  #1  
Old 2/5/10, 9:04 AM
Tom Leahy Tom Leahy is offline
InterNACHI Member
 
Join Date: Dec 2009
Location: Arlington, Texas
Posts: 358
Default Dishwasher outlet

Reading the post about the outlet on the other side of a bar sink below 18 inches not being GFCI'd but people writing up anyway for safety reasons, got me thinking about the dishwasher outlet. Just curious if anybody has called this out.

NEC is somewhat vague.
422.16(B)2......Receptacle shall be located to avoid physical damage to the flexible cord.....The receptacle shall be located in the space occupied by the appliance or ADJACENT thereto.......The receptacle shall be ACCESSIBLE.

90% of the time here in North Texas the outlet is in the cut out of the dishwasher. Here is a Whirlpool brand spec.
• Power supply cord must plug into a mating three prong,
grounded outlet, located in the cabinet next to the
dishwasher opening. Outlet must meet all local codes and
ordinances.




Last edited by tleahy; 2/5/10 at 9:35 AM..
Reply With Quote
Need a home inspection in Ohio? Check out InterNACHI's listing of Ohio certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 2/5/10, 12:18 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,207
Default Re: Dishwasher outlet

When it is under the cabinet it does not serve the countertop therefore it does not need to be GFCI protected. Some local codes may require the dishwasher to be hardwired as I remember seeing posted on here before.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
License NC2449 and SC1597
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #3  
Old 2/5/10, 12:38 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: Dishwasher outlet

The dishwasher is usualy pluged in behind it and reset would need to be at the panel.

The fridge is not on GFCI either remember.
Reply With Quote
  #4  
Old 2/5/10, 1:19 PM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,749
Default Re: Dishwasher outlet

Tom's question is not whether the outlet should be GFCI protected but rather should it be 'accessible' since many of them are under the enclosed cabinet and behind the dishwasher. The IRC (and I suspect the NEC) defines Accessible as:
Quote:
ACCESSIBLE. (As applied to wiring methods.) Capable of being removed or exposed without damaging the building structure or finish, or not permanently closed in by the structure or finish of the building.
Since the dishwasher can be slid out from under the cabinet then I consider that outlet 'accessible'. I do not write up outlets hidden behind a dishwasher as deficient.
Reply With Quote
  #5  
Old 2/5/10, 11:23 PM
Tom Leahy Tom Leahy is offline
InterNACHI Member
 
Join Date: Dec 2009
Location: Arlington, Texas
Posts: 358
Default Re: Dishwasher outlet

Thanks Mike!!

The majority of dishwashers here in Texas have cords on them. NEC says outlet can be in cut out and manufacturer says not to. Not sure who supersedes. I would have a HARD time calling this out myself, but it came up and got stuck in my head needing an answer. Wasn't sure if the dishwasher being considered built-in would change the accessible status.
Reply With Quote
  #6  
Old 2/5/10, 11:27 PM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,749
Default Re: Dishwasher outlet

Well, my first thought is that if the manufacturer says that then so be it....they override code. I'll go look at that Whirlpool reference. I'd like to use that for an RFI to TREC maybe.

Last edited by mboyett; 2/5/10 at 11:31 PM..
Reply With Quote
  #7  
Old 2/5/10, 11:39 PM
Tom Leahy Tom Leahy is offline
InterNACHI Member
 
Join Date: Dec 2009
Location: Arlington, Texas
Posts: 358
Default Re: Dishwasher outlet

Mike,
I just went to Whirlpool.com and selected a dishwasher and pulled the installations instructions to get the info. They seem to be the same instructions for most of the models.
Reply With Quote
  #8  
Old 2/6/10, 8:06 AM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,749
Default Re: Dishwasher outlet

Yeah, I see that although those instructions are a little vague regarding the outlet, i.e. like you said in your 1st post..."located in the cabinet next to the dishwasher".



Excellence in Inspections
Mike Boyett, TREC #7290
mikeb@capcityinspections.com
Capital City Inspections
Austin, Texas
(512) 577-2579

Company blog is: www.capcityinspections.com/blog
Reply With Quote
  #9  
Old 2/6/10, 9:42 AM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: Dishwasher outlet

Sorry my first post was a quick read through.

In the situation of the plug being accessible it is still not required to be gfci if down in the cabinet.

You could make the same argument for the micro hood plug too, otherwise.
Reply With Quote
  #10  
Old 2/6/10, 10:34 AM
Tom Leahy Tom Leahy is offline
InterNACHI Member
 
Join Date: Dec 2009
Location: Arlington, Texas
Posts: 358
Default Re: Dishwasher outlet

GE has a little more detail than Whirlpool. Here's GE's

"For power cord connections, install a 3-prong grounding
type receptacle in the adjacent cabinet rear wall, 6" min.
or 18" max. from the opening, 6" to 18" above the floor.
The receptacle must be accessible and therefore cannot
be installed in the back wall of the dishwasher enclosure"

To help you on the RFI, I called 3 builder friends. (1)Centex homes, (1) Gehan and the other MHI homes. They all buy direct from Whirlpool and Whirlpool will refuse to install unless outlets are in adjacent cabinet.

I called a local Whirlpool Salesman and he said about 10 years ago alot of the builders here got away from the direct connect due to theft. To get the electrical final/meter the dishwasher had to be installed, which put the appliances in the house to early and were getting stolen. Put the outlet in and get the meter and appliances could come in closer to the end. (makes sense). He also said the electricians would put the outlet to high. The plug and back of dishwasher would come into contact and create a SAFETY issue from vibration and jamming the dishwasher back to far, therefore changing the rule to be cabinet adjacent. Not sure of these facts, but sounded good.


I'm sure this might be overkill but just trying to help.
Reply With Quote
  #11  
Old 2/12/10, 5:58 PM
Rick Marton Rick Marton is offline
InterNACHI Member
 
Join Date: Feb 2010
Location: Paramus, New Jersey
Posts: 58
Default Re: Dishwasher outlet

Remember, the whole idea of the cord & plug/outlet is for the repairman who can unplug it while working on the unit. What I do and is acceptable is hard wire the unit and install a lockout/ tag out device on the breaker. The repairman can turn off the breaker and place a lock on it in the off position. This saves me time and money. Thanks Rick
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Washing Machine Outlet < 6' from Utility Sink tdomingues Electrical Inspections 16 1/28/10 5:01 PM
Dishwasher outlet directly under unit jfrederick Electrical Inspections 7 10/8/09 11:34 PM
Maytag recalls dishwashers. 135 reports of dishwasher fires. gromicko Interior Inspections 2 2/5/07 8:07 AM
Exploding Dishwasher mbledsoe Plumbing Inspections 8 2/28/06 7:13 AM


All times are GMT -4. The time now is 8:50 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts