  #1  
Old 5/1/09, 12:55 AM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,845
Default Defect??

House built in 2005

Last edited by bkelly2; 6/12/09 at 7:48 PM..
Reply With Quote
Find an InterNACHI certified Vermont Home Inspector (and anywhere else in North America)
  #2  
Old 5/1/09, 1:59 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 30,553
Default Re: Defect??

Quote:
Originally Posted by bkelly2 View Post
House built in 2005
Are you a code inspector?



He who knows nothing is closer to the truth than he whose mind is filled with falsehoods and errors - Thomas Jefferson - Founding Father

The democracy will cease to exist when you take away from those who are willing to work and give to those who would not. Thomas Jefferson

Never underestimate the difficulty of changing false beliefs by facts.
- Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
and
Minnesota Home Inspector

Reply With Quote
  #3  
Old 5/1/09, 2:00 AM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,845
Default Re: Defect??

Quote:
Originally Posted by mlarson View Post
Are you a code inspector?

Have been for over 20 years. Thanks for asking.

Is that your final answer??? Or would you like a life line??
Reply With Quote
  #4  
Old 5/1/09, 2:06 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 30,553
Default Re: Defect??

It is not a defect IMHO.

In fact it may exactly what is needed by the new owner.



He who knows nothing is closer to the truth than he whose mind is filled with falsehoods and errors - Thomas Jefferson - Founding Father

The democracy will cease to exist when you take away from those who are willing to work and give to those who would not. Thomas Jefferson

Never underestimate the difficulty of changing false beliefs by facts.
- Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
and
Minnesota Home Inspector

Reply With Quote
  #5  
Old 5/1/09, 2:09 AM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,845
Default Re: Defect??

Quote:
Originally Posted by mlarson View Post
It is not a defect IMHO.

In fact it may exactly what is needed by the new owner.
Excellent, my friend. I got me thinking today. But ...............
Reply With Quote
  #6  
Old 5/1/09, 10:27 AM
brian winkle brian winkle is offline
Active Poster
 
Join Date: Sep 2005
Location: Arizona
Posts: 454
Please Note: brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Defect??

If you are asking about code, four wire dryer circuits were first required in the 1996 code. What probably happened is the HO had a dryer with a 3 wire cord, and instead of changing the cord, which would have been the proper approach, they changed the receptacle.

In my opinion it should be mentioned.
Reply With Quote
  #7  
Old 5/2/09, 10:54 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,845
Default Re: Defect??

Quote:
Originally Posted by brian winkle View Post
If you are asking about code, four wire dryer circuits were first required in the 1996 code. What probably happened is the HO had a dryer with a 3 wire cord, and instead of changing the cord, which would have been the proper approach, they changed the receptacle.

In my opinion it should be mentioned.
That is kind of how I reported it Brian.
Reply With Quote
  #8  
Old 5/3/09, 1:02 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Defect??

Lets look at it beyond being a code issue. Is it a safety issue.......which would warrant it being reported.....Yes Indeed as it imply's that a case to neutral connection is taking place which can potentially put currents onto the metal casing of the dryer......not acceptable in 2005 and not today either....this was a good change in 1996 NEC for new installations.



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #9  
Old 5/3/09, 8:18 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,845
Default Re: Defect??

Quote:
Originally Posted by pabernathy View Post
Lets look at it beyond being a code issue. Is it a safety issue.......which would warrant it being reported.....Yes Indeed as it imply's that a case to neutral connection is taking place which can potentially put currents onto the metal casing of the dryer......not acceptable in 2005 and not today either....this was a good change in 1996 NEC for new installations.

Thanks Paul, that makes sense.
Reply With Quote
  #10  
Old 5/3/09, 9:34 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 18,909
Default Re: Defect??

You guys are making me doubt myself.
I had to go back and check.
Thanks

defect-sdc10698.jpg

Marcel
Reply With Quote
  #11  
Old 5/3/09, 9:38 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Defect??

Quote:
Originally Posted by mcyr View Post
You guys are making me doubt myself.
I had to go back and check.
Thanks

Attachment 28431

Marcel
On that image you posted.....even if not a code guy I would tell them to secure that NM Cable within 12" of that box and running it behind those studs even if tight is not considered supported per 334.30.

I don't really have to establish why it is a safety concern because the NEC as a minimum safety standard has already done that for me.....so even when not a code inspection.....still a safety concern.

lol...on a plumbing note I would tell them to apply the nailplates on those pipe running through the studs just to polish off the day.....



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #12  
Old 5/3/09, 9:46 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 18,909
Default Re: Defect??

Thanks Paul, the day of that photo, I had just finished releasing the wirings to frame in the dryer box at the last minute, but do not have a photo of the corrected proper installation of the wires. The electrician was not there at time of the photo.

I posted the picture to make sure it was a 10-3.
Reply With Quote
  #13  
Old 5/3/09, 9:49 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Defect??

Gotcha Fella....yep the old orange color gives it away every time.



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Where's the defect? kshepard Electrical Inspections 11 10/3/08 10:47 PM
Is secrecy a major structural defect in buyer protection? rwand1 Canadian Inspectors 0 1/26/08 5:56 PM
Is inadequate roof or attic ventilation a defect? gliebig Exterior Inspections 85 1/16/08 7:56 PM


All times are GMT -4. The time now is 6:23 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts