Default What defects do you see in this main panel?

-No bonding device, and...
Attached Thumbnails
defects-do-you-see-main-panel-main-panel-1.jpg   defects-do-you-see-main-panel-main-panel-2.jpg  




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
InterNACHI Director of International Development
Director of Green Building

EXPERT WITNESS SERVICE
Conventional and Log homes

(303) 717-8940
Reply With Quote
Need a home inspection in Wisconsin? Check out InterNACHI's listing of Wisconsin certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 8/29/11, 1:58 PM
KEVIN WOOD's Avatar
KEVIN WOOD KEVIN WOOD is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 3,107
Default Re: What defects do you see in this main panel?

I think you better call Paul Abernathy to explain all the problems.
He can right a book on it. LOL



THE RIGHT TRAK
CIAQP, IAC2
Certified Master Inspector
kwoodinspections@hotmail.com
www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ
www.linkedin.com/in/kevinwoodiaq
OOVOO account kwoodinspections
Cell: 705-971-2096
Ph : 705-946-2676
Reply With Quote
  #3  
Old 8/29/11, 3:01 PM
Chiun D. Ng Chiun D. Ng is offline
InterNACHI Member
 
Join Date: Jun 2011
Location: South Florida
Posts: 131
Default Re: What defects do you see in this main panel?

I can see all kind of problems, undersize wires, double tapping.. and the panel is not even finish
Reply With Quote
  #4  
Old 8/29/11, 3:11 PM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 3,417
Send a message via ICQ to kshepard
Default Re: What defects do you see in this main panel?

What look like double-taps are actually neutral wires connected to neutral bus bars partially hidden beneath circuit breakers. Wire gauges were correct.




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
InterNACHI Director of International Development
Director of Green Building

EXPERT WITNESS SERVICE
Conventional and Log homes

(303) 717-8940
Reply With Quote
  #5  
Old 8/29/11, 4:29 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,251
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What defects do you see in this main panel?

All of the cables entering at the bottom left are a problem. That MAIN CB is backfed so that would require a retention clip, bolt or other device to hold it in place. Is the backfed CB the service disconnect?

Reply With Quote
  #6  
Old 8/29/11, 4:33 PM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: What defects do you see in this main panel?

Panel is not flush, or projecting out from a combustible surface. Unused wires should be terminated with wire nuts (good practice). No retainer clip on backfed breaker. Cables not attached to panel.

Edit ... RM, ya beat me to the punch by a few minutes while I was spell checking ... Rats! But in your rush to be the winner, ya missed a few things ...



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...

Last edited by roconnor; 8/30/11 at 9:23 AM..
Reply With Quote
  #7  
Old 8/29/11, 4:57 PM
KEVIN WOOD's Avatar
KEVIN WOOD KEVIN WOOD is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 3,107
Default Re: What defects do you see in this main panel?

Linas:

I will not teach in this area.
Certified Master Inspector does not mean I can explain the problems of a panel in detail.
The AHJ in this area is Paul Abernathy.
If he sees anything missed he will point it out in more detail and that is the CMI way.



THE RIGHT TRAK
CIAQP, IAC2
Certified Master Inspector
kwoodinspections@hotmail.com
www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ
www.linkedin.com/in/kevinwoodiaq
OOVOO account kwoodinspections
Cell: 705-971-2096
Ph : 705-946-2676
Reply With Quote
  #8  
Old 8/29/11, 6:53 PM
Terry Clayton Terry Clayton is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Arnold, MO
Posts: 246
Default Re: What defects do you see in this main panel?

Are the feeders trimmed to fit the breaker lugs, can't quite tell.
Reply With Quote
  #9  
Old 8/29/11, 9:51 PM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 3,417
Send a message via ICQ to kshepard
Default Re: What defects do you see in this main panel?

Quote:
Originally Posted by Robert Meier View Post
All of the cables entering at the bottom left are a problem. That MAIN CB is backfed so that would require a retention clip, bolt or other device to hold it in place. Is the backfed CB the service disconnect?

Yes, and the main disconnect is my main area of concern.




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
InterNACHI Director of International Development
Director of Green Building

EXPERT WITNESS SERVICE
Conventional and Log homes

(303) 717-8940
Reply With Quote
  #10  
Old 8/30/11, 1:36 AM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: What defects do you see in this main panel?

Are you concerned about the fact that the main breaker is backfed apparently without a retainer clip, or that it may not be rated as suitable for use as service equipment if backfed (would have to check the panel cover).



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
  #11  
Old 8/30/11, 1:52 AM
Nick Gromicko's Avatar
Nick Gromicko Nick Gromicko is offline
InterNACHI Member
 
Join Date: Aug 2002
Location: Valley Forge, PA
Posts: 30,614
Default Re: What defects do you see in this main panel?

I think the backfed, double-pole main breaker (which connects to both busbars, just like any other 240V breaker) being used as the service disconnect on this lug-only panel is what's throwing you Kenton, as that configuration is not the local practice in Boulder... but is fine, IMHO.

Anyway, I think it's a subpanel because the grounds and neutrals look to be split, but I'm not an electrician (which is why I referred to this remote distribution panel or secondary panelboard as a "subpanel" ).



Nick Gromicko, Certified Master Inspector

Find a Home Inspector
"Just as iron sharpens iron, one man sharpens another." Proverbs 27:17

Last edited by gromicko; 8/30/11 at 2:57 AM..
Reply With Quote
  #12  
Old 8/30/11, 4:55 AM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,251
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What defects do you see in this main panel?

Quote:
Originally Posted by Robert Meier View Post
All of the cables entering at the bottom left are a problem. That MAIN CB is backfed so that would require a retention clip, bolt or other device to hold it in place. Is the backfed CB the service disconnect?
Quote:
Originally Posted by kshepard View Post
Yes, and the main disconnect is my main area of concern.

OK, this is then the service which means that the GEC(s) from the grounding electrodes should terminate here on the neutral bus not on the equipment grounding bus. Also the neutral should be bonded to the enclosure. The backed CB is fine if it has the aforementioned clip, screw or other device to hold it in place. You would still have an issue with of the cables entering in the lower left of the panel and the panel edge not be flush with a combustible material (wood).
Reply With Quote
  #13  
Old 8/30/11, 9:05 AM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: What defects do you see in this main panel?

Quote:
Originally Posted by kwood View Post
I think you better call Paul Abernathy to explain all the problems. He can right a book on it. LOL
I only see a handful of issues ... most of them not major. Paul is not the local AHJ, but he is a master electrician (and a really good and knowledgeable guy also). But these are some pretty basic issues for an experienced inspector. As a master inspector you should at least be able to identify the issues.

JMO & 2-Nickels ...



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
Need a home inspection in Wisconsin? Check out InterNACHI's listing of Wisconsin certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 8/30/11, 9:11 AM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: What defects do you see in this main panel?

Quote:
Originally Posted by Robert Meier View Post
OK, this is then the service which means that the GEC(s) from the grounding electrodes should terminate here on the neutral bus not on the equipment grounding bus.
Good point ... but I see that all the time. Just like neutrals terminated on the ground bar (but apparently not in this panel) ...

Come on it's a "ground" wire ... it must go to the ground bar ...



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
  #15  
Old 8/30/11, 10:11 AM
KEVIN WOOD's Avatar
KEVIN WOOD KEVIN WOOD is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 3,107
Default Re: What defects do you see in this main panel?

Inspector points makes him the AHJ.
Not any code crap company.



THE RIGHT TRAK
CIAQP, IAC2
Certified Master Inspector
kwoodinspections@hotmail.com
www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ
www.linkedin.com/in/kevinwoodiaq
OOVOO account kwoodinspections
Cell: 705-971-2096
Ph : 705-946-2676

Last edited by kwood; 8/30/11 at 10:16 AM..
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Main panel double tap dmccauley Electrical Inspections 20 1/25/07 5:31 PM
Sub panel main tripping? crichiii Electrical Inspections 6 12/28/06 10:08 AM
Main Panel location dmacy Electrical Inspections 5 12/6/06 6:32 PM
Main disconnect at meter instead of main panel. OK? kshepard Electrical Inspections 14 11/8/06 6:24 PM
Bad electrical problem Pest Guy Electrical Inspections 4 1/20/06 9:26 PM


All times are GMT -4. The time now is 8:47 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts