Default Re: What defects do you see in this main panel?

The equipment grounding conductors terminate on the grounding bus bar which is fastened directly to the metal panel. The neutrals terminate on the neutral bus bars which float, are bonded to each other, but lack a bonding strap or screw. I recommended a bonding device be installed. I don't see any problem with that.
This is the first time I've ever heard the term "backfed" breaker used except with a grid-tie PV system. Never heard it mentioned on a job, an inspection , or by any electrician. It's not mentioned in any of the inspection books we have (including Paul's) and I've never seen one in Colorado. My impression is that they're more common back east.
Ya think that maybe sometimes things are done differently in different parts of the country?




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
InterNACHI Director of International Development
Director of Green Building

EXPERT WITNESS SERVICE
Conventional and Log homes

(303) 717-8940
Reply With Quote
Need a home inspection in New Mexico? Check out InterNACHI's listing of New Mexico certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #17  
Old 8/30/11, 1:24 PM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: What defects do you see in this main panel?

Backfed panels are sometimes found in my neck of the woods. The big thing is the main breaker/disconnect needs some type of devise (clip, bolt, bracket) to hold the breaker in place. Otherwise it could come loose and still be energized by the service wires ...

Example backfed panel with retainer bolt ...
http://www.nachi.org/forum/attachmen...aker-screw.jpg
http://www.nachi.org/forum/attachmen...0a-breaker.jpg
http://www.nachi.org/forum/attachmen...iner-screw.jpg

Another more sticky issue is that some panels are not listed for use as service equipment with a backfed main breaker.



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
  #18  
Old 8/30/11, 2:04 PM
KEVIN WOOD's Avatar
KEVIN WOOD KEVIN WOOD is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 3,107
Default Re: What defects do you see in this main panel?

My point exactly Kenton!
Unless you have been everywhere you can't make comments on Electrical this complicated without being in the same area. Yes there are evident things up front but I also have not seen this type of set up here either. Back fed panels sometimes but not very often.



THE RIGHT TRAK
CIAQP, IAC2
Certified Master Inspector
kwoodinspections@hotmail.com
www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ
www.linkedin.com/in/kevinwoodiaq
OOVOO account kwoodinspections
Cell: 705-971-2096
Ph : 705-946-2676
Reply With Quote
  #19  
Old 8/31/11, 8:02 AM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: What defects do you see in this main panel?

I can respect when someone posts a question about something they havent seen before that isn't covered in reference books they have, as opposed to just disclaiming everything for a master electrician to figure out.



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Main panel double tap dmccauley Electrical Inspections 20 1/25/07 5:31 PM
Sub panel main tripping? crichiii Electrical Inspections 6 12/28/06 10:08 AM
Main Panel location dmacy Electrical Inspections 5 12/6/06 6:32 PM
Main disconnect at meter instead of main panel. OK? kshepard Electrical Inspections 14 11/8/06 6:24 PM
Bad electrical problem Pest Guy Electrical Inspections 4 1/20/06 9:26 PM


All times are GMT -4. The time now is 8:47 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts