Default Distribution panel question

Service panel on the exterior of home. Home is two years old. Distribution panel in garage about 50 feet away. I only see two ungrounded conductors and one grounded conductor coming to panel. I dont see a ground? I usually see a ground lug attacthed to the ground strip or bus. What is going on or am I missing something? How much smaller can the ground be on a 4-wire system. Any help would be appreciated. PS - all the ground wires appear to be 12 gauge. 60 amp feed from service panel. I would think mininum of a #6 ground conductor would be needed on a 4 wire system goint to the distribution panel.
Attached Thumbnails
distribution-panel-question-nachi.jpg   distribution-panel-question-nachi2.jpg   distribution-panel-question-nachi3.jpg  

Last edited by jlybolt; 4/3/07 at 9:32 PM..
Reply With Quote
  #2  
Old 4/3/07, 9:32 PM
William A. Rosario's Avatar
William A. Rosario William A. Rosario is offline
InterNACHI Member
 
Join Date: Jul 2006
Location: Bayamon, PR
Posts: 43
Default Re: Distribution panel question

Quote:
Originally Posted by jlybolt
... I only see two ungrounded conductors and one grounded conductor coming to panel. I dont see a ground?...
I don't undestand your message here...

What I saw on the second image is a Neutral cable (White) which appears to be connected directly to a circuit breaker when its color is incorrect base on color code and circuit breaker appears not to be GFCI/AFCI.

Can you give me more information on the statement quoted?

Which type of panel is this?

William
Reply With Quote
  #3  
Old 4/3/07, 9:53 PM
wsiegel wsiegel is offline
Active Poster
 
Join Date: Oct 2006
Location: Hialeah, Fl
Posts: 2,542
Please Note: wsiegel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Distribution panel question

The over bundling of wires should be a concern to you.
Reply With Quote
  #4  
Old 4/3/07, 9:56 PM
jlybolt jlybolt is offline
Active Poster
 
Join Date: Feb 2005
Location: Conroe, TX
Posts: 305
Please Note: jlybolt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Distribution panel question

In other words two hot conductors and one neutral, but I dont see a ground.
This is a subpanel in the garage. It should have a 4 wires going to it from the main panel. All the ground wires that are in the panel appear to be 12 gauge. Should there be a #6 mininum for the ground wire coming in from the main panel since a 60 amp breaker supplies the distribution panel.?
Reply With Quote
  #5  
Old 4/3/07, 10:11 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Distribution panel question

Quote:
Originally Posted by jlybolt
Should there be a #6 mininum for the ground wire coming in from the main panel since a 60 amp breaker supplies the distribution panel.?
No. It will be a #10. Could you be mistaking a #10 for all #12s?
Reply With Quote
  #6  
Old 4/3/07, 10:12 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Distribution panel question

Quote:
Originally Posted by wsiegel
The over bundling of wires should be a concern to you.
How do you know they are "over" bundled?
Reply With Quote
  #7  
Old 4/3/07, 10:20 PM
jlybolt jlybolt is offline
Active Poster
 
Join Date: Feb 2005
Location: Conroe, TX
Posts: 305
Please Note: jlybolt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Distribution panel question

#10 ? Were do you get this number? It is possible that I mistaken a 10 for a 12 but they sure all look the same.
Reply With Quote
  #8  
Old 4/3/07, 10:25 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Distribution panel question

Quote:
Originally Posted by jlybolt
#10 ? Were do you get this number?
From the NEC. The ground for 60 amp is #10.
Reply With Quote
  #9  
Old 4/3/07, 10:39 PM
William A. Rosario's Avatar
William A. Rosario William A. Rosario is offline
InterNACHI Member
 
Join Date: Jul 2006
Location: Bayamon, PR
Posts: 43
Default Re: Distribution panel question

Quote:
Originally Posted by jlybolt
In other words two hot conductors and one neutral, but I dont see a ground.
I would recommend to install a Ground to all the panels and provide in the report the pictures that show missing of gorund cable.

However Neutral Bar and Ground Bar are both connected, since the Neutral Cable act as a Mechanical Ground that starts on your main entrance facility prior to reach the electric meter.
Reply With Quote
  #10  
Old 4/3/07, 10:44 PM
jlybolt jlybolt is offline
Active Poster
 
Join Date: Feb 2005
Location: Conroe, TX
Posts: 305
Please Note: jlybolt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Distribution panel question

Mark could you be a little more specific? I know its somewhere in the NEC but I must be flipping over the pages. I have fallen and I cant get up. Must be to much sun today. Its a change from all the rain we have had lately.
Reply With Quote
  #11  
Old 4/3/07, 10:47 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Distribution panel question

Quote:
Originally Posted by wrosario
I would recommend to install a Ground to all the panels and provide in the report the pictures that show missing of gorund cable.

However Neutral Bar and Ground Bar are both connected, since the Neutral Cable act as a Mechanical Ground that starts on your main entrance facility prior to reach the electric meter.
WHAT???

First off, why would you recommend a certain fix? How do you know this fix is appropriate? HOW do you know the ground is missing????
WHY would you install a ground rod???????????


The neutral conductor MOST CERTAINLY DOES NOT "act" as a ground.
This is a sub panel. I can only assume itis within the same structure as the main since it is of the main lug variety. Look closer at the pics and you will see the bars are definitely NOT connected. The ground bar is bonded, the neutral is not.
Reply With Quote
  #12  
Old 4/3/07, 10:48 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Distribution panel question

Quote:
Originally Posted by jlybolt
Mark could you be a little more specific? I know its somewhere in the NEC but I must be flipping over the pages. I have fallen and I cant get up. Must be to much sun today. Its a change from all the rain we have had lately.
Table 250.122
A modern copper 6/3NM cable will have a #10 ground within the sheath.
Reply With Quote
  #13  
Old 4/3/07, 10:55 PM
jlybolt jlybolt is offline
Active Poster
 
Join Date: Feb 2005
Location: Conroe, TX
Posts: 305
Please Note: jlybolt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Distribution panel question

Excellent. I didnt see that one. It is possible that the 10 looked like a 12. I was looking at 250-66 GEC sizing.
Thank you

Last edited by jlybolt; 4/3/07 at 10:59 PM..
Reply With Quote
  #14  
Old 4/3/07, 10:59 PM
William A. Rosario's Avatar
William A. Rosario William A. Rosario is offline
InterNACHI Member
 
Join Date: Jul 2006
Location: Bayamon, PR
Posts: 43
Default Re: Distribution panel question

Quote:
Originally Posted by Speedy Petey
WHAT???

First off, why would you recommend a certain fix? How do you know this fix is appropriate? HOW do you know the ground is missing????
WHY would you install a ground rod???????????


The neutral conductor MOST CERTAINLY DOES NOT "act" as a ground.
This is a sub panel. I can only assume itis within the same structure as the main since it is of the main lug variety. Look closer at the pics and you will see the bars are definitely NOT connected. The ground bar is bonded, the neutral is not.
First looking closer to the panel found there is no connection as I said before. My excuses for not take a closer look first.

But

Why I would not recommend a ground to the panel, why I have ground connections to a bar where there is no connection to Ground. I'm not saying to install a ground Rod but if you can provide ground cable from previous panel will this won't work?
Reply With Quote
  #15  
Old 4/3/07, 11:02 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Distribution panel question

Quote:
Originally Posted by wrosario
I'm not saying to install a ground Rod but if you can provide ground cable from previous panel will this won't work?
Absoultey not. A ground rod DOES NOT "provide" a ground.

The installation in question is so new I guarantee there is a ground there. Unless the 6/3 cable used was 40 years old.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Panel question bgraham Electrical Inspections 3 4/4/07 7:30 PM
Wiring question in panel dmacy Electrical Inspections 23 2/14/07 12:27 PM
Service panel Question cpetty Electrical Inspections 4 1/24/07 10:36 PM
Service Panel question for board sparkies pbolliger Electrical Inspections 8 5/14/06 10:24 AM
Bad electrical problem Pest Guy Electrical Inspections 4 1/20/06 10:26 PM


All times are GMT -4. The time now is 7:31 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts