If I read this correctly with CU wiring I can double tap this breaker......am I correct? Even without the w style seizure clamp? It's hard to read but says (1) 8-14 AL/CU or (2) 10-14 CU only.
Thanks in advance..... "He is no fool who gives what he cannot keep to gain that which he cannot lose." Jim Elliot 1949 Gerald Wilcox Harvey, ND CMIA, RMT www.housecheckhomeinspections.com www.homeinspectorinnorthdakota.com 701.324.4075 Minot, ND Home Inspections Devil's Lake, ND Home Inspections Bismarck, ND Home Inspections Jamestown, ND Home Inspections Home Inspector in North Dakota North Dakota Home Inspection |
| Find an InterNACHI certified Ohio Home Inspector (and anywhere else in North America) |
|
#2
|
|||
|
|||
|
Please Note:
Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
You are correct. Two conductors properly sized and of a CU material can be terminated on that breaker.
|
|
#3
|
||||
|
||||
|
Thanks Jim!
"He is no fool who gives what he cannot keep to gain that which he cannot lose." Jim Elliot 1949 Gerald Wilcox Harvey, ND CMIA, RMT www.housecheckhomeinspections.com www.homeinspectorinnorthdakota.com 701.324.4075 Minot, ND Home Inspections Devil's Lake, ND Home Inspections Bismarck, ND Home Inspections Jamestown, ND Home Inspections Home Inspector in North Dakota North Dakota Home Inspection |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| AFCI Questions and Answers - Mike Holt | pabernathy | Electrical Inspections | 2 | 1/8/11 8:04 PM |
| Double Taps in Cutler Hammer Panel | bhartley | Electrical Inspections | 38 | 7/1/09 6:42 AM |
| Cutler Hammer panel with Square D breakers | bhartley | Electrical Inspections | 3 | 11/25/08 10:48 PM |
| Sq D 200 amp panel with Cutler Hammer Breaker | lfoster | Electrical Inspections | 7 | 6/28/07 11:06 PM |
| Great New Products- Cutler Hammer | pabernathy | Electrical Inspections | 8 | 3/10/07 8:46 PM |