Default derating

i saw mention of this on another message board and its giving me pause.

Can someone please explain, in simple terms, the theory of derating of the wires when there are more conductors in a conduit or raceway than there should be?

I understand higher temps mean lower amp carrying ability of the conductor.

I understand that the sheathing of the wire (conductors)
is rated for a certain temp. I understsnd the danger of crimping the wire.

Is this something we should be delving into as Home Inspectors???
I mean, beyond noting the obvious "super crowded" conduit filled with wire, where do we draw the line?

Last edited by jtribuzio; 3/31/08 at 3:12 AM..
Reply With Quote
  #2  
Old 3/31/08, 3:43 AM
Joseph Tribuzio's Avatar
Joseph Tribuzio Joseph Tribuzio is offline
InterNACHI Member
 
Join Date: Jul 2007
Location: Harwood Heights, IL 60706
Posts: 708
Default Re: derating

This is a way to adjust for the amp and voltage drop? yes ?

Seems to be the domain of a experienced licensed elecrician imo
Reply With Quote
  #3  
Old 3/31/08, 5:36 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,049
Default Re: derating

It's a matter of heat dissipation or the lack thereof.



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

[/I]
Reply With Quote
  #4  
Old 3/31/08, 12:23 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: derating

More wires in a pipe = more heat buildup

More heat buildup = insulation of the conductors gets hotter

conductor insulation exposed to heat for long periods of time = brittle conductor insulation

Brittle conductor insulation = insulation failure

Insulation failure = possible fire, catastrophic equipment damage, etc.

Same thing goes for bundles of cables that ara bundled for great lengths.
Reply With Quote
  #5  
Old 3/31/08, 1:02 PM
Joseph Tribuzio's Avatar
Joseph Tribuzio Joseph Tribuzio is offline
InterNACHI Member
 
Join Date: Jul 2007
Location: Harwood Heights, IL 60706
Posts: 708
Default Re: derating

I see Marc, and Michael, thank you.

Now- how can this be determined for the whole house?
this is just for conduit in hot areas like an attic, correct?
Reply With Quote
  #6  
Old 3/31/08, 1:17 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: derating

Quote:
Originally Posted by jtribuzio
this is just for conduit in hot areas like an attic, correct?
No, it applies to all conductors in conduit, regardless of where they're installed. As the number of conductors in the bundle increases, they "self heat". There is additional "math" to account for when the conduit is also installed in a hot ambient, like in an attic or running accross a flat roof.

The actual determination of whether a conduit is overloaded or not, in accordance with the gauge of conductor installed, is way beyond the scope of a home inspector's purview. If you see some crazy amount of conductors coming out of a pipe into a panel, or lots of cables tied together in a bundle running across a basement, the best thing you can do is call it out as suspicious enough to warrant a look-see by an electrician.
Reply With Quote
  #7  
Old 3/31/08, 1:50 PM
Joseph Tribuzio's Avatar
Joseph Tribuzio Joseph Tribuzio is offline
InterNACHI Member
 
Join Date: Jul 2007
Location: Harwood Heights, IL 60706
Posts: 708
Default Re: derating

Thank you MARC, I think i understand now.

In the past i have commented on " too many wires in conduit"

before, i imagined that the action of pulling and forcing it in there would damage the outer coating, leading to arcs and sparks. i guess thats possible too, especially if the conduit is bent wrong.
Reply With Quote
  #8  
Old 3/31/08, 2:01 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: derating

Where derating is probably ignored the most is large conductors in the attic.
Usually 240.4(D) covers you on small conductors (14/12) since the breaker size is artificially lower than the 60c column and you can derate from the 90c column. Not so much on #10.
When you might have a problem is if you used the label to size a conductor for an A/C compressor @ 75c and then ran it through a 130 degree attic. We usually get away with it in Florida by having the air handler and condenser on the same circuit and you size the circuit for the strip heaters. When the strip heat is on the attic is cool so the derating table is actually a plus number.
The condenser is usually considerably smaller than strip heaters. In my case the air handler is on 6ga which extends to the 40a disconnect for the condenser. I could have used 12ga for the whip (23a on the label) but I went nuts and used #10. Again with an ambient of close to 100f that is probably closer to right. If you had the condenser in the sun (dumb idea) you might want to figure an ambient more like 130.
Reply With Quote
  #9  
Old 4/6/08, 10:55 AM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: derating

http://www.copper.org/about/pressrel...5_01_13_4.html
Reply With Quote
  #10  
Old 4/6/08, 11:12 AM
Joseph Tribuzio's Avatar
Joseph Tribuzio Joseph Tribuzio is offline
InterNACHI Member
 
Join Date: Jul 2007
Location: Harwood Heights, IL 60706
Posts: 708
Default Re: derating

Intersting stuff.

this can be very serious.
It will be way better when the entire distribution panel is ARC FAULT protected.
Reply With Quote
  #11  
Old 4/6/08, 12:15 PM
Joseph Tribuzio's Avatar
Joseph Tribuzio Joseph Tribuzio is offline
InterNACHI Member
 
Join Date: Jul 2007
Location: Harwood Heights, IL 60706
Posts: 708
Default Re: derating

ok, I found some charts in my pocket ref book that help

I see some wire ( sheathing ) is rated at 140 degrees F, ( TF, UF)
some are rated at 167 F (THW,THWN,ZW,RHW, THHW, XHHW )
And there are a lot rated at 194 F

ampacity of a 140 F rated sheathing 12 awg wire is 30 at 86 degrees, BUT FOR AMBIENT TEMPS ABOVE THAT, there needs to be adjustments made.

So if that wire is in an attic that is 115 degrees F, You multiply ampacity by .58 and find that the wire now has an ampacity rating of 17.4.

has anyone seen the newest charts or info from NEC on this and is it available online?

i can try to post it here, but i dont know if what i have is still the standard
Reply With Quote
  #12  
Old 4/6/08, 12:23 PM
Joseph Tribuzio's Avatar
Joseph Tribuzio Joseph Tribuzio is offline
InterNACHI Member
 
Join Date: Jul 2007
Location: Harwood Heights, IL 60706
Posts: 708
Default Re: derating

""has anyone seen the newest charts or info from NEC on this and is it available online?"" -- me

AH ! wait a minute , THANK YOU Mr Joe Tedesco you already did that - That link is great!
Reply With Quote
  #13  
Old 4/6/08, 12:27 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: derating

The NEC recently addressed rooftops ref derating, I bet attics are next
Reply With Quote
  #14  
Old 4/6/08, 12:34 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,049
Default Re: derating

Quote:
Originally Posted by jtribuzio
""has anyone seen the newest charts or info from NEC on this and is it available online?"" -- me

AH ! wait a minute , THANK YOU Mr Joe Tedesco you already did that - That link is great!
Free Access(read only) to NEC 2008



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

[/I]
Reply With Quote
  #15  
Old 4/6/08, 1:16 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: derating

Gerald Newton has an interesting article about table 310.15 and the Neher-McGrath formula in general. I imagine it is on electrician.com, his web site. I can't seem to find a copy on my hard drive. It is something like "Where did 310.16 come from"
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Newer stuff dmacy Electrical Inspections 15 7/22/06 8:51 AM


All times are GMT -4. The time now is 2:30 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts