Default Dishwasher on GFCI circuit

Today's afternoon inspection was a 4 year old. The dishwasher is on the same circuit as one of the counters, and testing the GFCI shut off the d/w. Since this is the first time I've come across this, I wonder if it's ok to have the dishwasher on the same circuit as a GFCI counter circuit. Any help is greatly appreciated.
Stu
Reply With Quote
  #2  
Old 2/8/07, 11:11 PM
Stephen W. Stanczyk's Avatar
Stephen W. Stanczyk Stephen W. Stanczyk is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Kapowsin, WA
Posts: 4,965
Send a message via AIM to sstanczyk
Default Re: Dishwasher on GFCI circuit

Nope, not allowed.

"A fastened-in-place appliance (dishwasher, garbage disposer, etc.) shall not be connected to a small appliance branch circuit."

Steve




Stephen Stanczyk
Washington State Licensed Home Inspector # 221
President, Washington Association of Property Inspectors (WAPI)
(253) 241-0602 calls answered until 10pm


Pierce County -Thurston County - King County - Snohomish County
Reply With Quote
  #3  
Old 2/9/07, 12:08 AM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,629
Default Re: Dishwasher on GFCI circuit

Today's GFCI outlets seem to be subject to nuisance tripping when appliances with motors turn on, so I always recommend a dedicated standard circuit when I find the dishwasher, disposal, washer, or dryer on a GFCI circuit.



NACHI 2005 U.S. Member of the Year
Reply With Quote
  #4  
Old 2/9/07, 10:28 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Dishwasher on GFCI circuit

Quote:
Originally Posted by rray
Today's GFCI outlets seem to be subject to nuisance tripping when appliances with motors turn on, so I always recommend a dedicated standard circuit when I find the dishwasher, disposal, washer, or dryer on a GFCI circuit.
Firstly, NO the DW should not be on the GFCI for a kitchen counter simply because the NEC states this, the small appliance circuit requirements prohibit it.

Secondly, the NEC Code Panel seems to disagree in terms of the GFCI's and nuisance tripping. The panel is on record saying in 2008 NEC the allowances of readily accessible and dedicated ( like freezer ) in the garage area and other places which were allowed in the past to not have GFCI....WILL have to be GFCI protected now ( includeding freezers....) because they said DIRECTLY and on record....GFCI's no longer have the issues of nuisance tripping .......check out the ROC on 210.8 for the 2008 NEC...

Should be VERY interesting.....



Paul W. Abernathy
Reply With Quote
  #5  
Old 2/9/07, 10:37 AM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Dishwasher on GFCI circuit

How many circuits are feeding the kitchen?
If there are more than 2 20a circuits in there it is not really a problem. Look at the intent of the rule. They are just trying to insure the owner has enough power for their counter top appliances.
Reply With Quote
  #6  
Old 2/9/07, 10:49 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Dishwasher on GFCI circuit

not sure an HI will be going into determining that...so we generally speak in terms of the Minimum (2) Small Appliance circuits on the counter top. The problem is ( the way I read it )....is 2 or 3 or more serving the counter space would not be able to have a Dishwasher on it.

Now this is why a dedicated circuit is required to this appliance, usually due to the location.....and ofcourse load...but if the counter top has a GFCI and it trips the DishWasher...it is MOOT...should not be on the counter top circuit or the dedicated Small Appliance circuit.......but again just my opinion....


(B) Small Appliances.

(1) Receptacle Outlets Served.
In the kitchen, pantry,
breakfast room, dining room, or similar area of a dwelling
unit, the two or more 20-ampere small-appliance branch
circuits required by 210.11(C)(1) shall serve all wall and
floor receptacle outlets covered by 210.52(A), all countertop
outlets covered by 210.52(C), and receptacle outlets for
refrigeration equipment.



(2) No Other Outlets.
The two or more small-appliance
branch circuits specified in 210.52(B)(1) shall have no
other outlets.



Exception No. 1: A receptacle installed solely for the electrical

supply to and support of an electric clock in any of
the rooms specified in 210.52(B)(1).
Exception No. 2: Receptacles installed to provide power
for supplemental equipment and lighting on gas-fired
ranges, ovens, or counter-mounted cooking units.


I agree with Greg in that the intent was to properly supply the needed electricity...but the NEC clearly does not want anything on the circuits which are going to the counter space and like areas ( basically because the original poster said it was on the GFCI counter top..... ) but it is not correct to put a dishwasher on any circuit serving the kitchen counter or so on.....or tied to the dedicated kichen circuit for small appliances be it (2) or more.....this is why I feel it is called to be dedicated to the fixed appliance.



Paul W. Abernathy

Last edited by pabernathy; 2/9/07 at 10:52 AM..
Reply With Quote
  #7  
Old 2/9/07, 10:57 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Dishwasher on GFCI circuit

I have seen this in older construction ( not within 4 years ) where the home owner wanted to add a Dishwasher and they simply had the service guy tap into a counter top receptacle...the problem with that is chances are in older homes for one is you probably only have (1) circuit on the counter...and you are LUCKY if it is a 20A circuit.......so it is just a bad idea in all situations...

As an electrical contractor I would simply like most electricians to say....sure we can wire that up for you but it will need an additional circuit ran to it....and if the house panel does not allow this....Prime example of how a house electrical panel should be updated to meet the demands and expansion of todays technology.....a good reason to suggest a FILLED 100A panel...should be updated....or even a less sized panel...prime example to defer and suggest service upgrade....

Remember guys...my opinions are just mine.......and only intended as such as if you don't argee......fine.....I have no problem with that....



Paul W. Abernathy
Reply With Quote
  #8  
Old 2/9/07, 12:31 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,925
Default Re: Dishwasher on GFCI circuit

Inductive loads should not be put on small GFCI's like at the counter.

The counter outlets are basically dedicated circuits and should go no where else.
Reply With Quote
  #9  
Old 2/9/07, 12:36 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Dishwasher on GFCI circuit

except where permitted......Agreed !

Ironically the CP for the review of the 2008 NEC are saying GFCI's no longer have a nusiance trip issues.....only time will tell when the exceptions for GFCI locations ( Garages & The Like) is removed and all plugs will be all GFCI....then I guess we will really see.

I agree......and my belief is based on my previous post but I concur 100% with Mr Anderson.



Paul W. Abernathy
Reply With Quote
  #10  
Old 2/9/07, 4:44 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Dishwasher on GFCI circuit

Code aside, from the standpoint of servicibility for the occupant.... the dishwasher can almost fully "load" the circuit during the drying cycle, when the heating element inside comes on fully for a long period of time. That won't leave much capacity on the countertop receptacle(s) for whatever the occupant might want to use at the time the dishwasher is running. This may well yeild a tripping breaker from time to time.
Reply With Quote
  #11  
Old 2/9/07, 10:09 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Dishwasher on GFCI circuit

This "inductive load" and "motor load" stuff is BS. We run motors on GFCIs every day without problems. Just think of all the power tools that run in garage shops without problems. You couldn't build a house if motors tripped GFCIs. They are REQUIRED for ALL construction outlets in OSHA.
Faulty appliances trip GFCIs ... PERIOD!
Reply With Quote
  #12  
Old 2/10/07, 5:34 AM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,629
Default Re: Dishwasher on GFCI circuit

Faulty GFCIs also trip GFCIs. So if an appliance with a motor trips a GFCI when the appliance starts, there is a problem that needs to be determined. It could be the appliance, it could be the GFCI; other causes or multiple causes are also possible. In some cases, however, it is simply leakage from older appliances on older GFCIs.



NACHI 2005 U.S. Member of the Year
Reply With Quote
  #13  
Old 2/10/07, 8:09 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Dishwasher on GFCI circuit

I work with GFCI's all day on DRILLS and so on and they simply don't trip....so I have no problems with GFCI's today......they really just dont nuissance trip anymore.....Agreed



Paul W. Abernathy
Reply With Quote
  #14  
Old 2/10/07, 6:18 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,925
Default Re: Dishwasher on GFCI circuit

Quote:
This "inductive load" and "motor load" stuff is BS.
"BS", Well put, so long as you're talking out your *****.
What's the difference in a 15 amp inductive appliance versus a 15 amp resistance appliance?
If you can answer that, we can continue this conversation and clear the air of"BS".

It doesn't mean you can't run an inductive load on a GFCI. It means that the load is substantially increased and that an accumulative load may cause the device to think that someone is getting shocked and shutdown.
Remember back in physics class, where energy can't be created or destroyed only transformed?

Well, when you start a motor under an inductive load there is a loss of electrical energy when the appliance converts electrical energy into work which has a resulting transformation to heat.

Also, kitchen countertop GFCI's are not designed to handle excessive loads. There are GFCI devices that can handle hundreds of thousands of amp's and will handle anything you can throw at them. But then, there are GFCI devices that can handle hundreds of thousands of amps and will trip at the drop of a hat. An associate of mine shut down the worldwide Union Carbide office testing an HVAC system. I have done work at numerous power plants across the state of Tennessee and have always had three to five engineers looking over my shoulder to respond to a GFCI trip in the plant that I may potentially be caused during my diagnostic testing.

If you consider it "BS", then that is your prerogative.

This may not be a problem in every case, but when you put three or four bathrooms on the same circuit covered by the same GFCI and then decide to take the electrical circuit out to the back patio and then hook it up to the dishwasher , just maybe there might be a problem.
Reply With Quote
  #15  
Old 2/10/07, 7:04 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Dishwasher on GFCI circuit

Quote:
Originally Posted by dandersen
Remember back in physics class, where energy can't be created or destroyed only transformed?
That's absolutely true. There has been no new electricity generated since 1937. We just keep recyling it.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Help. What is the correct way to report a breaker that is too big. gromicko Electrical Inspections 77 5/10/12 6:13 PM
AFCI Questions and Answers - Mike Holt pabernathy Electrical Inspections 7 4/16/12 9:51 PM
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
The question asked on the new HI Study test here? jtedesco1 Electrical Inspections 28 10/4/06 9:31 AM


All times are GMT -4. The time now is 8:50 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts