Default Cut Service Ground Wire.

Hello,

I recently completed an inspection on a 3 year old home and found the grounding wire cut about 12" below the meter. Have any inspectors run across this? Is there possibly another wire in the chaseway below the meter? How would you report this?

Howard Tennyson
Attached Thumbnails
cut-service-ground-wire-005.jpg  
Reply With Quote
Find an InterNACHI certified Washington Home Inspector (and anywhere else in North America)
  #2  
Old 3/28/09, 1:02 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Cut Service Ground Wire.

That may have been a grounding tail left out so that the utilities like phone and cable could tie their grounds to. Without seeing inside the panel it would be hard to tell. If another conductor is available perhaps from a ufer ground this may not be an issue. Did you look for a ground rod below the meter?
Reply With Quote
  #3  
Old 3/29/09, 7:38 PM
Howard Tennyson's Avatar
Howard Tennyson Howard Tennyson is offline
InterNACHI Member
 
Join Date: Mar 2008
Location: Warner Robins, GA
Posts: 21
Default Re: Cut Service Ground Wire.

Jim,

There was not a rod below the meter....
Reply With Quote
  #4  
Old 3/29/09, 7:44 PM
Wayne B. Wilson's Avatar
Wayne B. Wilson Wayne B. Wilson is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Powell, Tn
Posts: 8,234
Default Re: Cut Service Ground Wire.

Did you see a ground on the water line?
Reply With Quote
  #5  
Old 3/29/09, 11:18 PM
Frank P. Newman Frank P. Newman is offline
InterNACHI Member
 
Join Date: Aug 2007
Location: Dublin, GA
Posts: 668
Default Re: Cut Service Ground Wire.

If I cannot observe any system ground (after looking thoroughly) I call it out and refer it to a qualified electrician. I've never seen a situation as is shown in your picture



Frank P. Newman
Emerald City Inspections, LLC
Dublin, GA
Reply With Quote
  #6  
Old 4/5/09, 1:17 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Cut Service Ground Wire.

Very well could be the tail of a 6 AWG trying to comply with 250.94. However, it should be easy to determine this once you pull the panel inside. If you can't see other GEC's within the enclosure other than one 6 AWG leaving then you have your answer.....if you see others inside the panel then you have to look around.....do you see a 4AWG going to any water pipe....?...do you see one going to a ufer...?...are you able to find any ground rods...?

If you find yourself not able to answer those questions once the panel is pulled and you have other issues in your report most certainly call it out to have it evaluated by a licensed electrical contractor....why...? simply because of liability if you really want a single reason.

IN my areas ( Richmond,VA ) you will see this all the time and not because they are trying to comply with the intrasystem bonding requirement. They are CUT because people steal copper all the time. In a single day with a concentrated area a THIEF can earn quite a little take on stealing this.....Why hold a sign at the street corner beggin for a dollar when you can steal copper in 1/3rd the time.



Paul W. Abernathy
Reply With Quote
  #7  
Old 4/6/09, 7:54 AM
Howard Tennyson's Avatar
Howard Tennyson Howard Tennyson is offline
InterNACHI Member
 
Join Date: Mar 2008
Location: Warner Robins, GA
Posts: 21
Default Re: Cut Service Ground Wire.

Wayne, Frank & Paul,

Thanks so much for looking this over with me. The homeowner asked the builder to send out his electrician. The electrician contacted me and told me the grounding is a ufer grounding to the rebar in the slab... not visible above ground. I am still uncertain if seeing a 6 AWG in the panel connected to a ground bar is a sure sign the home is properly grounded.

Howard T.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Does the ground wire need a clamp? jkogel Electrical Inspections 7 10/9/08 5:30 AM
Electrical Safety Foundation International Links jtedesco1 Electrical Inspections 5 12/8/07 3:10 PM
Bare wire on old dryer or stove circuit: neutral or ground? fbartlo Electrical Inspections 9 8/28/06 1:08 AM
Ground wire in neutral bar, neutral to breaker, hot to ground? rmc3inspection Electrical Inspections 4 8/1/06 9:44 AM
Electrical Inspection Training for Home Inspectors jtedesco1 Inspection Education & Training 6 4/27/06 10:43 PM


All times are GMT -4. The time now is 8:46 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts