Default Distribution panel GEC

If a distribution (sub) panel is connected by conduit to the main disconnect panel is that method of bonding sufficient to replace the 4th wire?



"A man cannot be truly grateful and remain unhappy"
http://www.SmithHomeInspection.com
SmithHomeInspection@yahoo.com
NY State Lic. # 16000008304
631-434-5200
Reply With Quote
  #2  
Old 9/12/06, 7:57 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: Distribution panel GEC

That is not for you to determine (even though it may be okay).

Metallic conduit can be used as the EGC (equipment grounding conductor). It must be continuous and bonded to both enclosures (service and load side panels), and the neutral must be isolated at the load side panel.

If the entire conduit was not visible for inspection, it should be deferred for verification.

GEC = grounding electrode conductor



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net



Last edited by jpope; 9/12/06 at 8:37 PM..
Reply With Quote
  #3  
Old 9/12/06, 8:31 PM
Bill Smith's Avatar
Bill Smith Bill Smith is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: East Northport, NY
Posts: 1,043
Default Re: Distribution panel EGC

Quote:
That is not for you to determine
Very true Jeff, but I was wondering for future reference. The whole system was a mess. Another fused main disconnect with 2 distribution panels - one was a Pushmatic and the other an FPE Stab-lock both loosely connected by conduit. Thanks for your reply.



"A man cannot be truly grateful and remain unhappy"
http://www.SmithHomeInspection.com
SmithHomeInspection@yahoo.com
NY State Lic. # 16000008304
631-434-5200

Last edited by bsmith; 9/12/06 at 9:05 PM.. Reason: mispelling
Reply With Quote
  #4  
Old 9/13/06, 1:22 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Distribution panel GEC

AS jeff stated...the conduit MAY be fine for the " Equipment Grounding Conductor" to the remote distribution panel. While proving this can be difficult for the HI.....it is important to note that IF a person is attempting to do this ( which I am sure they do alot in Illinois ) that all the connections and ko's and so on it correct within the enclosure for it to even be allowed...not so mention like jeff said....that is it conduit on both ends of the application.



Paul W. Abernathy
Reply With Quote
  #5  
Old 9/13/06, 7:19 AM
Bill Smith's Avatar
Bill Smith Bill Smith is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: East Northport, NY
Posts: 1,043
Default Re: Distribution panel GEC

Thanks Paul-

The conduit run was only about 18" so it was easy to check, but the locknut were loose and not secure connections. Referal time.



"A man cannot be truly grateful and remain unhappy"
http://www.SmithHomeInspection.com
SmithHomeInspection@yahoo.com
NY State Lic. # 16000008304
631-434-5200
Reply With Quote
  #6  
Old 9/13/06, 8:39 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Distribution panel GEC

Bill,

yeppers....also keep an eye out their for those who also do this with a metal nipple and STILL run (4) wires through the nipple. You can't use the nipple for this and then expect to also use the enclosed conductor.....that creates parallel paths and not allowed.

This is why the majority of installers will use PVC for the connections between distribution panels.....IF they are going to run a 4 wire setup...but keep an eye open for it...as it would be wrong.



Paul W. Abernathy
Reply With Quote
  #7  
Old 9/13/06, 10:35 AM
Bill Smith's Avatar
Bill Smith Bill Smith is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: East Northport, NY
Posts: 1,043
Default Re: Distribution panel GEC

Good info Paul - Thanks



"A man cannot be truly grateful and remain unhappy"
http://www.SmithHomeInspection.com
SmithHomeInspection@yahoo.com
NY State Lic. # 16000008304
631-434-5200
Reply With Quote
  #8  
Old 9/13/06, 10:46 AM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,206
Default Re: Distribution panel GEC

Quote:
Originally Posted by jpope
That is not for you to determine (even though it may be okay).

Metallic conduit can be used as the EGC (equipment grounding conductor). It must be continuous and bonded to both enclosures (service and load side panels), and the neutral must be isolated at the load side panel.

If the entire conduit was not visible for inspection, it should be deferred for verification.

GEC = grounding electrode conductor
Home Inspectors should not defer something for further evaluation unless evidence or a reasonable issue exists. If the correct conduit is present at both ends, no problem is evident and it would be unfair and out of scope to recommend anything else. Some states have limitations also on this type of reporting.

As a comparison, if you defer that then why not recommend the wall studs be verified for proper spacing? Why not recommend the ground rod be checked to see if it is only two feet long? Why not recommend the ground be dug up to verify the footers are there? See where this could lead?

If other issues are requiring an electrician anyway it could be noted that additional testing may be obtained at the clients discretion but not for that sole purpose (partially hidden conduit) only.
Reply With Quote
  #9  
Old 9/13/06, 10:50 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: Distribution panel GEC

Quote:
Originally Posted by bking
Home Inspectors should not defer something for further evaluation unless evidence or a reasonable issue exists.
I completely agree.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #10  
Old 9/13/06, 12:44 PM
jclark1's Avatar
jclark1 jclark1 is offline
Active Poster
 
Join Date: Nov 2005
Location: Vashon, Wa
Posts: 644
Please Note: jclark1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Distribution panel GEC

A few variables exist when using conduit as a ECG. The type of connector (if emt), double locknuts (rigid), rules regarding concentric knockouts, whether or not bonding bushings are required, etc. Not things the average HI is qoing to know.
Reply With Quote
  #11  
Old 9/13/06, 1:12 PM
Andrew Cox Andrew Cox is offline
InterNACHI Member
 
Join Date: May 2006
Location: Kissimmee, FL
Posts: 1,064
Default Re: Distribution panel EGC

Quote:
Originally Posted by bsmith
The whole system was a mess. Another fused main disconnect with 2 distribution panels - one was a Pushmatic and the other an FPE Stab-lock both loosely connected by conduit.
It would be a complete disservice to refer out unnecessarily. It doesn't look like that's the case here, though...



Andy Cox
http://www.CoxInspections.com
Kissimmee, FL
You’re Your Own Job Security.
Reply With Quote
  #12  
Old 9/13/06, 3:26 PM
Bill Smith's Avatar
Bill Smith Bill Smith is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: East Northport, NY
Posts: 1,043
Default Re: Distribution panel EGC

Quote:
Originally Posted by acox
It would be a complete disservice to refer out unnecessarily. It doesn't look like that's the case here, though...
No - the referal in this case is completely justified. In regards to the conduit - the locknuts were loose and poor connections were made.
Attached Thumbnails
distribution-panel-grounding-electrode-conductor-dscf1960.jpg  



"A man cannot be truly grateful and remain unhappy"
http://www.SmithHomeInspection.com
SmithHomeInspection@yahoo.com
NY State Lic. # 16000008304
631-434-5200
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
National Electrical Code Information and Discussion jtedesco1 Electrical Inspections 50 6/15/10 7:28 PM
Remote distribution panel or subpanel? rwilcox Electrical Inspections 57 1/11/08 6:49 PM
Panel Inspection Safety roconnor Electrical Inspections 10 9/24/06 9:02 PM
Distribution panel cpennick Electrical Inspections 2 7/7/06 10:23 PM
Bad electrical problem Pest Guy Electrical Inspections 4 1/20/06 9:26 PM


All times are GMT -4. The time now is 2:32 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts