Default disposer romex

Ug, Sunday morning and typing report after last nights party.

Is romex allowed to be directly connected to a disposer?

Can romex be directly attached to a three prong plug and used as an appliance cord?

I know these conditins are common. Just looking to dot the i

Thanks
Reply With Quote
Find an InterNACHI certified New Mexico Home Inspector (and anywhere else in North America)
  #2  
Old 12/13/09, 1:12 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,848
Default Re: disposer romex

Quote:
Originally Posted by jcahill View Post
Can romex be directly attached to a three prong plug and used as an appliance cord?
Not properly...



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #3  
Old 12/13/09, 1:18 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: disposer romex

Quote:
Originally Posted by jcahill View Post
Is romex allowed to be directly connected to a disposer?
There should be a Romex connector or strain relief bushing where it enters the disposal. It should not be directly on the edges of the entrance opening without being protected from abrasion damage.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #4  
Old 12/13/09, 1:23 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,925
Default Re: disposer romex

Romex was not intended for use outside of a finished wall system.

Romex cannot be used as an extension cord.

Armor shielding should be used to protect Romex to the garbage disposal as this is a high traffic area and the wiring is susceptible to damage.



"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein

David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #5  
Old 12/13/09, 1:26 PM
John Cahill John Cahill is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Plano, TX
Posts: 826
Default Re: disposer romex

Two concerns

If solid wire can be properly attached (per code or manufacturer) to the connectors inside a disposer or receptacle.

I suppose there is a special plug out there designed for romex but I am concerned with the everyday type plug.

I see this all the time on older homes. Romex through a wall and directly connected to the disposer. Obvious its been there and working for years.
Reply With Quote
  #6  
Old 12/13/09, 2:19 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: disposer romex

I don't see properly secured NM under a sink as subject to damage. It is the common installation method that I am familiar with. I have never seen a cord and plug connected disposal.

Connections between NM and the disposal leads would not be any different that connections to a lighting fixture.

You will not find a cord cap that is listed for use with NM cable.
Reply With Quote
  #7  
Old 12/13/09, 2:48 PM
Doug Edwards's Avatar
Doug Edwards Doug Edwards is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Florida panhandle
Posts: 4,850
Default Re: disposer romex

You are likely going to see all kinds of homeowner installed crap as a home inspector. The frequency of times it is seen does not change it and make it right. Just as orange (or any color) extension cord is not appropriate wiring for use as permanent house wiring, Romex or any other NM cable should not be used for applications like garbage disposals, where an appliance (stranded / flexible) cord with an approved plug should be used.



"War is an ugly thing, but not the ugliest of things; the decayed and degraded state of moral and patriotic feeling which thinks nothing is worth a war, is worse. A man who has nothing which he cares more about than he does about his personal safety is a miserable creature who has no chance at being free, unless made and kept so by the exertions of better men than himself."

- John Stuart Mill







Reply With Quote
  #8  
Old 12/13/09, 2:53 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: disposer romex

I do see ALOT of cord connected disposals. The NEC allows this type of application with length limitations and properly listed cords. NM Cable would not be allowed for this applcation with a plug attached to the end.



Paul W. Abernathy
Reply With Quote
  #9  
Old 12/13/09, 5:37 PM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,749
Default Re: disposer romex

What...didn't you write it down the first time John?

http://www.nachi.org/forum/f19/romex...=disposer+plug
Reply With Quote
  #10  
Old 12/13/09, 8:26 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: disposer romex

Let's all bookmark this page!



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #11  
Old 12/13/09, 10:21 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: disposer romex

lol....yeah I liked my last line on that link....regarding the paper cuts....



Paul W. Abernathy
Reply With Quote
  #12  
Old 12/13/09, 11:48 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: disposer romex

Are you guys talking about this?

Sure seems common to me as this is from the first Inspection pictures I opened on seeing this thread.

disposer-romex-dsc06695-1024x768-.jpg
Reply With Quote
  #13  
Old 12/14/09, 10:53 AM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: disposer romex

Bob, In your pic I would certainly say it could have followed the cabinet surface better and could be neater and not being secured. I would have used a Panduit clamshell to secure it and kept it much neater.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Romex question jcahill Electrical Inspections 22 7/11/07 8:26 AM
Romex connected to male plug... OK? ghawley Electrical Inspections 20 3/4/07 6:05 PM
Romex Wire Through Stucco Wall Tab M. Wilcox Electrical Inspections 12 5/11/06 1:33 AM
Romex wire connected to standard male plug. ghawley Electrical Inspections 2 3/2/06 1:35 PM
Romex on a Boiler? mgifford Electrical Inspections 7 1/10/06 4:27 PM


All times are GMT -4. The time now is 8:50 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts