Default Disconnect at the exterior

I am not sure where I got the idea that there is supposed to be a means of disconnecting the electrical service at the exterior, but I can not find anything to verify this.
Most of the panels are located at the exterior of the houses around here, so it is typicallly not an issue.
I thought the fire department wanted to be able to disconnect the electricity at the exterior.
Any thoughts would be appreciated.
Reply With Quote
Find an InterNACHI certified Kentucky Home Inspector (and anywhere else in North America)
  #2  
Old 8/19/09, 8:57 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Disconnect at the exterior

No requirement for an exterior disconnect.

There is a requirement for a disconnect in the service entrance panel (no matter where it is located) unless 6 or less breakers are there (you don't need a main breaker if 6 or less hand movements can turn off all the power).



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #3  
Old 8/19/09, 11:14 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: Disconnect at the exterior

I almost never see a disconnect outside as that means someone like kids could be shutting you off at night.

Fire
Department can do what many do to work on the inside ,which is pull the meter head.
Reply With Quote
  #4  
Old 8/20/09, 12:19 AM
bdoles2's Avatar
bdoles2 bdoles2 is offline
Active Poster
 
Join Date: Aug 2006
Location: Atlanta, GA
Posts: 3,071
Please Note: bdoles2 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Disconnect at the exterior

Many of our newer homes and multi family developments have the disconnect on the exterior.

i.e. this picture shows the exact situation for a 4 unit townhome.

disconnect-exterior-img_6232.jpg
Reply With Quote
  #5  
Old 8/20/09, 12:47 AM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: Disconnect at the exterior

Quote:
Originally Posted by bdoles2 View Post
Many of our newer homes and multi family developments have the disconnect on the exterior.

i.e. this picture shows the exact situation for a 4 unit townhome.

Attachment 31020
Must admit I do not understand why someone would want to have to go outset to reset the thing.
Reply With Quote
  #6  
Old 8/20/09, 3:13 AM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Disconnect at the exterior

One of the primary reason for the disconnect is because the panel inside is too far from the exterior. The NEC requires the length of unfused cable or conductors to be kept as short as practical. A distance is not clearly spelled out. It is up the the AHJ. Some areas only allow 5-6 feet of cable before the panel.

FD SOPS probably vary, but pulling a meter under load can be deadly. Safer to wait for the POCO to cut the feed at the ople or transformer.
Reply With Quote
  #7  
Old 8/20/09, 9:49 AM
Frank P. Newman Frank P. Newman is offline
InterNACHI Member
 
Join Date: Aug 2007
Location: Dublin, GA
Posts: 668
Default Re: Disconnect at the exterior

Quote:
Originally Posted by relliott View Post
I almost never see a disconnect outside as that means someone like kids could be shutting you off at night.

Fire
Department can do what many do to work on the inside ,which is pull the meter head.
We see them everywhere here because is a requirement of the AHJ (in the city at least). They cite fire department requirements as mentioned above. Note also that pulling the meter under load can be hazardous and for larger services, the meter may be reading only a set of CTs and PTs so will not disconnect the service conductors.



Frank P. Newman
Emerald City Inspections, LLC
Dublin, GA
Reply With Quote
  #8  
Old 8/21/09, 1:07 AM
rbrady's Avatar
rbrady rbrady is offline
Active Poster
 
Join Date: Feb 2007
Location: Eureka, CA
Posts: 619
Please Note: rbrady is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Disconnect at the exterior

Thanks for the replies. I don't know where I got the idea that it is required, but when I tried to double check in my code books I couldn't find anything. I'll have to double check with the AHJ (or a local electrician) to see if it could be a local thing.
Reply With Quote
  #9  
Old 8/21/09, 6:08 AM
ldapkus ldapkus is offline
Active Poster
 
Join Date: Mar 2006
Posts: 5,717
Please Note: ldapkus is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Disconnect at the exterior

Quote:
Originally Posted by bdoles2 View Post
Many of our newer homes and multi family developments have the disconnect on the exterior.

i.e. this picture shows the exact situation for a 4 unit townhome.

Attachment 31020
That's where I see them most.
Reply With Quote
  #10  
Old 8/21/09, 7:00 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: Disconnect at the exterior

Quote:
Originally Posted by ldapkus View Post
That's where I see them most.

Yes, but Single Family homes have them too.

As a matter of fact, my house has the SE disconnect outside, below the meter.
Reply With Quote
  #11  
Old 8/22/09, 11:01 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Disconnect at the exterior

Firstly, I get this asked alot on the "ROAD" and as Jim so nicely stated, the real concern is the amount of "unprotected" conductor that canbe run on the inside of the building [ 230.70(A)(1)]. Also since the nature of the "condo" experience is that you have individual units that get panels and since as stated earlier you can't meet the minimum safety standards on a conductor running wildly through the building with no protection. So they install a grouped set of disconnection means outside and then conductors on the load side of the disconnect are now feeders and they can be run through the building since they have protection on them.

Now I wont go into groupings and allowances on exterior run SE conductors if all outside and so on......just remember the above and you should be fine. Also remember that in some local jurisdictions they have a standard policy on the point of entry of service conductors where they say they are aware it can be outside or inside the nearest point but we want it outside, their rules their requirements are required to be followed in a given locality. Many take the following standard in many ways:

230.70 General.
Means shall be provided to disconnect all
conductors in a building or other structure from the service entrance
conductors.

(A) Location.
The service disconnecting means shall be
installed in accordance with 230.70(A)(1), (A)(2), and
(A)(3).

(1) Readily Accessible Location.
The service disconnecting
means shall be installed at a readily accessible location
either outside of a building or structure or inside nearest the
point of entrance of the service conductors.




Paul W. Abernathy
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Moisture Management mcyr Exterior Inspections 15 9/8/08 12:11 PM
Exterior Service Disconnect Clearances? rcramer Electrical Inspections 18 7/28/07 1:12 PM
exterior main disconnect afrost Electrical Inspections 16 5/12/07 1:02 PM


All times are GMT -4. The time now is 8:50 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts