International Association of Certified Home Inspectors
|
|||||||
| Electrical Contains discussions about electrical systems. This includes outlets, panels, wiring, et cetera. |
![]() |
|
|
LinkBack | Thread Tools |
|
#1
|
|||
|
|||
|
Please Note:
jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
The LFMC here is used to supply an AC unit.
What do you see that may not be acceptable? This equipment is outside in front of a Las Vegas Casino. See the picture in my next post, trying to do 3 things at once while teaching here in Milwaukee is not easy especially for an old man like me! Last edited by jtedesco1; 4/19/06 at 9:53 AM.. |
|
#2
|
||||
|
||||
|
Joe,
You link did not work...comes back invalid link. Paul W. Abernathy,CMI,CEI,CEPE NECŪ Consultant/Columnist www.twitter.com/ElectricalGuru - ICC & IAEI Certified Electrical Inspector - ICC & IAEI Certified Electrical Plans Examiner - Look for my article in the Nov/Dec 2009 IAEI Magazine - 2007 "Top Gun" Winner - Mike Holt Enterprises " visit www.TheElectricalGuru.com Today !" |
|
#3
|
|||
|
|||
|
Please Note:
jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Here's the picture mentioned in #1 above.
Last edited by jtedesco1; 6/15/06 at 1:35 AM.. |
|
#4
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Bonding of the raceway may be a problem. Hard to tell
|
|
#5
|
|||
|
|||
|
Please Note:
jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
I was thinking about the "reducing donuts" where the LFMC angle connector is designed with a locknut seal to make contact with the full knockout. The RD's interfere with the purpose of the fitting, which is raintight. |
|
#6
|
|||
|
|||
|
Please Note:
Pierre Belarge is a non-member guest and is in no way affiliated with InterNACHI or its members.
If that fitting is entering the enclosure above the live parts, it is a violation, If it enters below the live parts, it is acceptable.
312.2(A)Damp and Wet Locations. (last paragraph) For enclosures in wet locations, raceways or cables entering above the level of uninsulated live parts shall use fittings listed for wet locations. |
|
#7
|
|||
|
|||
|
Please Note:
jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
This supply was installed before the rule you describe was added. Are you saying that this existing work is now considered legal? Hmmmm? |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Is inadequate roof or attic ventilation a defect? | gliebig | Exterior | 85 | 1/16/08 7:56 PM |
| Defect recognition | bkelly1 | Electrical | 13 | 4/25/07 4:52 PM |
| Shingle defect? | gschatz | Exterior | 9 | 5/12/06 5:57 PM |
| Homeowner special....defect or just informational? | tneumann | Plumbing | 7 | 2/9/06 3:32 AM |