Default Did you KNOW this about NM Cable?

Things to Consider when inspecting homes...check the attics, basements and so on.....
334.80 Ampacity.
The ampacity of Types NM, NMC, and
NMS cable shall be determined in accordance with 310.15.
The ampacity shall be in accordance with the 60°C (140°F)
conductor temperature rating. The 90°C (194°F) rating
shall be permitted to be used for ampacity derating purposes,
provided the .nal derated ampacity does not exceed
that for a 60°C (140°F) rated conductor. The ampacity of
Types NM, NMC, and NMS cable installed in cable tray
shall be determined in accordance with 392.11.
Where more than two NM cables containing two or
more current-carrying conductors are bundled together and
pass through wood framing that is to be .re- or draftstopped
using thermal insulation or sealing foam, the allowable
ampacity of each conductor shall be adjusted in
accordance with Table 310.15(B)(2)(a).

334.30 Securing and Supporting.
Nonmetallic-sheathed
cable shall be supported and secured by staples, cable ties,
straps, hangers, or similar fittings designed and installed so
as not to damage the cable, at intervals not exceeding 1.4 m
(4 1/2"
) and within 300 mm (12 in.) of every outlet box,
junction box, cabinet, or .tting. Flat cables shall not be
stapled on edge.
Sections of cable protected from physical damage by raceway
shall not be required to be secured within the raceway.

314.17(D)

(C) Nonmetallic Boxes and Conduit Bodies.
Nonmetallic
boxes and conduit bodies shall be suitable for the lowest
temperature-rated conductor entering the box. Where nonmetallic
boxes and conduit bodies are used with messenger
supported wiring, open wiring on insulators, or concealed
knob-and-tube wiring, the conductors shall enter the box
through individual holes. Where .exible tubing is used to
enclose the conductors, the tubing shall extend from the last
insulating support to not less than 6 mm (
1.4 in.) inside the
box and beyond any cable clamp. Where nonmetallicsheathed
cable or multiconductor Type UF cable is used,
the sheath shall extend not less than 6 mm (
1.4 in.) inside
the box and beyond any cable clamp. In all instances, all
permitted wiring methods shall be secured to the boxes.

Exception: Where nonmetallic-sheathed cable or multiconductor
Type UF cable is used with single gang boxes
not larger than a nominal size 57 mm × 100 mm (2
1/4 in.
× 4 in.) mounted in walls or ceilings, and where the cable
is fastened within 200 mm (8 in.) of the box measured along
the sheath and where the sheath extends through a cable
knockout not less than 6 mm (
1/4 in.), securing the cable to
the box shall not be required. Multiple cable entries shall
be permitted in a single cable knockout opening.

Just some things to think about when doing your inspection.......look around and be aware of what ya might see.





Paul W. Abernathy,CMI,CEI,CEPE
NEC® Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Interesting article from U/L on armored cable Greg Fretwell Electrical 18 2/27/07 10:02 PM
Short circuit failures with 12/3 NM-B cable and NM clamp connectors pabernathy Electrical 5 2/16/07 1:19 PM
- low voltage cable burning at the SPLICES ?!?! wtf ?!? spanishman Electrical 6 9/9/06 2:55 PM
Hey Joe Tedesco pbolliger Electrical 7 4/11/06 1:17 AM
Ceilings falling with wires in it. jsmith3 Interior 8 3/16/06 8:24 PM


All times are GMT -4. The time now is 10:32 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts