Today, I inspecteda 200 AMP Cutler Hammer service panel, Cutler Hammer main, breakers are Square D, I could not find anywhere on cover that stated this is acceptable. Service panel was installed in new house three years ago. Any thoughts?
Thanks, for your help in advance |
|
#2
|
||||
|
||||
|
Violates NEC 2005 110.3B and should be called out.
James H. Bushart Professional Building Analyst, BPI Missouri, Kansas and Arkansas 314-803-2167 Inspecting in Aurora, Branson, Carthage, Granby, Joplin, Kimberling City, Monett, Mount Vernon, Neosho, Nixa, Purdy, Reed Spring, Republic, Springfield and surrounding areas. |
|
#3
|
|||
|
|||
|
Please Note:
wsiegel is a non-member guest and is in no way affiliated with InterNACHI or its members.
It it is not listed and labeled for those breakers, then it voids the warranty on the box an possilbly the UL rating.
|
|