Ug, Sunday morning and typing report after last nights party.
Is romex allowed to be directly connected to a disposer? Can romex be directly attached to a three prong plug and used as an appliance cord? I know these conditins are common. Just looking to dot the i Thanks |
| Find an InterNACHI certified New Mexico Home Inspector (and anywhere else in North America) |
|
#2
|
|||
|
|||
|
Not properly...
InterNachi Awards Portal: http://co.nachi.org/inachiawards/ ____________________________________________ "An Education, not just an Inspection" Larry Kage, CMI Lake Ann (Traverse City), Michigan 49650 231 929 3525 Professional Inspector serving the Traverse City, Michigan area and beyond.
|
|
#3
|
||||
|
||||
|
There should be a Romex connector or strain relief bushing where it enters the disposal. It should not be directly on the edges of the entrance opening without being protected from abrasion damage.
“The things that will destroy America are peace at any price, prosperity at any cost, safety first instead of duty first, the love of soft living, and the get-rich-quick theory of life.” Theodore Roosevelt Joe Funderburk, CMI Alpha & Omega Home Inspections, LLC Inspecting Upstate SC & Charlotte Metro, NC NACHI ID: NACHI05120170 www.aohomeinspection.com |
|
#4
|
||||
|
||||
|
Romex was not intended for use outside of a finished wall system.
Romex cannot be used as an extension cord. Armor shielding should be used to protect Romex to the garbage disposal as this is a high traffic area and the wiring is susceptible to damage. "Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein Clarksville - Nashville Home Inspector Lic#40 http://www.midtninspections.com ITC Level III Thermographer Cert#1958 Building Science Thermographer Cert#33784 http://www.thermalimagingscan.com HVAC Certification EPA Cert#2046620 Link to my Website at: http://www.midtninspections.com/link-submission |
|
#5
|
|||
|
|||
|
Two concerns
If solid wire can be properly attached (per code or manufacturer) to the connectors inside a disposer or receptacle. I suppose there is a special plug out there designed for romex but I am concerned with the everyday type plug. I see this all the time on older homes. Romex through a wall and directly connected to the disposer. Obvious its been there and working for years. |
|
#6
|
|||
|
|||
|
Please Note:
Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
I don't see properly secured NM under a sink as subject to damage. It is the common installation method that I am familiar with. I have never seen a cord and plug connected disposal.
Connections between NM and the disposal leads would not be any different that connections to a lighting fixture. You will not find a cord cap that is listed for use with NM cable. |
|
#7
|
||||
|
||||
|
You are likely going to see all kinds of homeowner installed crap as a home inspector. The frequency of times it is seen does not change it and make it right. Just as orange (or any color) extension cord is not appropriate wiring for use as permanent house wiring, Romex or any other NM cable should not be used for applications like garbage disposals, where an appliance (stranded / flexible) cord with an approved plug should be used.
"War is an ugly thing, but not the ugliest of things; the decayed and degraded state of moral and patriotic feeling which thinks nothing is worth a war, is worse. A man who has nothing which he cares more about than he does about his personal safety is a miserable creature who has no chance at being free, unless made and kept so by the exertions of better men than himself." - John Stuart Mill |
|
#8
|
|||
|
|||
|
I do see ALOT of cord connected disposals. The NEC allows this type of application with length limitations and properly listed cords. NM Cable would not be allowed for this applcation with a plug attached to the end.
Paul W. Abernathy |
|
#9
|
||||
|
||||
|
What...didn't you write it down the first time John?
http://www.nachi.org/forum/f19/romex...=disposer+plug |
|
#10
|
||||
|
||||
|
Let's all bookmark this page!
“The things that will destroy America are peace at any price, prosperity at any cost, safety first instead of duty first, the love of soft living, and the get-rich-quick theory of life.” Theodore Roosevelt Joe Funderburk, CMI Alpha & Omega Home Inspections, LLC Inspecting Upstate SC & Charlotte Metro, NC NACHI ID: NACHI05120170 www.aohomeinspection.com |
|
#11
|
|||
|
|||
|
lol....yeah I liked my last line on that link....regarding the paper cuts....
Paul W. Abernathy |
|
#12
|
||||
|
||||
|
Are you guys talking about this?
Sure seems common to me as this is from the first Inspection pictures I opened on seeing this thread.
|
|
#13
|
|||
|
|||
|
Please Note:
Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Bob, In your pic I would certainly say it could have followed the cabinet surface better and could be neater and not being secured. I would have used a Panduit clamshell to secure it and kept it much neater.
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Romex question | jcahill | Electrical Inspections | 22 | 7/11/07 8:26 AM |
| Romex connected to male plug... OK? | ghawley | Electrical Inspections | 20 | 3/4/07 6:05 PM |
| Romex Wire Through Stucco Wall | Tab M. Wilcox | Electrical Inspections | 12 | 5/11/06 1:33 AM |
| Romex wire connected to standard male plug. | ghawley | Electrical Inspections | 2 | 3/2/06 1:35 PM |
| Romex on a Boiler? | mgifford | Electrical Inspections | 7 | 1/10/06 4:27 PM |