  #1  
Old 5/1/09, 12:55 AM
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 11,733
Default Defect??

House built in 2005



"Never ever threaten anyone in Camoflage"
Tim Wilson

"Not everyone follows the same path"
Governor Sanford, musings on the Appalachian Trail

Last edited by bkelly2; 6/12/09 at 7:48 PM..
Reply With Quote
Find an InterNACHI certified New Jersey Home Inspector (and anywhere else in North America)
  #2  
Old 5/1/09, 1:59 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: Defect??

Quote:
Originally Posted by bkelly2 View Post
House built in 2005
Are you a code inspector?



"Never underestimate the difficulty of changing false beliefs by facts."
Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
or
Minnesota Home Inspector

Reply With Quote
  #3  
Old 5/1/09, 2:00 AM
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 11,733
Default Re: Defect??

Quote:
Originally Posted by mlarson View Post
Are you a code inspector?

Have been for over 20 years. Thanks for asking.

Is that your final answer??? Or would you like a life line??



"Never ever threaten anyone in Camoflage"
Tim Wilson

"Not everyone follows the same path"
Governor Sanford, musings on the Appalachian Trail
Reply With Quote
  #4  
Old 5/1/09, 2:06 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: Defect??

It is not a defect IMHO.

In fact it may exactly what is needed by the new owner.



"Never underestimate the difficulty of changing false beliefs by facts."
Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
or
Minnesota Home Inspector

Reply With Quote
  #5  
Old 5/1/09, 2:09 AM
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 11,733
Default Re: Defect??

Quote:
Originally Posted by mlarson View Post
It is not a defect IMHO.

In fact it may exactly what is needed by the new owner.
Excellent, my friend. I got me thinking today. But ...............



"Never ever threaten anyone in Camoflage"
Tim Wilson

"Not everyone follows the same path"
Governor Sanford, musings on the Appalachian Trail
Reply With Quote
  #6  
Old 5/1/09, 10:27 AM
brian winkle brian winkle is offline
Active Poster
 
Join Date: Sep 2005
Location: Arizona
Posts: 454
Please Note: brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Defect??

If you are asking about code, four wire dryer circuits were first required in the 1996 code. What probably happened is the HO had a dryer with a 3 wire cord, and instead of changing the cord, which would have been the proper approach, they changed the receptacle.

In my opinion it should be mentioned.
Reply With Quote
  #7  
Old 5/2/09, 10:54 PM
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 11,733
Default Re: Defect??

Quote:
Originally Posted by brian winkle View Post
If you are asking about code, four wire dryer circuits were first required in the 1996 code. What probably happened is the HO had a dryer with a 3 wire cord, and instead of changing the cord, which would have been the proper approach, they changed the receptacle.

In my opinion it should be mentioned.
That is kind of how I reported it Brian.



"Never ever threaten anyone in Camoflage"
Tim Wilson

"Not everyone follows the same path"
Governor Sanford, musings on the Appalachian Trail
Reply With Quote
  #8  
Old 5/3/09, 1:02 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Defect??

Lets look at it beyond being a code issue. Is it a safety issue.......which would warrant it being reported.....Yes Indeed as it imply's that a case to neutral connection is taking place which can potentially put currents onto the metal casing of the dryer......not acceptable in 2005 and not today either....this was a good change in 1996 NEC for new installations.



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #9  
Old 5/3/09, 8:18 PM
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 11,733
Default Re: Defect??

Quote:
Originally Posted by pabernathy View Post
Lets look at it beyond being a code issue. Is it a safety issue.......which would warrant it being reported.....Yes Indeed as it imply's that a case to neutral connection is taking place which can potentially put currents onto the metal casing of the dryer......not acceptable in 2005 and not today either....this was a good change in 1996 NEC for new installations.

Thanks Paul, that makes sense.



"Never ever threaten anyone in Camoflage"
Tim Wilson

"Not everyone follows the same path"
Governor Sanford, musings on the Appalachian Trail
Reply With Quote
  #10  
Old 5/3/09, 9:34 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 12,356
Default Re: Defect??

You guys are making me doubt myself.
I had to go back and check.
Thanks

defect-sdc10698.jpg

Marcel




Cyr Home and Commercial Property Inspections

IAC2 Certified
NACHI04070211
http://co.nachi.org/inachiawards


Commercial Builder
CertainTeed
Master Shingle Applicator
Shingle Technology
Ouellet Associaties Inc.
http://www.oaconstruction.com/
Reply With Quote
  #11  
Old 5/3/09, 9:38 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Defect??

Quote:
Originally Posted by mcyr View Post
You guys are making me doubt myself.
I had to go back and check.
Thanks

Attachment 28431

Marcel
On that image you posted.....even if not a code guy I would tell them to secure that NM Cable within 12" of that box and running it behind those studs even if tight is not considered supported per 334.30.

I don't really have to establish why it is a safety concern because the NEC as a minimum safety standard has already done that for me.....so even when not a code inspection.....still a safety concern.

lol...on a plumbing note I would tell them to apply the nailplates on those pipe running through the studs just to polish off the day.....



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #12  
Old 5/3/09, 9:46 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 12,356
Default Re: Defect??

Thanks Paul, the day of that photo, I had just finished releasing the wirings to frame in the dryer box at the last minute, but do not have a photo of the corrected proper installation of the wires. The electrician was not there at time of the photo.

I posted the picture to make sure it was a 10-3.




Cyr Home and Commercial Property Inspections

IAC2 Certified
NACHI04070211
http://co.nachi.org/inachiawards


Commercial Builder
CertainTeed
Master Shingle Applicator
Shingle Technology
Ouellet Associaties Inc.
http://www.oaconstruction.com/
Reply With Quote
  #13  
Old 5/3/09, 9:49 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Defect??

Gotcha Fella....yep the old orange color gives it away every time.



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Where's the defect? kshepard Electrical 11 10/3/08 10:47 PM
Is secrecy a major structural defect in buyer protection? rwand1 Canadian Inspectors 0 1/26/08 5:56 PM
Is inadequate roof or attic ventilation a defect? gliebig Exterior 85 1/16/08 7:56 PM


All times are GMT -4. The time now is 7:03 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts