Default Detached garage

Is this right? There's one shop light and one receptacle.
Attached Thumbnails
detached-garage-058nachi.jpg  

Last edited by rwilcox; 9/11/07 at 12:40 PM..
Reply With Quote
  #2  
Old 9/11/07, 12:49 PM
William E. Siegel William E. Siegel is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Hialeah, Fl
Posts: 1,788
Default Re: Detached garage

It may work, but you have three ground wires under one screw, which is not allowed, and the top feeds are double tapped, which is not allowed, and you have white wires improperly marked and being used as hot wires.
Reply With Quote
  #3  
Old 9/11/07, 1:15 PM
Bruce M. Graham, III's Avatar
Bruce M. Graham, III Bruce M. Graham, III is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Gainesville, FL
Posts: 1,605
Default Re: Detached garage

Where are your neutrals?



Bungalows to Mansions
Professional Inspection Services, LLC dba
1st Inspection Services
Bruce M. Graham III
Gainesville, FL 32608
352 871 8989
NACHI05091592
ICC 5268478
www.1stinspectionsfl.com
www.bungalowstomansions.com
Reply With Quote
  #4  
Old 9/11/07, 1:29 PM
Mike Whitt's Avatar
Mike Whitt Mike Whitt is offline
Active Poster
 
Join Date: Sep 2005
Location: North Carolina
Posts: 474
Please Note: Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Detached garage

Quote:
Originally Posted by rwilcox
Is this right? There's one shop light and one receptacle.
No


there are several things wrong
Reply With Quote
  #5  
Old 9/11/07, 2:04 PM
rwilcox rwilcox is offline
InterNACHI Member
 
Join Date: Jul 2005
Location: Blairsville, GA
Posts: 9
Thumbs down Re: Detached garage

Thanks for the help, this is one of 4 DIY subpanel jobs and they all have issues, I will refer this mess to Sparky.
Reply With Quote
  #6  
Old 9/11/07, 2:49 PM
Thomas H. Dietrich's Avatar
Thomas H. Dietrich Thomas H. Dietrich is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: Detached garage

Is this back-feed through the breaker supplying two 240(ish) circuits?

Just thinking out-loud, official answer it looks confusing.

tom
Reply With Quote
  #7  
Old 9/11/07, 5:19 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,033
Default Re: Detached garage

There is nothing proper about this installation. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #8  
Old 9/11/07, 5:28 PM
Frank P. Newman Frank P. Newman is offline
InterNACHI Member
 
Join Date: Aug 2007
Location: Dublin, GA
Posts: 505
Default Re: Detached garage

I don't think I've ever seen the likes of that before...

I wonder what the rest of the 'wiring' looks like?



Frank P. Newman
Emerald City Inspections, LLC
Dublin, GA

Last edited by fnewman; 9/12/07 at 4:04 PM..
Reply With Quote
  #9  
Old 9/11/07, 11:28 PM
brian winkle brian winkle is offline
Active Poster
 
Join Date: Sep 2005
Location: Arizona
Posts: 454
Please Note: brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Detached garage

Wow. All I can say is WTF?
Reply With Quote
  #10  
Old 9/12/07, 9:17 PM
Marc Benz Marc Benz is offline
Active Poster
 
Join Date: Sep 2007
Location: Paris France for now
Posts: 137
Please Note: Marc Benz is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Detached garage

I did see that before and i have to expain that to the comuster about this situation and this type what you show to us on the photo that if that wired for only 120 volts the netrual is never be switch or controled by breaker or switch and this is very dangerous pratice. [ this is not allowed the netural to be fused/breaker after 1930's so it is in the code senice that time ]

And i think there are some issue it will crop up is the permits i know pretty good percentage of HO[ Homeowners ] don't bother to get the proper permits to do the job safe.

the other area is the spa tub but i think i will leave this in other area for now if want to talk about it we can run seperted thread on this one.


Merci , Marc
Reply With Quote
  #11  
Old 9/13/07, 1:15 AM
Paul Dickerson Paul Dickerson is offline
InterNACHI Member
 
Join Date: May 2004
Location: Clinton, WA
Posts: 327
Default Re: Detached garage

Marc is right. The biggest problem here is that this is a 120 volt panel with an OCPD on the neutral. Bad news.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Installing GFCI in garage with no ground cyezza Electrical 53 11/30/07 6:05 PM
Evaporative cooler in garage chellickson HVAC 9 7/23/07 1:08 AM
Garage ceiling & door header Al Barb Interior 7 3/27/07 1:07 PM
Garage Door Safety...No Reverse...Advice Please gliebig Exterior 33 3/17/07 8:28 PM
Garage fire rated wall jlybolt Interior 3 6/18/06 7:21 PM


All times are GMT -4. The time now is 3:15 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts