Default Distance?

Need Help Quick.....

What is the maximum distance a 125V receptacle can be from a Heat Pump to service it.

This is new construction, commercial. Is it still 25'...???? in the 2005 NEC.

The Heat Pumps are on the roof, the electrician said the receptacles on the wall below are good enough. Don't they have to be on the roof, or am I losing my mind? Was the rule changed in 2005, doesn't make sense if it was.

Paul, Joe, Jeff...anyone...if you could reference the rule number please, I'm sitting in my truck.
Reply With Quote
  #2  
Old 7/14/06, 6:10 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: Distance?

I believe they have to be IN SIGHT OF Dale

I think I read your question wrong, never mind

Last edited by bkelly2; 7/14/06 at 6:16 PM..
Reply With Quote
  #3  
Old 7/14/06, 6:32 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: Distance?

02 NEC 210.63 within 25' on same elevation
Reply With Quote
  #4  
Old 7/14/06, 7:00 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: Distance?


Brian's got it. No change from '02 to '05.

210.63 Heating, Air-Conditioning, and Refrigeration Equipment Outlet.
A 125-volt, single-phase, 15- or 20-ampere-rated receptacle outlet shall be installed at an accessible location for the servicing of heating, air-conditioning, and refrigeration equipment. The receptacle shall be located on the same level and within 7.5 m (25 ft) of the heating, air-conditioning, and refrigeration equipment. The receptacle outlet shall not be connected to the load side of the equipment disconnecting means.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net



Last edited by jpope; 7/14/06 at 7:12 PM..
Reply With Quote
  #5  
Old 7/14/06, 7:13 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Distance?

Historical Information:

When that rule was first added to the NEC ? it was set at 75 feet maximum distance away from the HACR (note never did call in ventilation) , so if this is true in your instance (time of installation) then I would let it be. The change to 25 feet was only to settle the disputes between the Mechanical Code Inspectors and the Electrical AHJ's who were calling out different distances.
Reply With Quote
  #6  
Old 7/14/06, 7:18 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Distance?

Research 210.8(A) too, also for more on this rule especially where they say the receptacle was not, and is now required on the rooftop, the changes now call for ALL outdoor receptacles to be GFCI protected.
Reply With Quote
  #7  
Old 7/14/06, 8:46 PM
Dale Duffy's Avatar
Dale Duffy Dale Duffy is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Scottsdale, AZ
Posts: 8,261
Default Re: Distance?

Thanks guys,

I was inspecting a different building and a friend called me to look at his roof and AC units before they foamed it tomorrow.

Not thinking much about the electrical because I was not inspecting it.

I look for an outlet to plug a drill in to tighten numerous access panels on the package Heat Pumps and there wasn't a single receptacle on the roof.

The electrician was arguing with me saying the electrical just passed inspection yesterday.

Needless to say...City Inspectors don't go on roofs in Arizona, but the electrician is going back on the roof.
Reply With Quote
  #8  
Old 7/16/06, 12:03 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Distance?

Dale,

If on the roof...make sure they take into account derating...



Paul W. Abernathy
Reply With Quote
  #9  
Old 7/16/06, 2:08 PM
Dale Duffy's Avatar
Dale Duffy Dale Duffy is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Scottsdale, AZ
Posts: 8,261
Default Re: Distance?

Quote:
Originally Posted by pabernathy
Dale,

If on the roof...make sure they take into account derating...
Yeah Right!

I'll probably see one leg jumped from a 240V next week......
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Hose pipe distance from outlet lprinzi Plumbing Inspections 2 10/21/06 4:20 PM
Distance between Refrigerator & Stove wrosario Interior Inspections 32 8/6/06 7:17 PM
Distance from gas meter? psmothers Electrical Inspections 1 3/9/06 4:51 PM
Proper distance between a washer drain pipe and 220 volt dryer connection rpaul Electrical Inspections 14 1/3/06 9:43 PM