If a distribution (sub) panel is connected by conduit to the main disconnect panel is that method of bonding sufficient to replace the 4th wire?
http://www.SmithHomeInspection.com SmithHomeInspection@yahoo.com NY State Lic. # 16000008304 631-434-5200 |
That is not for you to determine (even though it may be okay).
Metallic conduit can be used as the EGC (equipment grounding conductor). It must be continuous and bonded to both enclosures (service and load side panels), and the neutral must be isolated at the load side panel. If the entire conduit was not visible for inspection, it should be deferred for verification. GEC = grounding electrode conductor IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net Last edited by jpope; 9/12/06 at 9:37 PM.. |
http://www.SmithHomeInspection.com SmithHomeInspection@yahoo.com NY State Lic. # 16000008304 631-434-5200 Last edited by bsmith; 9/12/06 at 10:05 PM.. Reason: mispelling |
AS jeff stated...the conduit MAY be fine for the " Equipment Grounding Conductor" to the remote distribution panel. While proving this can be difficult for the HI.....it is important to note that IF a person is attempting to do this ( which I am sure they do alot in Illinois ) that all the connections and ko's and so on it correct within the enclosure for it to even be allowed...not so mention like jeff said....that is it conduit on both ends of the application.
Paul W. Abernathy,CMI,CPI,CME National Electrical Code Expert Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru Weekly Chat on Wednesdays -7:30 PM E.S.T * Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections" 2007 InterNACHI Member of the Year |
Thanks Paul-
The conduit run was only about 18" so it was easy to check, but the locknut were loose and not secure connections. Referal time. "A man cannot be truly grateful and remain unhappy"
Bill,
yeppers....also keep an eye out their for those who also do this with a metal nipple and STILL run (4) wires through the nipple. You can't use the nipple for this and then expect to also use the enclosed conductor.....that creates parallel paths and not allowed. This is why the majority of installers will use PVC for the connections between distribution panels.....IF they are going to run a 4 wire setup...but keep an eye open for it...as it would be wrong. Paul W. Abernathy,CMI,CPI,CME National Electrical Code Expert Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru Weekly Chat on Wednesdays -7:30 PM E.S.T * Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections" 2007 InterNACHI Member of the Year |
Good info Paul - Thanks
As a comparison, if you defer that then why not recommend the wall studs be verified for proper spacing? Why not recommend the ground rod be checked to see if it is only two feet long? Why not recommend the ground be dug up to verify the footers are there? See where this could lead? If other issues are requiring an electrician anyway it could be noted that additional testing may be obtained at the clients discretion but not for that sole purpose (partially hidden conduit) only. |
jclark1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
A few variables exist when using conduit as a ECG. The type of connector (if emt), double locknuts (rigid), rules regarding concentric knockouts, whether or not bonding bushings are required, etc. Not things the average HI is qoing to know.
acox is a non-member guest and is in no way affiliated with InterNACHI or its members.