Today, I inspecteda 200 AMP Cutler Hammer service panel, Cutler Hammer main, breakers are Square D, I could not find anywhere on cover that stated this is acceptable. Service panel was installed in new house three years ago. Any thoughts?
Thanks, for your help in advance |
|
#2
|
||||
|
||||
|
Violates NEC 2005 110.3B and should be called out.
|
|
#3
|
|||
|
|||
|
It it is not listed and labeled for those breakers, then it voids the warranty on the box an possilbly the UL rating.