-No bonding device, and...
Kenton Shepard, InterNACHI member # 04082383 Certified Master Inspector (CMI) InterNACHI Director of International Development Director of Green Building EXPERT WITNESS SERVICE Conventional and Log homes (303) 717-8940
|
| Need a home inspection in Wisconsin? Check out InterNACHI's listing of Wisconsin certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#2
|
||||
|
||||
|
I think you better call Paul Abernathy to explain all the problems.
He can right a book on it. LOL THE RIGHT TRAK CIAQP, IAC2 Certified Master Inspector kwoodinspections@hotmail.com www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ www.linkedin.com/in/kevinwoodiaq OOVOO account kwoodinspections Cell: 705-971-2096 Ph : 705-946-2676 |
|
#3
|
|||
|
|||
|
I can see all kind of problems, undersize wires, double tapping.. and the panel is not even finish
|
|
#4
|
||||
|
||||
|
What look like double-taps are actually neutral wires connected to neutral bus bars partially hidden beneath circuit breakers. Wire gauges were correct.
Kenton Shepard, InterNACHI member # 04082383 Certified Master Inspector (CMI) InterNACHI Director of International Development Director of Green Building EXPERT WITNESS SERVICE Conventional and Log homes (303) 717-8940
|
|
#5
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
All of the cables entering at the bottom left are a problem. That MAIN CB is backfed so that would require a retention clip, bolt or other device to hold it in place. Is the backfed CB the service disconnect?
|
|
#6
|
||||
|
||||
|
Panel is not flush, or projecting out from a combustible surface. Unused wires should be terminated with wire nuts (good practice). No retainer clip on backfed breaker. Cables not attached to panel.
Edit ... RM, ya beat me to the punch by a few minutes while I was spell checking ... Rats! But in your rush to be the winner, ya missed a few things ... Robert O'Connor, PE Consulting Engineer & Inspector LIU CW Post Adjunct Professor NACHI Education Committee www.reporthost.com/-rjo I am absolutely amazed sometimes by how much thought goes into doing things wrong ... Last edited by roconnor; 8/30/11 at 9:23 AM.. |
|
#7
|
||||
|
||||
|
Linas:
I will not teach in this area. Certified Master Inspector does not mean I can explain the problems of a panel in detail. The AHJ in this area is Paul Abernathy. If he sees anything missed he will point it out in more detail and that is the CMI way. THE RIGHT TRAK CIAQP, IAC2 Certified Master Inspector kwoodinspections@hotmail.com www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ www.linkedin.com/in/kevinwoodiaq OOVOO account kwoodinspections Cell: 705-971-2096 Ph : 705-946-2676 |
|
#8
|
|||
|
|||
|
Are the feeders trimmed to fit the breaker lugs, can't quite tell.
|
|
#9
|
||||
|
||||
|
Yes, and the main disconnect is my main area of concern.
Kenton Shepard, InterNACHI member # 04082383 Certified Master Inspector (CMI) InterNACHI Director of International Development Director of Green Building EXPERT WITNESS SERVICE Conventional and Log homes (303) 717-8940
|
|
#10
|
||||
|
||||
|
Are you concerned about the fact that the main breaker is backfed apparently without a retainer clip, or that it may not be rated as suitable for use as service equipment if backfed (would have to check the panel cover).
Robert O'Connor, PE Consulting Engineer & Inspector LIU CW Post Adjunct Professor NACHI Education Committee www.reporthost.com/-rjo I am absolutely amazed sometimes by how much thought goes into doing things wrong ... |
|
#11
|
||||
|
||||
|
I think the backfed, double-pole main breaker (which connects to both busbars, just like any other 240V breaker) being used as the service disconnect on this lug-only panel is what's throwing you Kenton, as that configuration is not the local practice in Boulder... but is fine, IMHO.
Anyway, I think it's a subpanel because the grounds and neutrals look to be split, but I'm not an electrician (which is why I referred to this remote distribution panel or secondary panelboard as a "subpanel" Nick Gromicko, Certified Master Inspector Find a Home Inspector "Just as iron sharpens iron, one man sharpens another." Proverbs 27:17 Last edited by gromicko; 8/30/11 at 2:57 AM.. |
|
#12
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
OK, this is then the service which means that the GEC(s) from the grounding electrodes should terminate here on the neutral bus not on the equipment grounding bus. Also the neutral should be bonded to the enclosure. The backed CB is fine if it has the aforementioned clip, screw or other device to hold it in place. You would still have an issue with of the cables entering in the lower left of the panel and the panel edge not be flush with a combustible material (wood). |
|
#13
|
||||
|
||||
|
Quote:
JMO & 2-Nickels ... Robert O'Connor, PE Consulting Engineer & Inspector LIU CW Post Adjunct Professor NACHI Education Committee www.reporthost.com/-rjo I am absolutely amazed sometimes by how much thought goes into doing things wrong ... |
| Need a home inspection in Wisconsin? Check out InterNACHI's listing of Wisconsin certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#14
|
||||
|
||||
|
Quote:
Come on it's a "ground" wire ... it must go to the ground bar ... Robert O'Connor, PE Consulting Engineer & Inspector LIU CW Post Adjunct Professor NACHI Education Committee www.reporthost.com/-rjo I am absolutely amazed sometimes by how much thought goes into doing things wrong ... |
|
#15
|
||||
|
||||
|
Inspector points makes him the AHJ.
Not any code crap company. THE RIGHT TRAK CIAQP, IAC2 Certified Master Inspector kwoodinspections@hotmail.com www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ www.linkedin.com/in/kevinwoodiaq OOVOO account kwoodinspections Cell: 705-971-2096 Ph : 705-946-2676 Last edited by kwood; 8/30/11 at 10:16 AM.. |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Main panel double tap | dmccauley | Electrical Inspections | 20 | 1/25/07 5:31 PM |
| Sub panel main tripping? | crichiii | Electrical Inspections | 6 | 12/28/06 10:08 AM |
| Main Panel location | dmacy | Electrical Inspections | 5 | 12/6/06 6:32 PM |
| Main disconnect at meter instead of main panel. OK? | kshepard | Electrical Inspections | 14 | 11/8/06 6:24 PM |
| Bad electrical problem | Pest Guy | Electrical Inspections | 4 | 1/20/06 9:26 PM |