I just ran across a very unusual situation. I was inspecting a 200 amp C-H main service panel and there were two unusual items mounted to the side. They were Delta surge capacitor M/N CA302-R and a Delta lightning arrestor M/N LA302-R.

Now the fun part. They were triple tapped to a 30 amp 220 VAC breaker (One on each leg). The feeders to these products are about AWG-12.

So...

I went to http://www.deltasurgeprotectors.com/...llmod=7&page=3 and the manufacturer's instructions show to do this. The reason for the tripple tapping is each unit has two "hot" leads (one per leg) and there were two separate units.


Questions.
  1. Shouldn't they be pigtailed since the last I knew C-H breakers are not rated for double taps besides the fact the wire gauges are different (A big No-No)?
  2. Does this product even work?
Thanks



Greg Liebig, Owner
Sheboygan Wisconsin Home Inspector

4-Square Home Inspections, LLC
Where Knowledge will put your Mind at Ease ©
Sheboygan, WI 53081
(920) 451-4646

www.sheboyganhomeinspector.com
www.4squarehi.com
Like Us on Facebook
Follow Us on Linked-In
Reply With Quote
  #2  
Old 9/23/08, 9:23 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Delta Surge Protection HELP!

They work all right.

This is a contradiction between TVSS manufacturer's instructions and breaker instructions, so it would seem. I seriously doubt the place is going to burn down today or tomorrow because of it, but it's an interesting puzzle in the mean time.

You're in a lucky position, in that you have the ability to note what you observed, and let other people sort out the solution. Honestly, if I was called out on that to correct it, as an electrician, I really don't know what I'd do. Probably tear it out and sell them another brand of TVSS. The drawings on Delta's website look like a kindergartner drew them, so it makes me suspicious of their product in general.
Reply With Quote
  #3  
Old 9/23/08, 11:21 PM
Gregory A. Liebig's Avatar
Gregory A. Liebig Gregory A. Liebig is offline
InterNACHI Member
 
Join Date: May 2006
Location: Sheboygan, WI
Posts: 687
Default Re: Delta Surge Protection HELP!

Here are some pictures to share. The first is the opened panel. The 2nd shows the Surge Protector and the Lightning Arrestor. The 3rd shows the Tripple Taps.
Attached Thumbnails
delta-surge-protection-help-devices_1.jpg   delta-surge-protection-help-devices.jpg   delta-surge-protection-help-surge_wiring.jpg  



Greg Liebig, Owner
Sheboygan Wisconsin Home Inspector

4-Square Home Inspections, LLC
Where Knowledge will put your Mind at Ease ©
Sheboygan, WI 53081
(920) 451-4646

www.sheboyganhomeinspector.com
www.4squarehi.com
Like Us on Facebook
Follow Us on Linked-In
Reply With Quote
  #4  
Old 9/25/08, 11:18 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Delta Surge Protection HELP!

I believe the issue is they simply did not have the space to install them properly. As to if they work....in theory they should but it would depend also on the age of these units and IF they are still providing the protection they were orginally installed for.

I agree with Marc ( ironically ) in that chances are they are fine but the method of which they are installed are improper and should be called out. I would venture to say the maximum circuit breaker they would be protected from should be no more than a 15A OCPD.....this is how the new versions of TVSS ( SPD's now ) from Eaton are required to be done.

Now in regards to the Double taps ( I did not look at that picture )....eaton does make the CH version for 15A and 20A breakers which does allow multiple taps (2 actually ) and only done if the conductors are of the same size as doing otherwise would be a problem as well.

Hope this helps.

BTW...I should add that the 30A showing would not be allowed for a double tap....only the 15A and 20A versions as the lug on a 30A is for a single conductor only.



Paul W. Abernathy
Reply With Quote
  #5  
Old 9/27/08, 4:24 PM
Pierre Belarge Pierre Belarge is offline
Active Poster
 
Join Date: Apr 2006
Posts: 202
Please Note: Pierre Belarge is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Delta Surge Protection HELP!

A couple of things with this product.

1. I do not see a listing, either from UL or any other NRTL.

2. When installing conductor for arrestors or TVSS, it is a known that the conductors should be as short and as straight as is possible. The installation pages show too much length and way too sharp an angle for bends.

I as an inspector would have issues with this installation.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
AFCI Questions and Answers - Mike Holt pabernathy Electrical Inspections 7 4/16/12 9:51 PM
What do you think? Can this work for you? jtedesco1 Electrical Inspections 21 2/26/11 2:00 PM
Where is it written.... bgromicko General Inspection Discussion 21 1/19/08 9:02 PM
Electrical Inspection Training for Home Inspectors jtedesco1 Inspection Education & Training 6 4/27/06 10:43 PM


All times are GMT -4. The time now is 2:30 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts