#1
|
|||
|
|||
|
Please Note:
jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Last edited by jtedesco1; 1/12/07 at 3:11 AM.. |
|
#2
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
This has been a "style" issue for years. If they are going to follow the new convention there is only one "grounding" conductor in the whole system. That is the conductor(s) that go from the bus in the service disconnect enclosure to the electrode(s)
I suppose we now have to call that bare/green wire in cables and raceways an equipment bonding conductor. It also means the wire going to the electrode can be bare or any other color besides white or green. (let the arguing begin) |
|
#3
|
|||
|
|||
|
Please Note:
Pierre Belarge is a non-member guest and is in no way affiliated with InterNACHI or its members.
Joe
This could be an excellent topic, but it would have to be dealt with very carefully. Especially as Greg has mentioned with the changes made already to the NEC and I would expect some sweeping changes that may come this way in the next few code cycles. IMO, the way to address this on a site such as this one, is to break a Thread down into one topic of Article 250 and work it that way. Pictures and illustrations to graphically explain with the wording. Bussmann has a great animated slide that shows what happens when a ground fault occurs in a system. Stuff like that. P.S. Grounding/Bonding is my favorite Article in the NEC. |
|
#4
|
|||
|
|||
|
Please Note:
jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
PIERRE:
I AGREE, You too are capable of doing this, and may have the time to do so, but be careful, some may not agree with your comments. The Bussmann information you mentioned sounds interesting, where can it be found. Last edited by jtedesco1; 12/30/06 at 4:25 PM.. |
|
#5
|
|||
|
|||
|
Please Note:
Pierre Belarge is a non-member guest and is in no way affiliated with InterNACHI or its members.
Since I have become an instructor, my best learning tool has been when a student or other individual disagrees with a statement or thought that I have. It makes me think much more about what I say. It has also shown me that my experiences are much more limited (in my little corner of the industry) than I really understood them to be.
I always, always tell my students that I welcome a well intentioned discussion. I cannot imagine what it was like for the "older" generation to find info without the benefit of the WWW. |
|
#6
|
|||
|
|||
|
Please Note:
jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Students help to clear the cobwebs in our minds, I am always challenged during my presentations.
Last edited by jtedesco1; 12/30/06 at 4:25 PM.. |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Terminations of Grounding & Bonding Equipment | pabernathy | Electrical | 24 | 12/6/07 6:56 PM |
| Demystify Grounding & Bonding Class | pabernathy | Education | 5 | 12/24/06 2:10 AM |
| Electrical Inspection Training for Home Inspectors | jtedesco1 | Education | 6 | 4/27/06 11:43 PM |