Default This is a defect because ...

The LFMC here is used to supply an AC unit.

What do you see that may not be acceptable?

This equipment is outside in front of a Las Vegas Casino.

See the picture in my next post, trying to do 3 things at once while teaching here in Milwaukee is not easy especially for an old man like me!

Last edited by jtedesco1; 4/19/06 at 8:53 AM..
Reply With Quote
  #2  
Old 4/19/06, 8:41 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: This is a defect because ...

Joe,

You link did not work...comes back invalid link.



Paul W. Abernathy
Reply With Quote
  #3  
Old 4/19/06, 8:54 AM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: This is a defect because ...

Here's the picture mentioned in #1 above.

Last edited by jtedesco1; 6/15/06 at 12:35 AM..
Reply With Quote
  #4  
Old 4/19/06, 11:32 AM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: This is a defect because ...

Bonding of the raceway may be a problem. Hard to tell
Reply With Quote
  #5  
Old 4/19/06, 1:16 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: This is a defect because ...

Quote:
Originally Posted by Greg Fretwell
Bonding of the raceway may be a problem. Hard to tell
Greg:

I was thinking about the "reducing donuts" where the LFMC angle connector is designed with a locknut seal to make contact with the full knockout.

The RD's interfere with the purpose of the fitting, which is raintight.
Reply With Quote
  #6  
Old 4/19/06, 1:31 PM
Pierre Belarge Pierre Belarge is offline
Active Poster
 
Join Date: Apr 2006
Posts: 202
Please Note: Pierre Belarge is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: This is a defect because ...

If that fitting is entering the enclosure above the live parts, it is a violation, If it enters below the live parts, it is acceptable.

312.2(A)Damp and Wet Locations.
(last paragraph)
For enclosures in wet locations, raceways or cables entering above the level of uninsulated live parts shall use fittings listed for wet locations.
Reply With Quote
  #7  
Old 4/19/06, 2:31 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: This is a defect because ...

Quote:
Originally Posted by Pierre Belarge
If that fitting is entering the enclosure above the live parts, it is a violation, If it enters below the live parts, it is acceptable.

312.2(A)Damp and Wet Locations.
(last paragraph)
For enclosures in wet locations, raceways or cables entering above the level of uninsulated live parts shall use fittings listed for wet locations.
Pierre:

This supply was installed before the rule you describe was added.

Are you saying that this existing work is now considered legal? Hmmmm?
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Is inadequate roof or attic ventilation a defect? gliebig Exterior Inspections 85 1/16/08 6:56 PM
Defect recognition bkelly1 Electrical Inspections 13 4/25/07 3:52 PM
Shingle defect? gschatz Exterior Inspections 9 5/12/06 4:57 PM
Homeowner special....defect or just informational? tneumann Plumbing Inspections 7 2/9/06 2:32 AM


All times are GMT -4. The time now is 2:28 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts