Default Distribution panel neutral/ground separation question

Need some help understanding something.

Since the whole idea of the separation is that its possible for current to follow a parallel path -- over the bare grounding wires -- instead of the insulated neutral wires -- as it finds its way back to the source, which can present the hazard. Right? Now, at yesterday's inspection all of the outlets were 2-prong, not one grounded or 3-prong outlet. Would the distribution panel still need to be separated? Would it matter? Thanks for all replies, and your time is appreciated!

Reply With Quote
Find an InterNACHI certified Utah Home Inspector (and anywhere else in North America)
  #2  
Old 9/15/09, 3:07 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,033
Default Re: Distribution panel neutral/ground separation question

Yes, although the term "separated" may cause a bit of confusion. The term should be "isolated" or "ungrounded" at the distribution panel.

The distribution panel must be bonded to the service equipment, which essentially means that it is grounded. If the neutrals are not isolated, they become "grounded" at the distribution panel which (as we know) is improper.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #3  
Old 9/15/09, 4:23 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 3,697
Default Re: Distribution panel neutral/ground separation question

I was trying to explain this the other day to a client...

Mr. Pope can correct me if I'm wrong (I consider him the expert).

You can connect neutral and ground at the Main service panel because that is the "junction point" where electrical service enters the house. Anything downstream of the main service panel has junctions which may become loose or inadequately connected allowing current to flow back into the neutral, rather than the ground due to inadequate path of least resistance to ground.

There is only one point of connection in the Main service panel for each component. Once you extend the electrical conductors to subsequent service panel's, you increase the potential of increased resistance which may cause electrical failure to back feed on a path of least resistance to a non-desirable location.

The main service panel has two legs of power, one neutral to the transformer, one grounded electrical conductor (to a grounding rod, hopefully below the meter box), one grounded electrical conductor back to the main transformer feed, and possible other connections depending on design.

Any interpretation that electrical current does not flow on neutral lines is a fallacy! It will in fact get you killed! Neutral wires are not on the same level as ground wires. They do carry electrical current where as ground wires do not. If you have an electrical failure which causes current to flow back onto the grounding system, you want the least path of resistance to be on the grounding conductors rather than the neutral.

Neutral wiring carries electrical current, therefore reducing its capacity to provide a line of least resistance back to earth where the electrical current does not cause physical injury. Grounding conductors should never be considered "the same as " neutral conductors.



David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Certified Level II Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620

Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #4  
Old 9/16/09, 4:46 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Distribution panel neutral/ground separation question

Your last sentence is incorrect in it's nature in some parts.....

You stated:
Quote:
Neutral wiring carries electrical current, therefore reducing its capacity to provide a line of least resistance back to earth where the electrical current does not cause physical injury. Grounding conductors should never be considered "the same as " neutral conductors.
Remember...electrical current on a neutral is NEVER trying to get to the earth...it is trying to get to the source of it's creation and nothing more. If the earth is presented as a path it will travel on all paths...not just the path of least resistance. However, since the earth is such a high path of impedence it is not considered a good path nor is it ever an allowed path. Neutral conductors always carry current....grounding conductors only carry current under an abnormal condition for the most part so they should never be confused.



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #5  
Old 9/16/09, 5:21 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2009
Location: Chicago
Posts: 1,045
Default Re: Distribution panel neutral/ground separation question

Quote:
Originally Posted by pabernathy View Post
Your last sentence is incorrect in it's nature in some parts.....

You stated:

Remember...electrical current on a neutral is NEVER trying to get to the earth...it is trying to get to the source of it's creation and nothing more. If the earth is presented as a path it will travel on all paths...not just the path of least resistance. However, since the earth is such a high path of impedence it is not considered a good path nor is it ever an allowed path. Neutral conductors always carry current....grounding conductors only carry current under an abnormal condition for the most part so they should never be confused.
Paul when you say Neutral conductors always carry current, you meant when under load?
Reply With Quote
  #6  
Old 9/16/09, 6:45 PM
Patrick Bolliger's Avatar
Patrick Bolliger Patrick Bolliger is offline
InterNACHI Member
 
Join Date: Aug 2005
Location: Chicago, IL
Posts: 830
Send a message via Skype™ to pbolliger
Default Re: Distribution panel neutral/ground separation question

Quote:
Originally Posted by belliott View Post
Paul when you say Neutral conductors always carry current, you meant when under load?

Yes Bob...when there is a load. Be it light, motor or toaster...or Bob

Hot wire------> Load<--------"neutral" wire
"Watts"

Now lets place Bob as the "load" Hot wire-----> "bob load"<---"neutral" wire.... ZZZAAAP!


OUCH! Notice the smoke from Bobs...shirt collar...
Reply With Quote
  #7  
Old 9/16/09, 6:49 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2009
Location: Chicago
Posts: 1,045
Default Re: Distribution panel neutral/ground separation question

Quote:
Originally Posted by pbolliger View Post
Yes Bob...when there is a load. Be it light, motor or toaster...or Bob

Hot wire------> Load<--------"neutral" wire
"Watts"

Now lets place Bob as the "load" Hot wire-----> "bob load"<---"neutral" wire.... ZZZAAAP!


OUCH! Notice the smoke from Bobs...shirt collar...
Thank You Paul.
You sure have gotten violent since you changed your name.
Reply With Quote
  #8  
Old 9/16/09, 6:55 PM
Patrick Bolliger's Avatar
Patrick Bolliger Patrick Bolliger is offline
InterNACHI Member
 
Join Date: Aug 2005
Location: Chicago, IL
Posts: 830
Send a message via Skype™ to pbolliger
Default Re: Distribution panel neutral/ground separation question

I like the "hands on" approach.. we can experiment at the next meeting..
I will bring the wires and you can hold them
Reply With Quote
  #9  
Old 9/16/09, 7:40 PM
Buck Hartley, CMI Buck Hartley, CMI is offline
InterNACHI Member
 
Join Date: Nov 2005
Location: Shawnee, KS
Posts: 843
Default Re: Distribution panel neutral/ground separation question

Is the proper way to do the separation? This was found in the main panel today. House is new, never been lived in. The local inspector, told the builder to remove this ground bar.
Attached Thumbnails
distribution-panel-neutral-ground-separation-question-100_4871.jpg  



Mid America Property Inspections, Inc.
Shawnee, KS 66217
NACHI # 05110992
KS-Registration # 0110-0008

Reply With Quote
  #10  
Old 9/16/09, 9:30 PM
Patrick Bolliger's Avatar
Patrick Bolliger Patrick Bolliger is offline
InterNACHI Member
 
Join Date: Aug 2005
Location: Chicago, IL
Posts: 830
Send a message via Skype™ to pbolliger
Default Re: Distribution panel neutral/ground separation question

Quote:
Originally Posted by bhartley View Post
Is the proper way to do the separation? This was found in the main panel today. House is new, never been lived in. The local inspector, told the builder to remove this ground bar.
Buck,
That piece of copper is used to "bond" the panel to the neutral buss. Known as panel bonding.

If that panel you opened is a distribution panel aka "sub" panel then the neutral buss and "grounds" should be isolated from each other. It would be nice to see a ground buss and a neutral buss in the distribution (sub) panel but it is not often that you see them (at least in my area $$) . Depending on the brand of the panel you may have two "buss-es" present that can be physically disconnected from each other by a bar or some type of connection..

Ideally the ground connections (GEC) should /would be back at the origin of the electrical service entry. Check your local requirements..
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Electrical for Dummies mcyr Electrical 16 6/9/08 10:59 PM
National Electrical Code Information and Discussion jtedesco1 Electrical 44 4/18/08 12:43 AM
Panel Question jwilliams7 Electrical 8 6/7/06 9:10 AM
Service Panel question for board sparkies pbolliger Electrical 8 5/14/06 10:24 AM
Bad electrical problem Pest Guy Electrical 4 1/20/06 10:26 PM


All times are GMT -4. The time now is 12:13 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts