Default Disconnect

I found this outside below the meter with a sub panel in the living room. Is it a disconnect?

disconnect-100_1024.jpg



Justin Roberts
Roberts Property Inspections
PO Box 1972
Big Bear City, CA 92314
(909) 618-4697

BigBearHomeInspections.com

Reply With Quote
Need a home inspection in Wisconsin? Check out InterNACHI's listing of Wisconsin certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 9/12/10, 12:43 AM
wsiegel wsiegel is offline
Active Poster
 
Join Date: Oct 2006
Location: Hialeah, Fl
Posts: 2,649
Please Note: wsiegel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Disconnect

It is the disconnect.
Reply With Quote
  #3  
Old 9/12/10, 5:22 AM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,251
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Disconnect

If it's between the meter and the panel then it's the service disconnect. The neutral should be bonded to the enclosure at that point. Since there are only three conductors on the load side of the disconnect the conduit would need to serve as the equipment grounding conductor. There should also be separation between the EGC's and neutrals at the sub panel.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Main Panel vs Sub-Panel and main disconnect? rbassett Electrical Inspections 11 10/24/09 6:16 PM
Exterior Service Disconnect Clearances? rcramer Electrical Inspections 18 7/28/07 1:12 PM
50 amp disconnect for 1600sf condo kmccullough Electrical Inspections 5 4/10/07 8:49 PM
A/C Disconnect question rslocum Inspecting HVAC Systems 15 9/21/06 12:16 AM
100 Amp Meter, 200 Amp Disconnect jweinberg Electrical Inspections 8 8/15/06 12:32 PM


All times are GMT -4. The time now is 8:50 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts