  #1  
Old 8/6/09, 9:57 PM
Gerald C. Wilcox's Avatar
Gerald C. Wilcox Gerald C. Wilcox is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: Harvey, ND
Posts: 333
Default Where did the wires go?

Three breakers tied together 30 amp breaker. Panel label says water heater and boiler. The center wires must go to the the off peak water heater. There is a separate disconnect at the water heater. Are they tied to the buss bar? Why would the propane boiler be tied to a 30 amp 3 pole breaker? Any thoughts? Thanks in advance.
Attached Thumbnails
did-wires-go-240-main-st-274-small-.jpg.jpg
Views:	157
Size:	69.6 KB
ID:	30669  
Reply With Quote
Find an InterNACHI certified Louisiana Home Inspector (and anywhere else in North America)
  #2  
Old 8/6/09, 11:04 PM
Gerald C. Wilcox's Avatar
Gerald C. Wilcox Gerald C. Wilcox is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: Harvey, ND
Posts: 333
Default Re: Where did the wires go?

bump
Reply With Quote
  #3  
Old 8/6/09, 11:30 PM
Patrick Bolliger's Avatar
Patrick Bolliger Patrick Bolliger is offline
InterNACHI Member
 
Join Date: Aug 2005
Location: Chicago, IL
Posts: 890
Send a message via Skype™ to pbolliger
Default Re: Where did the wires go?

Hi Gerald,

Couple of questions:

Is the panel totally full, meaning no empty breaker slots?

Are the appliances two totally separate devices in the same location?

It is quite possible that the installer was trying this concept:

Use three breaker to supply 220V on a different side of the (sine wave) to handle two appliances without using two individual double pole breakers (4 slots)
Common connection would the the "double tapped Center breaker" BUT the concept is goofy.... wrong anyway in my opinion...

Last edited by pbolliger; 8/6/09 at 11:33 PM.. Reason: Revised theory
Reply With Quote
  #4  
Old 8/7/09, 4:09 AM
rbibler rbibler is offline
Active Poster
 
Join Date: Nov 2008
Location: Healdsburg Ca
Posts: 1,114
Please Note: rbibler is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Where did the wires go?

Question did he bring the 3 wires in to the panel by a conduit ?

Very wrong.

Best

Ron
Reply With Quote
  #5  
Old 8/7/09, 8:52 AM
Marcel Gratton's Avatar
Marcel Gratton Marcel Gratton is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: Gatineau, QC
Posts: 1,778
Default Re: Where did the wires go?

Quote:
Originally Posted by gwilcox View Post
Three breakers tied together 30 amp breaker. Panel label says water heater and boiler. The center wires must go to the the off peak water heater. There is a separate disconnect at the water heater. Are they tied to the buss bar? Why would the propane boiler be tied to a 30 amp 3 pole breaker? Any thoughts? Thanks in advance.
Is that a commercial inspection?

Three breakers tied usually are for 3 phase.



Marcel Gratton, NACHI04011210, CMI
On The Level Inspection
Gatineau, Québec
http://www.onthelevelinspection.com/
Reply With Quote
  #6  
Old 8/7/09, 12:29 PM
Frank P. Newman Frank P. Newman is offline
InterNACHI Member
 
Join Date: Aug 2007
Location: Dublin, GA
Posts: 668
Default Re: Where did the wires go?

From the picture and the label on the center breaker it appears to be a special purpose 3 pole breaker - likely designed for the service. I'm guessing the two wires are properly terminated behind the center pole. Surely some expert has seen this before.



Frank P. Newman
Emerald City Inspections, LLC
Dublin, GA
Reply With Quote
  #7  
Old 8/7/09, 1:16 PM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,749
Default Re: Where did the wires go?

Frank, I agree...the wiring diagram tends to show an unusual configuration. I have to go by an electrical parts supply house this afternoon and will stop in to see if they can determine what this is. Maybe Paul A will chime in before that though.



Excellence in Inspections
Mike Boyett, TREC #7290
mikeb@capcityinspections.com
Capital City Inspections
Austin, Texas
(512) 577-2579

Company blog is: www.capcityinspections.com/blog
Reply With Quote
  #8  
Old 8/7/09, 3:32 PM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,749
Default Re: Where did the wires go?

OK, I was able to discuss this with two different electrical supply houses and got a couple of opinions. First, we have to assume this was a single phase residential panel. If it is a 3 phase panel then the following ideas are moot.

One supplier, who said he had been in the breaker business 40 years and seemed knowledgeable, assured me what we were looking at was what was referred to as a "delta breaker" which was used to start 3 phase equipment from a single phase source. He said once it was running then it didn't matter (I didn't know that but I'll take his word for it). He said those ITE Siemens delta breakers were over 30 years old, no longer UL approved nor were replacements available. So, if the equipment that this breaker was supplying was a 3 phase compressor or something similar then this idea may be accurate.

The other electrical supplier shrugged and said maybe, just maybe it was a Shunt Trip breaker. Remember, a shunt trip breaker can be remotely tripped via a wired signal for safety or maintenance requirements. They are normally seen in commercial applications. There were some indications that this might be a shunt trip breaker but, if so, then the configuration seemed to indicate it was a 110v shunt trip which they had not heard of.

I tend to lean toward the first explanation but I've still get feelers out to a couple of other knowledgable electrical contacts to see what they say.
Reply With Quote
  #9  
Old 8/7/09, 5:24 PM
Gerald C. Wilcox's Avatar
Gerald C. Wilcox Gerald C. Wilcox is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: Harvey, ND
Posts: 333
Default Re: Where did the wires go?

Thanks for all the imput guys. I will try to answer some of the questions. 1) Yes, it is a residential 200 amp service. 2)The panel was not totally full, there is room to add circuit breakers.3) They are two completely different devices located in opposite ends of the basement.4) All romex wiring.
The panel has an 1988 state inspection label, and the wiring from the three pole breaker in question feeds the water heater only. I see they have moved the boiler to a 15 amp breaker. Are the top and bottom circuits of the 3 pole breaker drawing off the same leg from the SEC? Or does the middle breaker split the leg and give you two 30 amp 240 v circuits? There is an abandoned water heater still hooked up to power but the disconnect is off.
Reply With Quote
  #10  
Old 8/7/09, 6:13 PM
Justin D. Schlueter Justin D. Schlueter is offline
New User
 
Join Date: Jul 2008
Location: Minnesota
Posts: 11
Please Note: Justin D. Schlueter is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Where did the wires go?

That's not a delta breaker. A delta breaker was used years ago in split bus panels to protect a three phase load from three phase supply when a standard single phase panel is used. (120/240 delta)

That breaker is a special type, but the little sticker on the face tells it all. A normal breaker plugs onto the bus bars and is fed that way. This breaker is fed seperately, not from the bus bars, rather the black and red wires in the center. These wires should come into the panel from outside through the same conduit as the other service wires where they are probably connected to a off peak load controller and separate kilowatt hour meter for the hot water heater.
Reply With Quote
  #11  
Old 8/7/09, 6:24 PM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,749
Default Re: Where did the wires go?

Thanks Justin..understanding that the red/black center wires are inputs rather than outputs makes much more sense. I'll have to go back to those two supply houses and clue them in.

So the configuration looks something like this then?

did-wires-go-special-brkr.jpg

Last edited by mboyett; 8/7/09 at 6:50 PM..
Reply With Quote
  #12  
Old 8/7/09, 7:11 PM
Gerald C. Wilcox's Avatar
Gerald C. Wilcox Gerald C. Wilcox is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: Harvey, ND
Posts: 333
Default Re: Where did the wires go?

Thanks Justin, That sounds exactly correct, as there is an offpeak meter controlling the water heater.
Reply With Quote
  #13  
Old 8/7/09, 8:01 PM
Marcel Gratton's Avatar
Marcel Gratton Marcel Gratton is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: Gatineau, QC
Posts: 1,778
Default Re: Where did the wires go?

Quote:
Originally Posted by Justin D. Schlueter View Post
That breaker is a special type, but the little sticker on the face tells it all. A normal breaker plugs onto the bus bars and is fed that way. This breaker is fed seperately, not from the bus bars, rather the black and red wires in the center. These wires should come into the panel from outside through the same conduit as the other service wires where they are probably connected to a off peak load controller and separate kilowatt hour meter for the hot water heater.
Thanks for that Justin!

This reminds me of a previous inspection where an off peak load controller circuit for the water heater simply bypassed the service panel...
Attached Thumbnails
did-wires-go-img_0125.jpg   did-wires-go-img_0126.jpg  



Marcel Gratton, NACHI04011210, CMI
On The Level Inspection
Gatineau, Québec
http://www.onthelevelinspection.com/
Reply With Quote
Find an InterNACHI certified Louisiana Home Inspector (and anywhere else in North America)
  #14  
Old 8/7/09, 8:30 PM
Justin D. Schlueter Justin D. Schlueter is offline
New User
 
Join Date: Jul 2008
Location: Minnesota
Posts: 11
Please Note: Justin D. Schlueter is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Where did the wires go?

Quote:
Originally Posted by mboyett View Post
Thanks Justin..understanding that the red/black center wires are inputs rather than outputs makes much more sense. I'll have to go back to those two supply houses and clue them in.

So the configuration looks something like this then?

Attachment 30727
Right. I think they called it a "water heater breaker." If that rings a bell to anyone.

Its always interesting to see all the different ways that the off peak setups were wired.
Reply With Quote
  #15  
Old 8/8/09, 11:27 AM
Patrick Bolliger's Avatar
Patrick Bolliger Patrick Bolliger is offline
InterNACHI Member
 
Join Date: Aug 2005
Location: Chicago, IL
Posts: 890
Send a message via Skype™ to pbolliger
Default Re: Where did the wires go?

Thanks Justin!!
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Wires ran from lugs to auxilary panels Kevin Luce Electrical Inspections 7 9/20/07 9:24 AM
Loose/terminated wires in main panel csteele Electrical Inspections 13 7/19/07 4:39 PM
Ground Wires Inside a Panel mveitenhans Electrical Inspections 13 10/29/06 11:39 AM