Default Dead front question

Recently on an inspection, I inspected a distribution panel with the dead front painted to the wall. The paint was so thick you could not get a screw driver in the slot to remove. I used a razor knife to cut the paint from the edge and cleared out the slots so I could remove it. My fear is the home owner would attempt to get me to repaint the home. What is the normal procedure for this problem. This is a dammed if you do and dammed if you don’t situation. I feel my duty is to my client but I don’t need a law suit over paint damage.



David K. Smith

David@HISafetyFirst.com
www.HISafetyFirst.com
Cooper City Fl,
Reply With Quote
  #2  
Old 11/28/06, 7:53 PM
pdickerson pdickerson is offline
InterNACHI Member
 
Join Date: May 2004
Location: Clinton, WA
Posts: 341
Default Re: Dead front question

This has been discussed on this board in the past, and I remember quite a few members said they would not open a panel that was painted shut. I am with you though. I always make an effort to open up the panel. I have chipped away paint, moved larger furnature, taken apart pantry shelves, etc. It is too important to skip on account of a little paint IMO.
Reply With Quote
  #3  
Old 11/28/06, 7:58 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Dead front question

This is a judgement call. It really depends on "your gut feeling." Is it imperative that this cover be removed by me? Are there other mitigating factors telling me there will be problems in this panel that I should note? Will the damage be such that the home owner will surely be upset?

If, for whatever reason, you do not remove the cover, be sure and "recommend" that the panel be made accessible and inspected by a qualified electrician prior to the close of escrow.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #4  
Old 11/28/06, 8:16 PM
aiannuzzi aiannuzzi is offline
InterNACHI Member
 
Join Date: Sep 2004
Location: EAST PATCHOGUE, NY
Posts: 12
Default Re: Dead front question

I had just performed an inspection this week where the panel was located in a small closet in the basement . In front of the closet door was a couch, table and lamp which only allowed about six inches of open door space. Inside the closet the seller had stored rolls of fiberglass insulation and ceiling tiles.After snapping a few pics I explained to my client that a proper inspection of the panel could not be performed at this time as stated in my contract that i do not move furniture. the seller was already ticked off that I was in my 4th hour inspecting the 3 thousand square foot house. but i did offer to my client that if the area was cleared out for a small fee I would return to inspect the panel. The realtor was on site and wanted the deal to proceed and he moved all the obstruction with the sellers permission. Cost him a couple bucks to replace the lamp he broke while moving it
Reply With Quote
  #5  
Old 11/28/06, 8:45 PM
jking2 jking2 is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Troy, MI
Posts: 183
Default Re: Dead front question

I ask about or look at the access to attic, furnace, and electric panel when first entering the home. If the seller is there, then he/she has time to leisurely clear any obstructions while I inspect the rest of the house.
Reply With Quote
  #6  
Old 11/28/06, 9:11 PM
David K. Smith's Avatar
David K. Smith David K. Smith is offline
InterNACHI Member
 
Join Date: Nov 2006
Location: Cooper City, FL
Posts: 47
Default Re: Dead front question

Thanks guys, I'm new to NACHI and have only been inspecting homes for just over one year. I've been inspecting and reporting on a large hospital complex Jackson in south Florida for 29 years. I'm very impressed with your timely response. I look forward to further communication.



David K. Smith

David@HISafetyFirst.com
www.HISafetyFirst.com
Cooper City Fl,
Reply With Quote
  #7  
Old 11/29/06, 8:32 PM
Peter Foxe Smothers's Avatar
Peter Foxe Smothers Peter Foxe Smothers is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Shreveport, LA
Posts: 912
Default Re: Dead front question

I inspected a home about 18 months ago where the outer edges of the panel were taped to the wall. The home was in a lower income area. I removed the tape knowing that it would probally pull a little paint off, but to me I wanted to look inside the panel for my clients. Well I got lucky, the tape did not pull off the paint. When I was done I restuck the tape on the wall. I ended up getting a call from the listing agent the next day stating that the home owner was upset because the tape had become unstuck in a corner. I ended up going back that afternoon to re-tape the thing. Now I have a roll of masking tape in the truck.



Foxe Smothers ( Owner / Inspector )
Pelican State Inspection
Your Best Choice for Home Inspection in the Shreveport & Bossier City Area!


www.PelicanState.Net
www.ShreveportHomeInspector.net
www.BossierCityHomeInspector.net
foxe@pelicanstate.net
LSBHI #10399
Reply With Quote
  #8  
Old 11/29/06, 8:39 PM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,722
Default Re: Dead front question

Quote:
Originally Posted by dsmith6
I've been inspecting and reporting on a large hospital complex Jackson in south Florida for 29 years.
Damn...I thought it took me a long time to get my inspections and reports done!
Reply With Quote
  #9  
Old 11/29/06, 8:50 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,482
Default Re: Dead front question

Quote:
Originally Posted by dsmith6
I've been inspecting and reporting on a large hospital complex Jackson in south Florida for 29 years.
Just what I was thinking, Michael. Mr. Smith is going to need to speed up the inspections if he wants to make any $.



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #10  
Old 11/29/06, 9:40 PM
lclark's Avatar
lclark lclark is offline
Active Poster
 
Join Date: Jan 2005
Location: Wabash, IN
Posts: 191
Please Note: lclark is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Dead front question

I was in a house for 7 1/2 hours Monday. I didnt think I would ever find the end. Took me almost as long to do the report.
Reply With Quote
  #11  
Old 11/29/06, 9:47 PM
lclark's Avatar
lclark lclark is offline
Active Poster
 
Join Date: Jan 2005
Location: Wabash, IN
Posts: 191
Please Note: lclark is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Dead front question

http://www.yoherealtyinc.com/listing.asp?ID=77038626
Reply With Quote
  #12  
Old 12/3/06, 11:47 PM
Justin Watts Justin Watts is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Rancho Santa Margarita, CA
Posts: 771
Default Re: Dead front question

David,
I have run into many subpanels in condos that have painted over panels...and some yes, I have screwed up and torn the paint. Even using a blade attempting to cut a line so the cover would come off easier...

First thing I do now, I look at the panel, if the circuits are not "labeled" as required per the national electric code, I state in my report that a licensed electrican needs to label the circuits and should further inspect the panel.
Why tear off the panel and the paint.... If you are already recommending service and further evaluation....

Ofcourse, you can always state also that the panel was painted over and that removing the cover would cause cosmetic damage to the walls... and that at time of inspection you did not have the consent of the seller. (if they were not present).

Just my thoughts....
Justin.
www.americandreamhomeinspection.net
Reply With Quote
  #13  
Old 12/4/06, 7:47 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,684
Default Re: Dead front question

I remove every cover not matter what.

If I feel that removing the screws will also remove any paint, I simply ask the Listing agent for permission to score the outside of the cover.
Reply With Quote
  #14  
Old 12/4/06, 12:28 PM
bpotts bpotts is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Granbury, Tx
Posts: 4
Default Re: Dead front question

Help!!
What does N.E.C. say about the nipple that joins the meter box to the breaker panel? Clients Ex is electrical Contractor, wants rigid with lock washers, job contractor belives running a bonding wire through rigid PVC
ok. What does 2002 code say? Thanks
Reply With Quote
  #15  
Old 12/4/06, 2:23 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Dead front question

If you run service conductors through a metal raceway you also need bonding bushings.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Interesting Question? jmckenna1 Miscellaneous Discussion for Inspectors 9 11/25/07 2:13 PM
70 MPH... Is that my Trucks front wheel passing us!?! jsieg Miscellaneous Discussion for Inspectors 9 4/2/07 8:51 AM
Plumbing vent Routing Question kweiss Plumbing Inspections 7 11/1/06 10:57 PM
Rule of Thumb A/C sizing question from Practice Exam gliebig Inspecting HVAC Systems 9 5/25/06 2:38 AM
Answer to a common question about GFCI's jtedesco1 Electrical Inspections 4 1/12/06 10:29 PM


All times are GMT -4. The time now is 10:12 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts