/08 at 8:43 PM..
Reply With Quote
  #10  
Old 10/20/07, 4:44 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: CT can inside home

Quote:
Originally Posted by mcyr
All I am saying is that different Utilities will prohibit interior CT cabinet installations, so it would be wise to check with that first before one inserts foot in month.
I agree, but when you consider that the utility both provides and wires the actual CT, it would be safe to assume that this was a permitted installation during its time.
Reply With Quote
  #11  
Old 10/20/07, 4:58 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 18,917
Default Re: CT can inside home

Agree ,it was approved by someone on the original timeline.

But this is being inspected for a client and the client needs to be made aware of this installation, for any extensive repair that might occurr in the future, there might be a possibility of an upgrade to the electrical system an this portion there/of might have to be re-installed to more current standards and compliance to the local Authorities.

JMO

Marcel

Reply With Quote
  #12  
Old 10/20/07, 5:13 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: CT can inside home

Quote:
Originally Posted by mcyr
But this is being inspected for a client and the client needs to be made aware of this installation, for any extensive repair that might occurr in the future, there might be a possibility of an upgrade to the electrical system an this portion there/of might have to be re-installed to more current standards and compliance to the local Authorities.
I didn't realize you guys did that. I thought the present requirements were generally poo-poo'd. Seems like different inspectors have reminded me here many times that you're only concerned if it's safe or not. Perhaps you're talking about the value-added service that many inspectors provide, that being the "head's up" on what might have to happen if the equipment requires replacement?
Reply With Quote
  #13  
Old 10/20/07, 5:53 PM
cgoyette cgoyette is offline
Active Poster
 
Join Date: May 2007
Posts: 364
Please Note: cgoyette is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: CT can inside home

Could someone explain without acronyms what this CT (spelled out) is. In the south I have not seen one at least not what the picture shows in the first post. What does it do what are the concerns?


Curt
Reply With Quote
  #14  
Old 10/20/07, 6:05 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: CT can inside home

Quote:
Originally Posted by cgoyette
Could someone explain without acronyms what this CT (spelled out) is. In the south I have not seen one at least not what the picture shows in the first post. What does it do what are the concerns?


Curt
A CT stands for "current transformer", also known as "doughnuts" for slang. The CT in the picture is the round black thing that says "200" on it (that's the amp rating). It's just another way of measuring the electricity usage. The CT has little wires that connect to the meter outdoors that tell it how much electricity has flowed through the actual CT, to put it in simple terms. These are used on services above 400 amps in size normally, since a regular "across the line meter" (such as you would normally find for a dwelling) would be prohibitively large. Matter of fact, across the line meters for greater than 400 amps just don't really exist, so large services are CT metered. The service conductors run through the center of the CT.

You'll find indoor CT cans for 200 amp services in some homes where security was a prime concern. These are typically homes originally constructed for people like congressmen, company CEO's, CIA agents, and so fourth. The service conductors arrive from underground, directly from the padmount transformer. The service conductors run through the CT, and right to the panel's main. The metering conductors are just little wee conductors run to the meter outdoors. This prevents future ne'er do wells from pulling the meter to put the place in the dark, since the service conductors don't even appear at the meter.
Reply With Quote
  #15  
Old 10/20/07, 8:27 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,466
Default Re: CT can inside home

Quote:
Originally Posted by Marc D. Shunk
Pop quiz...
I'm just encouraging a little expanded thinking...

Wow...that hurts!



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Common Defects List by Age of House trausch Inspection Education & Training 10 6/12/06 5:52 AM
No Ashi / Nachi Conflict!! fcarrio Legislation, Licensing & Legal Issues for Inspectors 5 2/11/06 2:32 PM


All times are GMT -4. The time now is 10:28 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts