Hi all,

I did a search for this but did not find anything.

I was told that I need to record the amperage and voltage ratings of services I inspect. I'm clear on amperage but not on reporting on voltage.

Thank you in advance for any help.

Tom
Reply With Quote
Need a home inspection in Mississippi? Check out InterNACHI's listing of Mississippi certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 6/14/11, 12:59 PM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,619
Default Re: Determining Voltage as well as Amperage of a Service

Where did you get this information I would love to read a copy ... Thanks ... Roy



Need help on inspection call my cell 613-827-2011

I like email Roycooke@hotmail.com

Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun.



Reply With Quote
  #3  
Old 6/14/11, 12:59 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,251
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Determining Voltage as well as Amperage of a Service

For the US in most dwellings it will be single phase, 120/240 volts. In a dwelling unit in a large building you might see single phase 120/208 volts. Some old houses around here still have single phase 120 volts services. There are other systems. Easiest way to tell is with a volt meter.
Reply With Quote
  #4  
Old 6/14/11, 4:31 PM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: Determining Voltage as well as Amperage of a Service

Most SOP's do require an inspector to report on service amps, as well as voltage (NACHI's SOP also indirectly requires reporting voltage), if it can be determined by visual means. Measuring current or voltage is NOT required by the standards.

Quote:
Originally Posted by twitt View Post
I'm clear on amperage but not on reporting on voltage.
Look at the number of wires on the service drop, or the number coming into the main service disconnect. Two (2) wires is an older 120V single phase service, and three (3) wires is a 120V/240V or 120V/208V single phase service. Commercial services may have more wires and/or higher voltages.

Most residential services are 3-wire 120V/240V, but in some areas (e.g around NYC) residences may have 120V/208V services. Check the panel label to help figure that out.

http://www.nachi.org/gallery/electri...vice/volts.jpg

P.S. On the utility side there is no "ground" wire, and the "neutral" is typically the bare wire.



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...

Last edited by roconnor; 6/16/11 at 2:11 AM..
Reply With Quote
  #5  
Old 6/14/11, 4:40 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,251
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Determining Voltage as well as Amperage of a Service

Quote:
Originally Posted by roconnor View Post
Some nice graphics there. I looked at a few of them and the fourth graphic (using the NEXT button) is incorrect. The CB in the center is a 2 pole not a single pole breaker. I would have added directly to the post but I do not have permission.
Reply With Quote
  #6  
Old 6/15/11, 3:46 PM
George P. Wells, CMI's Avatar
George P. Wells, CMI George P. Wells, CMI is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Michigan
Posts: 554
Send a message via Skype™ to gwells
Default Re: Determining Voltage as well as Amperage of a Service

Quote:
Originally Posted by twitt View Post
Hi all,

I did a search for this but did not find anything.

I was told that I need to record the amperage and voltage ratings of services I inspect. I'm clear on amperage but not on reporting on voltage.

Thank you in advance for any help.

Tom
Nominal Voltages in the United States for most residences are 120V and 240V, They are 60 Hz, single-split-phase. They are usually derived from a single-phase transformer with a 7,200V primary.

Other secondary Voltages that you may encounter are 208Y/120 and 480Y/277, three-phase, with 12,470V and 13,200V being the most common primary Voltages. Most light to moderately sized commercial systems are three-phase Wye. Three-phase Delta is more common in industrial facilities. Most are solidly grounded.

If you are in the Eastern US, you may also see some two-phase systems. Two-phase systems are rare West of the Mississippi and almost completely non-existent West of the Rocky Mountains. Two-phase systems are commonly mistaken for three-phase.



BestInspectors.Net
& Real Estate Training Academy

Inspection Report Software for
Windows - iOS - Mac - Android

Continuing Education
Home and Commercial Building Inspection - Skilled Trades – Real Estate – Appraisal – NFPA 921

http://www.bestinspectors.net

est. 1992

Last edited by gwells; 6/15/11 at 8:55 PM..
Reply With Quote
  #7  
Old 6/15/11, 9:05 PM
George P. Wells, CMI's Avatar
George P. Wells, CMI George P. Wells, CMI is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Michigan
Posts: 554
Send a message via Skype™ to gwells
Default Re: Determining Voltage as well as Amperage of a Service

Quote:
Originally Posted by Robert Meier View Post
Some nice graphics there. I looked at a few of them and the fourth graphic (using the NEXT button) is incorrect. The CB in the center is a 2 pole not a single pole breaker. I would have added directly to the post but I do not have permission.

Here's the graphic
Attached Thumbnails
determining-voltage-well-amperage-service-2pole-internachi_.jpg  



BestInspectors.Net
& Real Estate Training Academy

Inspection Report Software for
Windows - iOS - Mac - Android

Continuing Education
Home and Commercial Building Inspection - Skilled Trades – Real Estate – Appraisal – NFPA 921

http://www.bestinspectors.net

est. 1992
Reply With Quote
  #8  
Old 6/15/11, 9:10 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,251
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Determining Voltage as well as Amperage of a Service

Quote:
Originally Posted by gwells View Post
Here's the graphic
Yes that was the one.
Reply With Quote
  #9  
Old 6/16/11, 1:17 PM
George P. Wells, CMI's Avatar
George P. Wells, CMI George P. Wells, CMI is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Michigan
Posts: 554
Send a message via Skype™ to gwells
Default Re: Determining Voltage as well as Amperage of a Service

Quote:
Originally Posted by Robert Meier View Post
Yes that was the one.
I don't know all that much about how the message board works. You might want to ask Chris about being able to post pictures and graphics. The first time I tried to post the breaker graphic, a message popped up saying that I wasn't authorized to post a picture. It worked a few minutes a few minutes later though.



BestInspectors.Net
& Real Estate Training Academy

Inspection Report Software for
Windows - iOS - Mac - Android

Continuing Education
Home and Commercial Building Inspection - Skilled Trades – Real Estate – Appraisal – NFPA 921

http://www.bestinspectors.net

est. 1992
Reply With Quote
  #10  
Old 6/16/11, 5:40 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,251
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Determining Voltage as well as Amperage of a Service

Quote:
Originally Posted by gwells View Post
I don't know all that much about how the message board works. You might want to ask Chris about being able to post pictures and graphics. The first time I tried to post the breaker graphic, a message popped up saying that I wasn't authorized to post a picture. It worked a few minutes a few minutes later though.

I was able to copy the url but got a warning about using those graphics without permission. Seems to be pretty standard message board stuff. Even Mike Holt allows you to use his stuff if you get permission first.
Reply With Quote
  #11  
Old 6/30/11, 2:36 PM
Justin R. Ake Justin R. Ake is offline
InterNACHI Member
 
Join Date: Aug 2010
Posts: 14
Default Re: Determining Voltage as well as Amperage of a Service

I'm a little unclear as to the best way to determine amperage myself. I was taught to use the lowest capacity device to estimate amperage. For instance, if the panel is rated for 100amps and the meter is rated for 200 amps, then the amperage is 100. Of course, the SE cables have to be considered too. My question is how to determine the amperage of the SE cables and the main disconnect. Typically the main will be labeled but what happens when the main disconnect is not labeled? How do we estimate that?
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
New Washington Legislation Submitted gdomagala Legislation, Licensing & Legal Issues for Inspectors 294 2/10/08 1:20 AM
Electricians Check List pabernathy Electrical Inspections 74 12/5/07 6:39 PM
Stray Voltage can kill rcooke Electrical Inspections 24 10/26/07 11:40 AM
Rating Service Amperage scosta Electrical Inspections 3 9/25/07 10:50 PM


All times are GMT -4. The time now is 8:47 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts